Line Input Voltage - How to interpret Logs

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Line Input Voltage - How to interpret Logs
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:25 AM . Last Modified: ‎2024-03-18 12:28 AM

0 Likes
4
1369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:25 AM . Last Modified: ‎2024-03-18 12:28 AM

Line Input Voltage - How to interpret Logs

I am looking at the Data Logs on my SC620 and interpreting what I see for the maximum and minimum Line Input Voltage over an extended logging period. The values listed in this log seem to be selected from a list of possible values at discrete intervals of about 1.4 to 1.5 volts. Am I interpreting things correctly with the following?

The logged maximum voltage value is the threshold voltage which was not exceeded for more than a negligible amount of time during the set logging interval leading up to value.

I am also using a calibrated multimeter to do spot measurements during the logging period as a reference check. Any further information on this topic would be very helpful at this stage.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 07:25 AM . Last Modified: ‎2024-03-18 12:28 AM

0 Likes
0
1369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:25 AM . Last Modified: ‎2024-03-18 12:28 AM

I don't think there's published information about low-level details of that nature. It's reasonable to assume there's quantization from A/D conversion, processing, and binary to decimal conversion.

You might find a variac useful. I use it when testing UPS transfer behavior. It lets you set the voltage and see what happens.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 07:25 AM . Last Modified: ‎2024-03-18 12:28 AM

0 Likes
0
1369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:25 AM . Last Modified: ‎2024-03-18 12:28 AM

Big picture -- any notion of "max" or "min" voltage is subject to bandwidth constraints, otherwise it would just be measuring noise on the line.

In the case of the SmartUPS, the network management card samples the line voltage on the order of seconds and you're seeing the max or min of that. Good for observing long term voltage behaviors but you won't see transients. Newer UPSes don't even report max and min.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:25 AM . Last Modified: ‎2024-03-18 12:28 AM

0 Likes
0
1369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:25 AM . Last Modified: ‎2024-03-18 12:28 AM

Thank you voidstar for your feedback.  I do not have a network management card in my ups, just a serial interface.  I don’t know if that uses a different monitoring model.

I am looking at a monitoring session that ran for 11 days logging at 1 minute intervals.  So that is about 16,000 records.  What I can see is that all the voltage levels recorded are drawn from just eight voltage values, namely:

250.5
249.1
247.6
244.8
243.3
240.4
239.0
237.6

There are no intermediate voltages tabled for either Minimum Line Voltage or Maximum Line Voltage.  I can only conclude that the monitoring system is only acknowledging the tightest band of voltages for each sampling interval with the band limits drawn from the eight values given above.

For some logged intervals the maximum voltage and minimum voltage are the same.   You could conclude from this that there was insufficient transients/noise present during that interval to justify logging the next highest or lowest reference voltage.  This is just surmising on my part.  What I would really like to know is the model the monitoring system is using to discretize the recorded values.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:25 AM . Last Modified: ‎2024-03-18 12:28 AM

0 Likes
0
1369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:25 AM . Last Modified: ‎2024-03-18 12:28 AM

Do I need to conclude that the rationale for the method of voltage measurement on my SC620 is secret APC business?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 07:25 AM . Last Modified: ‎2024-03-18 12:28 AM

0 Likes
0
1370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:25 AM . Last Modified: ‎2024-03-18 12:28 AM

I don't think there's published information about low-level details of that nature. It's reasonable to assume there's quantization from A/D conversion, processing, and binary to decimal conversion.

You might find a variac useful. I use it when testing UPS transfer behavior. It lets you set the voltage and see what happens.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of