Information on New SMART-UPS Firmware Subscription Plan

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Information on New SMART-UPS Firmware Subscription Plan
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
deees
Crewman deees
Crewman

Posted: ‎2024-01-02 05:12 AM

0 Likes
13
5131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-02 05:12 AM

Information on New SMART-UPS Firmware Subscription Plan

I recently received a notification of a new firmware version for the AP964x NMC. I downloaded the firmware deployment package to start testing it.

I was surprised to discover that in order to upgrade the firmware I have to enroll the NMC in a subscription plan, ($60/year.) I have ~350 UPS that I manage.

I've contacted my APC account manager to try to understand the full ramifications of this change in policy.

I also want to know what this new policy wasn't communicated to customer early enough to budget for this new cost?

I have dozens technical questions I need to have answer to.

Has anyone else obtained detail information regarding this new policy?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Kirk Teken
Kirk

Posted: ‎2024-01-03 09:00 AM

0 Likes
5
5072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-03 09:00 AM

Unless something has drastically changed from APC you can simply download the required firmware and load the same either through USB, Serial, NMC. If its true firmware will be hidden behind a pay wall shame on APC and its time to move on to another hardware vendor!

 

Whether that be Eaton, Vertiv, Tripp Lite, CyberPower . . . 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 13
dpierce4776
Lt. Commander dpierce4776
Lt. Commander

Posted: ‎2024-01-02 08:54 PM

0 Likes
2
5097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-02 08:54 PM

We don’t subscribe to that. You can simply download it and go

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-01-03 09:00 AM

0 Likes
5
5073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-03 09:00 AM

Unless something has drastically changed from APC you can simply download the required firmware and load the same either through USB, Serial, NMC. If its true firmware will be hidden behind a pay wall shame on APC and its time to move on to another hardware vendor!

 

Whether that be Eaton, Vertiv, Tripp Lite, CyberPower . . . 

Reply

Link copied. Please paste this link to share this article on your social media post.

deees
Crewman deees
Crewman

Posted: ‎2024-01-03 11:15 PM

In response to dpierce4776
0 Likes
1
5072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-03 11:15 PM

Thanks for responding.

>> You can simply download it and go

Could you elaborate?

Do you mean you download the version 3.x firmware and install it without a subscription?

Or do you mean you remain on version 2.x and upgrade through the previous methods?

Reply

Link copied. Please paste this link to share this article on your social media post.

dpierce4776
Lt. Commander dpierce4776
Lt. Commander

Posted: ‎2024-01-04 09:24 AM

In response to deees
0 Likes
0
5037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-04 09:24 AM

You should be able to download it from the web at either APC.com or SE.com. From there you can install it manually. Also APC makes data center expert which is a program that monitors all your APC devices. And will do other manufactures as well. they also have a website for getting DDF files for DCE free of charge so DCE can read and understand multiple devices. DCE also downloads and pushes out new firmware/

Reply

Link copied. Please paste this link to share this article on your social media post.

deees
Crewman deees
Crewman

Posted: ‎2024-01-04 10:35 PM

In response to Teken
0 Likes
3
5040
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-04 10:35 PM

Teken,

 

I accidently mark your response as a solution.

 

If you read my response to my own question, I explain that something did change:

 - The new SNS tool and firmware require a subscription.

 - Keeping the current 2.x firmware will allow customers to continue with the previous method.

Reply

Link copied. Please paste this link to share this article on your social media post.

Sherminator
Sherminator
Cadet

Posted: ‎2024-01-06 05:59 AM

In response to deees
0 Likes
2
4970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-06 05:59 AM

We're facing the same situation. We run a bunch of Smart UPS 3000 with AP9630 (which is deprecated), so we want to upgrade to AP9640. Today I installed the first one, and now the SNS says "Activate license to update". First I would like to know: If we want to buy these licenses, which is the correct one? I found FWENMC3P-ST1Y-DIGI, but this seems to be just for Easy UPS, not for Smart UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2024-01-08 07:36 AM

In response to Sherminator
1 Like
0
4958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-08 07:36 AM

The Schneider Electric Network Management Card 3 Secure NMC System FAQ discusses the changes to firmware distribution and lists the subscription SKUs.

https://download.schneider-electric.com/files?p_Doc_Ref=SPD_HEPN-BFRL57_EN&p_enDocType=Brochure&p_Fi...

Reply

Link copied. Please paste this link to share this article on your social media post.

deees
Crewman deees
Crewman

Posted: ‎2024-01-09 01:37 AM

In response to Sherminator
0 Likes
0
4923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-09 01:37 AM

Shermintor,

 

Just continue to use the 2.x version: https://download.schneider-electric.com/files?p_Doc_Ref=APC_NMC3_SU_2506_EN&p_enDocType=Firmware&p_F...

APC has promised to continue to support this code train with security and reliability updates. I couldn't find a linkable FAQ for the statement, but the text from the PDF is: "There is no impact to the features or functionality of the Network Management Card. Customers can continue to download the NMC3 firmware v2.5 from www.apc.com/secure-nmc. This firmware will remain available to support product warranty; therefore, in the event of a critical vulnerability or a defect which impacts the operation of the Network Management Card, an update addressing the vulnerability or defect will be made available."

 

I only care about security patches and basic stability. I'm still trying to get APC to confirm whether the computer running the SNS Tool can manage UPS NMC's that are on a different subnet/VLAN/WAN site?

Reply

Link copied. Please paste this link to share this article on your social media post.

Sherminator
Sherminator
Cadet

Posted: ‎2024-01-10 12:40 AM

0 Likes
1
4901
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-10 12:40 AM

Thanks so much for your support!

Upgrading to 2.5.0.8 worked, so for now we plan to stick on 2.x.

Reply

Link copied. Please paste this link to share this article on your social media post.

Chris_P
Crewman Chris_P
Crewman

Posted: ‎2024-01-10 08:36 AM

0 Likes
0
4887
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-10 08:36 AM

From a legal perspective you may find that if they do eventually stop you download FW unless you subscribe, you may have a case (depending on the country you are in).

 

If you need to update because the product is not working correctly as expected, then it is not a fully functioning product, as would be expected.

Reply

Link copied. Please paste this link to share this article on your social media post.

Sherminator
Sherminator
Cadet

Posted: ‎2024-01-12 02:46 AM

0 Likes
0
4865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-12 02:46 AM

Thanks for replying!

To be honest: For the moment we're fine with AP9640 and Firmware version 2.x. But our next project will be without APC. Paying for software updates (on an already not so cheap product) is a no go for us.

Reply

Link copied. Please paste this link to share this article on your social media post.

frank.virtualizen
frank.virtualizen
Cadet

Posted: ‎2024-09-20 03:23 PM

In response to Teken
0 Likes
0
3508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-20 03:23 PM

APC has changed. They now require subscription for firmware updates (which often are included for the first year). Alternatively, you can purchase APC's AI Management Tool EcoStruxure IT Expert which includes firmware updates among many significant value propositions. Feel free to reach out to me for more information. We're an APC Elite Partner.

Reply

Link copied. Please paste this link to share this article on your social media post.

npereira
Crewman npereira
Crewman

Posted: ‎2025-03-06 12:26 PM

In response to Sherminator
0 Likes
0
2368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-06 12:26 PM

Hi, i need firmare version  AOS 2.5.0.8 , but i cant find it , do you have firmware ? do you can share ?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore