Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Is possible to restart the NMC AP9619 on Smart-UPS RT 5000 XL without affect UPS ??

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Is possible to restart the NMC AP9619 on Smart-UPS RT 5000 XL without affect UPS ??
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
lachito_apc
lachito_apc
Cadet

Posted: ‎2021-07-08 01:06 AM

0 Likes
3
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 01:06 AM

Is possible to restart the NMC AP9619 on Smart-UPS RT 5000 XL without affect UPS ??

This was originally posted on APC forums on 7/27/2015


Hi:

  Last night my APC network management card AP9619 began to send messages indicating error code: 0x0102 "Critical - UPS: Lost the local network management interface-to-UPS communication". After a few hours reading comments on this forum, I believe that I need to make a firmware upgrade to the NMC to 3.7.2. However, This UPS is the core unity of my infraestructure, so I need to create a window time frame to shutdown all the servers connected to it,  and make the firmware upgrade.

  My question is: can I do a Restart Management at any moment to recover communication with the UPS without affecting the UPS power outlets  to gain control over my UPS again on this days, and wait for the weekend to create the window time frame and apply the fix  ??

  I read it´s posible on a Smart-UPS RT6000 but I´n not sure about the Smart-UPS RT5000 and with AP6919 model.

  I really apreciate your comments !!!!!

  Best Regards,

Horacio Diaz-Requejo

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9619
  • NMC
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:06 AM

0 Likes
0
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 01:06 AM

This reply was originally posted by Angela on APC forums on 7/27/2015


Hi Horacio,

Yes, you can do this safely. Upgrading the firmware on the UPS Network Management Cards (AP9617/18/19/30/31/35) that we offer do not reboot the UPS when you upgrade their firmware.

You may want to just try a reboot before you go ahead and upgrade the firmware anyway..

See Answer In Context

Reply
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 01:06 AM

0 Likes
0
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 01:06 AM

This was originally posted on APC forums on 7/28/2015


The "communication lost" can be caused by one of 3 things: 1) the NMC (safe to reboot while UPS has load); 2) the microcontroller board on the UPS (generally requires a complete power cycle on the UPS, so shut down the load devices first); 3) something else on the same communication bus (serial console, extended runtime packs (on some UPS models) or other expansion cards (in some UPS models).

So, if rebooting the NMC doesn't clear the problem, I'd do a remove/insert on the NMC as my next step. After that, you'd need to power cycle the UPS (and "dead" it - see APC knowlege base) if the problem persists.

If you have one of the UPS models with a fancy front panel (I'm not too familiar with recent products) there may be useful information available on the LCD display if the problem is on the UPS side.

See Answer In Context

Reply
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:06 AM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 01:06 AM

This reply was originally posted by Angela on APC forums on 7/27/2015


Hi Horacio,

Yes, you can do this safely. Upgrading the firmware on the UPS Network Management Cards (AP9617/18/19/30/31/35) that we offer do not reboot the UPS when you upgrade their firmware.

You may want to just try a reboot before you go ahead and upgrade the firmware anyway..

Reply
lachito_apc
lachito_apc
Cadet

Posted: ‎2021-07-08 01:06 AM

0 Likes
0
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 01:06 AM

This was originally posted on APC forums on 7/27/2015


Thanks for your coments !!!!

 Best Regards,

 Horacio Díaz-Requejo

Reply
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 01:06 AM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 01:06 AM

This was originally posted on APC forums on 7/28/2015


The "communication lost" can be caused by one of 3 things: 1) the NMC (safe to reboot while UPS has load); 2) the microcontroller board on the UPS (generally requires a complete power cycle on the UPS, so shut down the load devices first); 3) something else on the same communication bus (serial console, extended runtime packs (on some UPS models) or other expansion cards (in some UPS models).

So, if rebooting the NMC doesn't clear the problem, I'd do a remove/insert on the NMC as my next step. After that, you'd need to power cycle the UPS (and "dead" it - see APC knowlege base) if the problem persists.

If you have one of the UPS models with a fancy front panel (I'm not too familiar with recent products) there may be useful information available on the LCD display if the problem is on the UPS side.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc