Is vMA or PowerChute Appliance required for PCNS 3.1 for VMware ESXi

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Is vMA or PowerChute Appliance required for PCNS 3.1 for VMware ESXi
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:38 AM . Last Modified: ‎2024-03-05 12:31 AM

0 Likes
5
1378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:38 AM . Last Modified: ‎2024-03-05 12:31 AM

Is vMA or PowerChute Appliance required for PCNS 3.1 for VMware ESXi

Hi, do anyone know if the vMA is REQUIRED or not in a configuration like this.

1 Physical Windows 2008 R2 with PCNS 3.1 installed and configured with VMware ESXi host options

1 VMware ESXi 5.1 server

1 APC 1500 mgmt board

4 VMs but no vMA or PowerChute Appliance

I'd like to Shutdown the Host and have the settings for VMs "Shutdown with the host" with the PCNS from the Physical server without any vMA

Page 10 and 11

http://www.apcmedia.com/salestools/PMAR-9DNLQK/PMAR-9DNLQK_R0_EN.pdf

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:38 AM . Last Modified: ‎2024-03-05 12:31 AM

0 Likes
0
1378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:38 AM . Last Modified: ‎2024-03-05 12:31 AM

Hi,

In the debug output:

2014-04-15T13:12:05.821Z [FFD81B90 info 'Vmomi'] Throw vim.fault.RestrictedVersion

2014-04-15T13:12:05.821Z [FFD81B90 info 'Vmomi'] Result:

--> (vim.fault.RestrictedVersion) {

-->    dynamicType = ,

-->    faultCause = (vmodl.MethodFault) null,

-->    msg = "",

--> }

vim.fault.RestrictedVersion would indicate that the free version of ESXi host is being used.

The free version of ESXi cannot be commanded to shut down down using the VMware SDK API functions in PCNS.

The following Kbase provides intstructions for shutting down the free version of ESXi via SOAP - FA159768


If you are only managing 1 ESXi host then the PCNS 3.1 Virtual Appliance or vMA can be used instead of installing PCNS on a Windows Machine.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:38 AM . Last Modified: ‎2024-03-05 12:31 AM

0 Likes
0
1378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:38 AM . Last Modified: ‎2024-03-05 12:31 AM

Hi,

You do not need to install PCNS on a vMA or install the Appliance in your configuration. PCNS client installed on the Windows system will sent the shut down signal to the VMware host.

Note: In order to gracefully shut down VMs, you must use the Virtual Machine Startup/Shutdown settings for the VMware host in the vSphere Client. This is accessible on the Configuration tab under Software in the vSphere Client.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:38 AM . Last Modified: ‎2024-03-05 12:31 AM

0 Likes
0
1378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:38 AM . Last Modified: ‎2024-03-05 12:31 AM

Hi Bill and thank you for your respons. That is good to hear but there seems to be some kind of bug in the PCNS 3.1 because the host isn't shutting down. Here is the output, attached log

Attachments
Logs.txt.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:38 AM . Last Modified: ‎2024-03-05 12:31 AM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:38 AM . Last Modified: ‎2024-03-05 12:31 AM

Hi,

In the debug output:

2014-04-15T13:12:05.821Z [FFD81B90 info 'Vmomi'] Throw vim.fault.RestrictedVersion

2014-04-15T13:12:05.821Z [FFD81B90 info 'Vmomi'] Result:

--> (vim.fault.RestrictedVersion) {

-->    dynamicType = ,

-->    faultCause = (vmodl.MethodFault) null,

-->    msg = "",

--> }

vim.fault.RestrictedVersion would indicate that the free version of ESXi host is being used.

The free version of ESXi cannot be commanded to shut down down using the VMware SDK API functions in PCNS.

The following Kbase provides intstructions for shutting down the free version of ESXi via SOAP - FA159768


If you are only managing 1 ESXi host then the PCNS 3.1 Virtual Appliance or vMA can be used instead of installing PCNS on a Windows Machine.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:38 AM . Last Modified: ‎2024-03-05 12:31 AM

0 Likes
0
1378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:38 AM . Last Modified: ‎2024-03-05 12:31 AM

After chaning the License key to a Enterprise Plus the host did a shutdown as expected! I guess that the required feature is "vSphere API" which is missing in the Standard Edition

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:38 AM . Last Modified: ‎2024-03-05 12:31 AM

0 Likes
0
1377
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:38 AM . Last Modified: ‎2024-03-05 12:31 AM

Will investigate further. It should be possible to access ESXi hosts via the API functions using Essentials, Standard and Enterprise Licensing. Read-only access to the API functions is provided for the free version.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore