cooling system InRow RD shuts down many times in a day

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • cooling system InRow RD shuts down many times in a day
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:45 PM . Last Modified: ‎2024-03-18 11:54 PM

0 Likes
7
3586
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:45 PM . Last Modified: ‎2024-03-18 11:54 PM

cooling system InRow RD shuts down many times in a day

Hello everyone.

The issue is I manage a cluster with a cooling system InRow and the cooling shuts down several times in a day, that causes the temperature to rise too in a few minutes. When the cooling goes off I have to turn it on and it works again. Do you have any idea what cause this ?

The cooling has these 3 warnings:

1 - cooling failure no longer exists.

2 - supply air high temperature violation.

3 - persistent low suction pressure.

I'm sorry about the questions, I'm new in this I hope you understand.

Thanks for your quick answers guys.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • cluster
  • cooling
  • datacenter
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:46 PM . Last Modified: ‎2024-03-18 11:53 PM

0 Likes
0
3585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:46 PM . Last Modified: ‎2024-03-18 11:53 PM

Hi everyone !

We contacted to an air conditioning company in our city and they made us maintain the external compressor (which was very dirty). This eliminated the suction alarms and values are already within a normal range, so the problem was solved.

Thank you were very helpfull

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:46 PM . Last Modified: ‎2024-03-18 11:53 PM

0 Likes
0
3585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:46 PM . Last Modified: ‎2024-03-18 11:53 PM

Hello Rick.

The low suction pressure alarm is what is causing this unit to shut down. Do you know what the pressures are (discharge and suction) and what the superheat is on the unit? These can be found under detailed status in the unit tab on the web interface or under view unit status from the front screen. Something is causing the unit to go into low suction which will turn off the cooling.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:46 PM . Last Modified: ‎2024-03-18 11:53 PM

0 Likes
0
3585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:46 PM . Last Modified: ‎2024-03-18 11:53 PM

Hi, thanks for answering.

today the cluster was turned off all day because this problem, I've seen the discharge pressure is 2380 Kpa and the suction pressure is 672 Kpa, these values with the cluster turned off and the cooling system working alone.

Could you tell me what is the range of normal suction and discharge pressure ?. I'll turn on the cluster again to see the new pressure values.

Thanks a lot for your answers.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:46 PM . Last Modified: ‎2024-03-18 11:53 PM

0 Likes
0
3585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:46 PM . Last Modified: ‎2024-03-18 11:53 PM

Hello Rick. The suction pressure should be between 850-1000 Kpa and the discharge between 2350-2800 Kpa. You are reading low on the suction. This would need to be checked out by a HVAC tech to see if there are any leaks or blockages in the refrigerant system.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:46 PM . Last Modified: ‎2024-03-18 11:53 PM

0 Likes
0
3585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:46 PM . Last Modified: ‎2024-03-18 11:53 PM

Thanks for the support, I'll do it to solve the problem. You were very helpfull, thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:46 PM . Last Modified: ‎2024-03-18 11:53 PM

0 Likes
0
3585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:46 PM . Last Modified: ‎2024-03-18 11:53 PM

There are twelve InRow ACRD502 in our data center.

The suction pressure is about 650 Kpa for all of them, even just after refrigerant charging. Is it normal?

We have no "low suction pressure" alarms, the discharge pressure is 1600-1700 Kpa.

Thanks.

  • Tags:
  • acrd502
  • suction
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:46 PM . Last Modified: ‎2024-03-18 11:53 PM

0 Likes
0
3585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:46 PM . Last Modified: ‎2024-03-18 11:53 PM

Hello Andrej. The ACRD502 uses refrigerant 407C, which have lower pressures then the ACRD100, which uses refrigerant 410A. The ACRD502 will run suction pressures between 70-95 PSI (480-655 KPa) and discharge pressures between 220-280 PSI (1500-1900 KPa) depending on the load and the time of year. Your units are running correct pressures for the refrigerant they use. The 410A refrigerant runs higher pressures so 650 KPa would be low for those units.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:46 PM . Last Modified: ‎2024-03-18 11:53 PM

0 Likes
0
3586
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:46 PM . Last Modified: ‎2024-03-18 11:53 PM

Hi everyone !

We contacted to an air conditioning company in our city and they made us maintain the external compressor (which was very dirty). This eliminated the suction alarms and values are already within a normal range, so the problem was solved.

Thank you were very helpfull

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of