Shutdown pysical host which runs PCNS for virtualization

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Shutdown pysical host which runs PCNS for virtualization
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
139
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

0 Likes
3
774
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

Shutdown pysical host which runs PCNS for virtualization

Hello to all,

on our network I have a Smart-UPS X 3000, which powers 3 physical machines.

Two of them belong to a small VMware Datacenter, the other is a Windows fileserver.

To make sure, each and any guest and at last both VMware hosts are shut down,

I installed PCNS (4.1) for virtualization on the physical Windows machine.

From this one I can connect to the vCenter VM which hopefully will send the whole VMware stuff to sleep, when initiaded.

The thing I'm puzzled about: what will happen to my Windows machine after the VMware environ is shut down ?

I didn't find an option, where to configure the shutdown for the host itself, that runs PCNS.

Did I oversee anything or do I have to install both PCNS applications on one machine ?

Any help is appreciated

Regards  R.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

0 Likes
0
773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

Hi,

Is PowerChute set up with 3 redundant UPS? If so this configuration is listed on page 3 of Application Note 180. What will happen is after the host are powered down PowerChute will command the Windows system to power down automatically. 

If each system is connected to an individual UPS then the Windows system running PowerChute will be powered down after the VMware host if all UPS are on battery. See page 6 of Application Note 180 for an example and explanation. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

0 Likes
0
774
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

Hi,

Is PowerChute set up with 3 redundant UPS? If so this configuration is listed on page 3 of Application Note 180. What will happen is after the host are powered down PowerChute will command the Windows system to power down automatically. 

If each system is connected to an individual UPS then the Windows system running PowerChute will be powered down after the VMware host if all UPS are on battery. See page 6 of Application Note 180 for an example and explanation. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

0 Likes
0
773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

Hello Bill,

it's just a single UPS, which powers all three servers.

Nevertheless, the Application Note recommended by you covers this scenario too and explains how to configure.

Thank you very much for providing the needed information !

In our case everything already would've worked

but it puzzled me, there was nothing in the configuration which pointed to the shutdown of the Windows host, running PCNS.

Just to put it clear: it will be shut down but there's no time interval with the need to configure as this is hardcoded inside the program ?

Regards  R.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

0 Likes
0
773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

On 12/10/2015 7:31 AM, R. said:

Just to put it clear: it will be shut down but there's no time interval with the need to configure as this is hardcoded inside the program ?

Yes.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore