I can't find description of few OIDs as part of PowerNet-MIB::rPDULoadStatusLoad
Hi,
I did look at the PowerNet MIB but I can't see description of:
PowerNet-MIB::rPDULoadStatusLoad.1 = Gauge32: 0
PowerNet-MIB::rPDULoadStatusLoad.2 = Gauge32: 0
PowerNet-MIB::rPDULoadStatusLoad.3 = Gauge32: 0
What is the meaning of 1,2 and 3? Are those banks? If yes which ones? What is 3 for example on a dual bank AP7832 but most of all I would like to know the source which explains those since it isn't in the MIB?
Thank you
~B
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:46 PM . Last Modified: 2024-03-18 11:53 PM
Hi Boyan,
Check out this knowledge base article and let us know if you need anything further than what it explains-> http://www.apc.com/us/en/faqs/FA156142 The 1, 2, and 3 refer to instances as mentioned in the knowledge base article itself.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:46 PM . Last Modified: 2024-03-18 11:53 PM
Thank you very much Angela; in my case (AP7832 single phase, dual bank) the answer was:
Single Phase Multibank PDU
Instance 2: Total Current on Bank 1
Instance 3: Total Current on Bank 2
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:46 PM . Last Modified: 2024-03-18 11:53 PM
Hi Boyan,
Check out this knowledge base article and let us know if you need anything further than what it explains-> http://www.apc.com/us/en/faqs/FA156142 The 1, 2, and 3 refer to instances as mentioned in the knowledge base article itself.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:46 PM . Last Modified: 2024-03-18 11:53 PM
Thank you very much Angela; in my case (AP7832 single phase, dual bank) the answer was:
Single Phase Multibank PDU
Instance 2: Total Current on Bank 1
Instance 3: Total Current on Bank 2