Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

Email alarm via SMTP from PowerChute Bussiness Agent

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Email alarm via SMTP from PowerChute Bussiness Agent
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:46 AM

0 Likes
11
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:46 AM

Email alarm via SMTP from PowerChute Bussiness Agent

This question was originally posted by ngthanhluan on APC forums on 6/12/2013


Hi everybody,

I'm a new user and could you please check for me this trouble smile

I have just bought UPS APC version SUA 1000i

I deploy it in to my network by connect it with PC 1 (which installed PowerChute Bussiness Agent). Can I use this PC 1 to sent email alarm for this UPS via SMTP ? 

I have SMTP server and I fill all information in Menu Change configuration list (in PowerChute Bussiness Console which installed in PC2). But i don't know why it doesn't work (fail in test email).

Our printer laserjet 3010/3015 still can sent email alarm normal via SMTP. Did I miss something ? 

I’m using PowerChute version 9.0.2, Windows 7. I don't have Network Management card.

Thanks and best regrads

Luan.


Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:46 AM

0 Likes
0
640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:46 AM

This reply was originally posted by ngthanhluan on APC forums on 6/13/2013


Thank for your support !

I think the SMTP Server is working normality. Because the HP printer still sending email alarm for me when it has a trouble. We are using same setting like you said, Angela. Port 25 and didn't use SSL.

The question here is; With connect via USB, can UPS SUA1000i can sent email alarm by the computer which installed PCBE (agent version) ?

Here is my topology:

- UPS SUA1000i connected by USB cable with PC 1 ( Installed PCBE agent)

- PC 2 Install PCBE Console and Server to Monitoring all UPS. (This PC isn't SMTP Server)

- Via PCBE (agent) PC1  can read all data of this UPS, and PC 2 via PCBE Console can read from so can this Computer.

- Please remember that i don't have Network Managerment Card for this UPS. I don't have permission change anything in SMTP Server, too.

Here is my configure in Profile (PCBE Console and Server)

1235_UPS.jpg

Here is information received from PC install PCBE Agent.

1237_UPS2.png

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:46 AM

0 Likes
0
640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:46 AM

This reply was originally posted by ngthanhluan on APC forums on 6/18/2013


Yes, i found the reason.

Symantec Endpoint Protection denied the email sent from Agent to Console.

When i set the email from SMTP passing Symantec, i got the mail alarm smile

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:46 AM

0 Likes
0
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:46 AM

This reply was originally posted by ngthanhluan on APC forums on 6/13/2013


Thank for your support !

I think the SMTP Server is working normality. Because the HP printer still sending email alarm for me when it has a trouble. We are using same setting like you said, Angela. Port 25 and didn't use SSL.

The question here is; With connect via USB, can UPS SUA1000i can sent email alarm by the computer which installed PCBE (agent version) ?

Here is my topology:

- UPS SUA1000i connected by USB cable with PC 1 ( Installed PCBE agent)

- PC 2 Install PCBE Console and Server to Monitoring all UPS. (This PC isn't SMTP Server)

- Via PCBE (agent) PC1  can read all data of this UPS, and PC 2 via PCBE Console can read from so can this Computer.

- Please remember that i don't have Network Managerment Card for this UPS. I don't have permission change anything in SMTP Server, too.

Here is my configure in Profile (PCBE Console and Server)

1235_UPS.jpg

Here is information received from PC install PCBE Agent.

1237_UPS2.png

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:46 AM

0 Likes
0
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:46 AM

This reply was originally posted by ngthanhluan on APC forums on 6/13/2013


Hi,

Where did you configure the e-mail settings? In the web interface or in the Server service and when the test fails where are you running the test from?

I configure the email setting in PowerChute Bussiess Edition Server and Console.


The configure you can check in the last i reply.


After i configured, i test by Test button in Console program and results is Fail.

Note: I don't have permission to change anything on SMTP Server.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:46 AM

0 Likes
0
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:46 AM

This reply was originally posted by ngthanhluan on APC forums on 6/12/2013


Hi everybody,

I'm a new user and could you please check for me this trouble smile

I have just bought UPS APC version SUA 1000i

I deploy it in to my network by connect it with PC 1 (which installed PowerChute Bussiness Agent). Can I use this PC 1 to sent email alarm for this UPS via SMTP ? 

I have SMTP server and I fill all information in Menu Change configuration list (in PowerChute Bussiness Console which installed in PC2). But i don't know why it doesn't work (fail in test email).

Our printer laserjet 3010/3015 still can sent email alarm normal via SMTP. Did I miss something ? 

I’m using PowerChute version 9.0.2, Windows 7. I don't have Network Management card.

Thanks and best regrads

Luan.


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:46 AM

0 Likes
0
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:46 AM

This reply was originally posted by Angela on APC forums on 6/12/2013


what SMTP service are you trying to use? Email in PCBE requires port 25 and it cannot be changed. PCBE also does not support email authentication using SSL, only plain text. Some of those items may prevent mail from sending properly if not taken into account.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:46 AM

0 Likes
0
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:46 AM

This reply was originally posted by Bill on APC forums on 6/13/2013


Hi,

I tested using the the from e-mail info you listed in your screenshots and the mail failed because the domain information is missing.

Thu Jun 13 09:10:36 EDT 2013: [SMTPMailWorker.transmitMailMessage()]- Send Mail Failed: javax.mail.internet.AddressException: Missing domain in string ``do_not_reply@''

Thu Jun 13 09:10:36 EDT 2013: [SMTPMailWorker.makeTestMessage()]- Failed to send test email message.

You need to enter the domain info for the to address and the from address. If you would like to check the error log, assuming you installed to the default path go to C:\Program Files\APC\PowerChute Business Edition\server. The error info is stored in debug.txt.




Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:46 AM

0 Likes
0
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:46 AM

This reply was originally posted by ngthanhluan on APC forums on 6/14/2013


Wed Jun 12 10:23:42 ICT 2013: [SMTPMailWorker.makeTestMessage()]- Failed to send test email message.

Wed Jun 12 10:24:12 ICT 2013: [SMTPMailWorker.transmitMailMessage()]- Send Mail Failed: javax.mail.MessagingException: Exception reading response; nested exception is: java.net.SocketTimeoutException: Read timed out

Here is information store in file debug.txt. Sorry because i cant't fill the domain behide @ so you can't test smile

Would you mind explain for me: With connect via USB, can UPS SUA1000i can sent email alarm by the computer which installed PCBE (agent version) ?


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:46 AM

0 Likes
0
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:46 AM

This reply was originally posted by Bill on APC forums on 6/14/2013


The error you are seeing means that PowerChute has sent the e-mail and timed out waiting for a response. That indicates that either the server cannot communicate with the SMTP server or the SMTP server cannot communicate with the system PowerChute is running on. You can test to see if the system can communicate with the SMTP server by typing the IP address of the SMTP mail server and type in the # 25 in the Port Name field, then press connect.

  Windows system

1. Go to Start | Run

2. Type Telnet

3. Type Open 10.72.5.185 25

If this fails, your SMTP server is not properly configured or does not accept connections on port 25. As Angela wrote earlier PowerChute requires port 25 and it cannot be changed and PowerChute does not support email authentication using SSL, only plain text.


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:46 AM

0 Likes
0
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:46 AM

This reply was originally posted by ngthanhluan on APC forums on 6/17/2013


Yes, everything config ok, i'm so sure about SMTP server. it is working normal.

Look like i must check the destination of data from client to server SMTP. Thanks for your support.  !!!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:46 AM

0 Likes
0
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:46 AM

This reply was originally posted by ngthanhluan on APC forums on 6/17/2013


I ping and tracert to IP of SMTP Server, here is a result

1243_Tracert.jpg

Time is good enough for send and recived email. I think something wrong in my config ... Haiz

This is test sent email by telnet. The result is the same. error ...

1244_SMTP.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:46 AM

0 Likes
0
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:46 AM

This reply was originally posted by ngthanhluan on APC forums on 6/17/2013


1246_Test.jpg

Today, i recive a mail from 10.72.5.185 with the reports like that. But when i try to shutdown the electric for UPS run on UPS, it didn't sent email for me.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:46 AM

0 Likes
0
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:46 AM

This reply was originally posted by ngthanhluan on APC forums on 6/18/2013


Yes, i found the reason.

Symantec Endpoint Protection denied the email sent from Agent to Console.

When i set the email from SMTP passing Symantec, i got the mail alarm smile

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc