Current UPSs won't stop server reboots. What equipment is reccommended?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Current UPSs won't stop server reboots. What equipment is reccommended?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

0 Likes
4
1752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

Current UPSs won't stop server reboots. What equipment is reccommended?

We're currently running four racks of servers and phone equipment in two of our buildings. Each rack has two rackmount SmartUPS 1400XLs (and a random Minuteman UPS) to keep everything up in the case of short power outages or brownouts, which are quite frequent here. Equipment is spread out across the multiple UPSs, all have good batteries, and none of them have loads showing more than 2-of-5 bars.

Problem is, our UPSs aren't switching over fast enough to stop the servers from blinking off and rebooting, and we then have to baby about half the servers back online, deal with corrupted databases, hardware failures, etc. We've hobbled through regular outages for a couple of years now, stalling till we were ready for a major equipment update. Most of the servers are being virtualized which will consolidate everything down to just one rack with three blades, some network storage equipment, and the phone system.

We're done with servers being knocked offline due to power. What should we be looking for as far as a replacement here, because all we really know is the APCs we have now are not what we need.

What should we be looking for here to get the best performance when we start ordering for the server room upgrade? Is there a best-value option for us? Are the new 1500s that much improved over the older 1400s we've got that just upgrading to the new model will take care of us? Or are we looking at retiring the SmartUPS for one of the Symmetra solutions?

Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

0 Likes
0
1754
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

I have some audio equipment from Meridian (not the same as Meridian phones), with extremely picky power supplies. Any sort of utility blip, regardless of duration and whether the UPS goes to battery or not, will cause the Meridian processor to shut down. This is on a Matrix 5000. There's a mechanical relay in the UPS (you can hear it when the UPS adjust taps or goes to battery) which produces a very brief dropout of less than one AC cycle (1/60th of a second).

Any decently designed power supply should be able to handle far more than a single AC cycle dropout. Meridian supplies are less than decent that way (there have been a number of "we suggest you visit your dealer to have your power supply upgraded - at your cost, of course" notices from Meridian).

In some cases this brief dropout is absolutely necessary - for example, on the APC Rackmount Automatic Transfer Switch, it HAS to be break-before-make when switching sources, as the 2 sources may not be phase-synchronized.

30 years or so ago, the "Continuous On-line UPS" was all the rage as it had 0 transfer delay (it always ran the load from the batteries - the AC input just charged the batteries). There were a lot of disadvantages to that design, and since then there have been many advances in UPS design which have been adopted by APC and others.

I'd check with Angela here to see which APC models have 0 transfer delay - I'm not up-to-date on APC's current product offerings (as you can tell by the fact that I'm running a Matrix 5000).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

0 Likes
0
1754
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

reading this my first question was "how do you know the actual problem is that the UPSs are not transferring fast enough?" are the servers doing a hard shutdown or rebooting during the transfer to battery and then shutting down?

are these configured for graceful shutdown with powerchute software? - this scenario could occur if you do not have any software or graceful shutdown software configured properly.

have you done a pull plug test or similar (pulling the plug on the UPS to see if it supports the load)?

any information in any log files? i wouldnt want to suggest something else until I knew the definite root cause to make sure we didnt get you something you didnt need or that would not fix the problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

0 Likes
0
1754
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

The supply not taking over fast enough is just a guess of ours. ('Cause that's what UPSs are supposed to do, right? ;D)

From watching them go down when we're present during a blip they appear to losing power, not just a reboot. They're shutting down hard then coming back up as soon as power is restored a moment later, no different than just flipping the switch on the PSU then back on again. (The logs don't have anything useful aside from a note that there was a shutdown due to power outage.) They do this on a "plug test" as well.

If the outage is more than a blip everything starts to come back online and it will run the servers till the batteries are drained, but at that point it doesn't matter. I thought it could be load-at-startup being too high but even the dedicated UPS running just the mail server and nothing else doesn't stop that moment of silence when every fan in the closet stops spinning at once. =/

Only a few if any of the servers would be running PowerChute, though. (I think the phone system is on a dedicated UPS with shutdown configured, since that one never comes back properly on its own. Can't verify from here at the moment, though.)

The software can make that much of a difference? That might be a place to start. We were under the impression that only mattered for configuring the sensitivity and audible warnings.

Message was edited by: Larva

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

0 Likes
0
1754
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

ok based on some of your comments, your guess sounds a bit more likely - the fact that they reboot during a long power outage but run on battery after they come back up (after the damage is done).

does this happen to every single UPS/server combination? Are the servers all the same model? does the UPS reboot at any point also (based on what you said I am guessing the answer is no)? one other thing i also might try is using a voltmeter on the UPS outlets (with maybe no load attached) and see if you see a disruption in output voltage during the switch to battery or if it is indeed just specific to your load (rather than an issue with the UPS hardware).

you mentioned a phone system. a lot of those do indeed require an "online" UPS which would be the Smart UPS RT line. if it is indeed the transfer time, you'd look at something like Smart UPS RT, Symmetra LX or Symmetra RM depending on requirements.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

0 Likes
0
1755
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:52 AM . Last Modified: ‎2024-03-13 01:17 AM

I have some audio equipment from Meridian (not the same as Meridian phones), with extremely picky power supplies. Any sort of utility blip, regardless of duration and whether the UPS goes to battery or not, will cause the Meridian processor to shut down. This is on a Matrix 5000. There's a mechanical relay in the UPS (you can hear it when the UPS adjust taps or goes to battery) which produces a very brief dropout of less than one AC cycle (1/60th of a second).

Any decently designed power supply should be able to handle far more than a single AC cycle dropout. Meridian supplies are less than decent that way (there have been a number of "we suggest you visit your dealer to have your power supply upgraded - at your cost, of course" notices from Meridian).

In some cases this brief dropout is absolutely necessary - for example, on the APC Rackmount Automatic Transfer Switch, it HAS to be break-before-make when switching sources, as the 2 sources may not be phase-synchronized.

30 years or so ago, the "Continuous On-line UPS" was all the rage as it had 0 transfer delay (it always ran the load from the batteries - the AC input just charged the batteries). There were a lot of disadvantages to that design, and since then there have been many advances in UPS design which have been adopted by APC and others.

I'd check with Angela here to see which APC models have 0 transfer delay - I'm not up-to-date on APC's current product offerings (as you can tell by the fact that I'm running a Matrix 5000).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore