Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:27 AM . Last Modified: 2024-03-13 05:33 AM
I charge the batteries of my unit (model no sua3000 ) to full. When the unit ran on batteries(26.1v and 26.3v)
it discharges quickly (5minutes) and trips off. i have change the batteries the problem still persist. PLEASE CAN SOME ONE HELP!!!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:27 AM . Last Modified: 2024-03-13 05:33 AM
The LEDs on the front of the UPS during this entire timeline indicate full bar. the batteries, although not new worked for other 3KVA UPS.When this particular 3KVA unit run on the batteries the run time is less than 5minutes and trips off. WHAT IS THE FAULT. PLEASE REPLY
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:27 AM . Last Modified: 2024-03-13 05:33 AM
are these new batteries? are they geniune APC batteries? how did you charge them? are there any LEDs on the front of the UPS during this entire timeline? do you have any network management card or APC software attached to the UPS for monitoring? what was happening before you charged or replaced the batteries? were you fixing a different problem?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:27 AM . Last Modified: 2024-03-13 05:33 AM
The LEDs on the front of the UPS during this entire timeline indicate full bar. the batteries, although not new worked for other 3KVA UPS.When this particular 3KVA unit run on the batteries the run time is less than 5minutes and trips off. WHAT IS THE FAULT. PLEASE REPLY
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.