Is there a line in the INI file for enabling System Name Synchronization? I haven't seen it, but I may be overlooking it.
Thanks,
Jeff
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:04 AM . Last Modified: 2024-03-08 04:35 AM
Hi Jeff,
System/Host name synchronization is not currently in the INI file. We have an open feature request created for the development team, but there is no ETA for if/when it would be added. I'll make sure to update it with this forum post, so we can see that customers are requesting it!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:04 AM . Last Modified: 2024-03-08 04:35 AM
Hi Jeff,
System/Host name synchronization is not currently in the INI file. We have an open feature request created for the development team, but there is no ETA for if/when it would be added. I'll make sure to update it with this forum post, so we can see that customers are requesting it!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 04:04 AM . Last Modified: 2024-03-08 04:35 AM
Matt.
Thanks for the response. I am in the process of configuring UPS's and NIC's for a new plant. It's a pain to be able to configure everything except one item.
Jeff
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-07-21 09:49 AM
Almost a year later and I don't think the feature was added.
you can turn on the synchronization through SSH.
The command to enable the synch is:
apc>dns -y enable
E000: Success
I do this on my python script to make sure all UPS are synched