I have an AP9618 UPS monitor card I can not ping

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • I have an AP9618 UPS monitor card I can not ping
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 03:45 AM . Last Modified: ‎2024-03-05 10:49 PM

0 Likes
6
2268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:45 AM . Last Modified: ‎2024-03-05 10:49 PM

I have an AP9618 UPS monitor card I can not ping

I can connect to the card using the browser, via TELNET and FTP however ping fails to obtain a response. It acts as if ICMP is disabled, however I can not find that setting anywhere. Firmware is 3.7.2 which appears to be the latest. Any ideas on how to resolve this? I want to add the card to HP SIM so I can receive traps from the card, but I can not add it if ping fails.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9617
  • apc
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:46 AM . Last Modified: ‎2024-03-05 10:49 PM

0 Likes
0
2268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:46 AM . Last Modified: ‎2024-03-05 10:49 PM

The only other thing you could try which I don't think will help is a reset to defaults. If you want to dig deeper too, we could check a packet capture as well.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-07-01 03:45 AM . Last Modified: ‎2024-03-05 10:49 PM

0 Likes
0
2268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:45 AM . Last Modified: ‎2024-03-05 10:49 PM

I should add that the card is configured with a static IP, gateway and mask.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:45 AM . Last Modified: ‎2024-03-05 10:49 PM

0 Likes
0
2268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:45 AM . Last Modified: ‎2024-03-05 10:49 PM

Did you reboot it yet?

So no hardware OR software firewalls, malware prevention, etc in the mix either.. The other thing after a reboot I would try if you could is a crossover connection and try to ping it (and maybe try one or two machines to rule out anything on one specific machine you might not be aware of) but beyond that, my gut tells me something is blocking it or the echo request is so slow that it is timing out since was we already noted, AP9618 does not support the ability to block ICMP requests.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 03:45 AM . Last Modified: ‎2024-03-05 10:49 PM

0 Likes
0
2268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:45 AM . Last Modified: ‎2024-03-05 10:49 PM

It has been rebooted several times before. The card responds quickly to all other requests, FTP, Telnet and HTTP.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 03:45 AM . Last Modified: ‎2024-03-05 10:49 PM

0 Likes
0
2268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:45 AM . Last Modified: ‎2024-03-05 10:49 PM

I can connect to the card using the browser, via TELNET and FTP however ping fails to obtain a response. It acts as if ICMP is disabled, however I can not find that setting anywhere. Firmware is 3.7.2 which appears to be the latest. Any ideas on how to resolve this? I want to add the card to HP SIM so I can receive traps from the card, but I can not add it if ping fails.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:45 AM . Last Modified: ‎2024-03-05 10:49 PM

0 Likes
0
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:45 AM . Last Modified: ‎2024-03-05 10:49 PM

Is it possible ICMP is blocked on your network or do other APC Network Management Cards that do respond on the same network? And you're right - only the AP9630/31/35 cards have the option to disable the ICMP IPv4 response for security. The AP9618 does not support this.

Also, via telnet, there is a ping utility. I am just curious if it can ping your HP SIM.

Lastly, if none of this works or you're not sure, have you tried to reboot the card?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:46 AM . Last Modified: ‎2024-03-05 10:49 PM

0 Likes
0
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:46 AM . Last Modified: ‎2024-03-05 10:49 PM

The only other thing you could try which I don't think will help is a reset to defaults. If you want to dig deeper too, we could check a packet capture as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore