Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Intermittent error - PowerChute cannot communicate with the Network Management Card.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Intermittent error - PowerChute cannot communicate with the Network Management Card.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5060
voidstar_apc
voidstar_apc
196
Teken
Teken
164
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
MRamsay_apc
MRamsay_apc
Explorer

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

0 Likes
7
2994
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

Intermittent error - PowerChute cannot communicate with the Network Management Card.

We have a newly installed APC Smart-UPS RT 5000 RM XL with a AP9631 NMC running version v6.4.0 firmware. We have PowerChute Network Shutdown 4.1.0.
Build 6428 running on a Windows 2012 R2 server. Both the NMC and PowerChute are on the same subnet.

Several times a day I see a log message "PowerChute cannot communicate with the Network Management Card" immediately followed by "Communication has been established". I ran a continuous ping from the PowerChute server to the NMC and checked it against when I was receiving the alerts and at no time did a ping to the NMC fail, despite having several of the above error messages logged.

Any idea how to reduce the sensitivity of PowerChute to this issue that clearly is not an issue? I have set up command files that email me when the various events are triggered so I am getting hit with numerous messages every day about the communications being re-established. I don't get an email message about the loss of communications because I set a 10 second delay on that, but I get a message immediately afterward that communications was re-established.

On another point, I was a little amazed that PowerChute could not natively send out emails for event triggers. The fact that I had to set up a series of command files that would send out customized email messages based on the various alerts is unheard of these days. No other management or monitoring package that I have at any of my clients can't send out an email with alert details. Time for APC to bring PowerChute into the 21st century and include email alerts!!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • cannot
  • communicate
  • PowerChute
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

0 Likes
0
2991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

I'm having the same thing in my logs during the day.

...

12/08/2016 11:15:06 Communication has been established.
12/08/2016 11:15:06 PowerChute cannot communicate with the Network Management Card.
12/08/2016 09:08:15 Communication has been established.
12/08/2016 09:08:15 Network Management Card cannot communicate with the UPS.

See Answer In Context

  • Tags:
  • cannot
  • card
  • communicate
  • log
  • management
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

0 Likes
0
2991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

Marc,

There is no way to adjust the sensitivity of PowerChute. PowerChute should only report lost comm to the NMC if it has not received a packet from the NMC for roughly 2 minutes. The NMC sends out a signal every 25 seconds informing PowerChute of its status. If PowerChute does not receive the packets it will post the lost comm error message. 

What is being recorded in the event log and in the error log?

On 8/18/2016 1:25 PM, Marc said:

On another point, I was a little amazed that PowerChute could not natively send out emails for event triggers. The fact that I had to set up a series of command files that would send out customized email messages based on the various alerts is unheard of these days. No other management or monitoring package that I have at any of my clients can't send out an email with alert details. Time for APC to bring PowerChute into the 21st century and include email alerts!!

We do not have any plans at this time to add an e-mail feature to PowerChute Network Shutdown. However, in the next version (4.2) we are including SNMP that will allow PowerChute to be monitored and configured. 

Reply

Link copied. Please paste this link to share this article on your social media post.

MRamsay_apc
MRamsay_apc
Explorer

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

0 Likes
0
2991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

Hi Bill,

Thank you for the prompt reply.

The PowerChute Event Log shows a series of 3 events. The first 2 are always showing the exact same time, and the third 10 seconds later:

18/08/2016 10:13:37 Running Command File.
18/08/2016 10:13:27 Communication has been established.
18/08/2016 10:13:27 PowerChute cannot communicate with the Network Management Card.

Where is the error log you are referring to?

The event log on the NMC is not showing any issues.

Marc

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

0 Likes
0
2991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

Marc,

If you install PowerChute to the default path the error log is in C:\Program Files\APC\PowerChute\group1

On 8/18/2016 3:53 PM, Marc said:

18/08/2016 10:13:27 Communication has been established.
18/08/2016 10:13:27 PowerChute cannot communicate with the Network Management Card.

The event log show the lose of communications and establishment simultaneously. 

Reply

Link copied. Please paste this link to share this article on your social media post.

MRamsay_apc
MRamsay_apc
Explorer

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

0 Likes
0
2991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

Thanks for the location Bill.

The error .txt file is clear except for an error dated back when Powerchute was being initially configured.

The EventLog.txt file shows what the web interface does. These are the errors for today so far:

22/08/2016 05:01:54 PowerChute cannot communicate with the Network Management Card. .3.5.1.5.6.5
22/08/2016 05:01:54 Communication has been established. .3.5.1.5.6.1
22/08/2016 05:02:04 Running Command File. .3.4.9.9
22/08/2016 11:10:39 PowerChute cannot communicate with the Network Management Card. .3.5.1.5.6.5
22/08/2016 11:10:39 Communication has been established. .3.5.1.5.6.1
22/08/2016 11:10:49 Running Command File. .3.4.9.9

As before, a continuous ping to the NMC does not show any interruptions in connectivity with the NMC.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

0 Likes
0
2991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

Marc,

How often is this happening? Is it daily or multiple times per day and is there any pattern to the occurrences? 

Reply

Link copied. Please paste this link to share this article on your social media post.

MRamsay_apc
MRamsay_apc
Explorer

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

0 Likes
0
2991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

Hi Bill;

Here is the log from yesterday. There are 8 occurrences and there is no pattern to the timing and it is typical of the days preceding it.

22/08/2016 05:01:54 PowerChute cannot communicate with the Network Management Card. .3.5.1.5.6.5
22/08/2016 05:01:54 Communication has been established. .3.5.1.5.6.1
22/08/2016 05:02:04 Running Command File. .3.4.9.9
22/08/2016 11:10:39 PowerChute cannot communicate with the Network Management Card. .3.5.1.5.6.5
22/08/2016 11:10:39 Communication has been established. .3.5.1.5.6.1
22/08/2016 11:10:49 Running Command File. .3.4.9.9
22/08/2016 11:54:01 PowerChute cannot communicate with the Network Management Card. .3.5.1.5.6.5
22/08/2016 11:54:01 Communication has been established. .3.5.1.5.6.1
22/08/2016 11:54:11 Running Command File. .3.4.9.9
22/08/2016 12:03:54 PowerChute cannot communicate with the Network Management Card. .3.5.1.5.6.5
22/08/2016 12:03:54 Communication has been established. .3.5.1.5.6.1
22/08/2016 12:04:04 Running Command File. .3.4.9.9
22/08/2016 12:12:55 PowerChute cannot communicate with the Network Management Card. .3.5.1.5.6.5
22/08/2016 12:12:55 Communication has been established. .3.5.1.5.6.1
22/08/2016 12:13:05 Running Command File. .3.4.9.9
22/08/2016 12:15:04 PowerChute cannot communicate with the Network Management Card. .3.5.1.5.6.5
22/08/2016 12:15:04 Communication has been established. .3.5.1.5.6.1
22/08/2016 12:15:14 Running Command File. .3.4.9.9
22/08/2016 12:36:07 PowerChute cannot communicate with the Network Management Card. .3.5.1.5.6.5
22/08/2016 12:36:07 Communication has been established. .3.5.1.5.6.1
22/08/2016 12:36:17 Running Command File. .3.4.9.9
22/08/2016 18:10:31 PowerChute cannot communicate with the Network Management Card. .3.5.1.5.6.5
22/08/2016 18:10:31 Communication has been established. .3.5.1.5.6.1
22/08/2016 18:10:41 Running Command File. .3.4.9.9

Thank you.

Marc

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

0 Likes
0
2991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

I'm having the same thing in my logs during the day.

...

12/08/2016 11:15:06 Communication has been established.
12/08/2016 11:15:06 PowerChute cannot communicate with the Network Management Card.
12/08/2016 09:08:15 Communication has been established.
12/08/2016 09:08:15 Network Management Card cannot communicate with the UPS.

  • Tags:
  • cannot
  • card
  • communicate
  • log
  • management
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore