General APC SU/SUA1500 behavior question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • General APC SU/SUA1500 behavior question
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:34 AM

0 Likes
3
920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:34 AM

General APC SU/SUA1500 behavior question

Hi Everyone,

I have some basic UPS questions - I'm hoping people in the forums here can set me straight. I have about 200 APC UPS units - 75% of them are SU/SUA1500s so let's assume this is the only model I'm referring to.

We track UPS health via NMC /SNMP but every now and then we'll miss a bad battery and a UPS will fail. I'm assuming we have a bad battery, and then when the self-test runs it kills the battery and the UPS unit shuts down. When we swap the battery the APC powers back up just fine. Is this by design? A dead/missing battery during a self test means the UPS should power off?

Why doesn't the APC switch to bypass mode whenever possible? Even if the battery is completely dead but there is commercial power, shouldn't the UPS provide pass-through power? If it's supposed to this isn't what I'm seeing. Is bypass mode only if the UPS is overloaded, has an internal fault, or if I'm hot swapping a battery?

We have redundancy UPS units/power supplies on our server setups but for network equipment it's always a point of failure.

Thanks!
Mike

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

0 Likes
0
920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

Doesn't the self-test put a load on the battery? I was theorizing failing (at least) two self-tests in a row was causing the issue. If a battery is completely dead (0v) and a self-test runs, won't the UPS shut down when it transfers over during the test?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:34 AM

0 Likes
0
920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:34 AM

hi mike,

that particular model does not have an autobypass. generally any of the Smart UPS RT have at a minimum an automatic bypass or even a manual bypass. larger UPSs, such as Symmetra single phase and all three phase units have a bypass as well.

the self test is supposed to put the UPS on battery every so often in order to measure the voltage drop against an internal table. if it is out of range, then it illuminates the replace battery LED. ideally, yes, it should try to warn you and tell you to replaced the battery based on this test about a month ahead of time before its totally "toast." i think for different reasons such as battery environment, heat, unforseen failures, this does not happen and you see the behavior that you mentioned. i am not sure of the granular detail of what causes this but it does happen once in a while. this particular unit does not have a bypass so rarely it can drop the load during a self test or power outage where the battery is faulty.

how old are the batteries that you see this on? i hope it'd only happen on older batteries of 3+ years because if its happening sooner, there may be an environmental issue causing the batteries to not last as long as they should.

one other thing, that particular model uses a line interactive UPS topology which means the inverter is not always online providing output to the load so if there is another issue with the transfer to battery, the load may see a slight 2-6ms delay (most modern power supplies can handle a 15-20ms transfer no problem) and cause this type of issue too.

hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:34 AM

0 Likes
0
920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:34 AM

Appreciate all your info!

It's definately a battery age issue, I actually have about 200 APCs that I'm monitoring with NMCs but about another 200 or so that aren't monitored whatsoever (lucky to get a visual inspection!).

Looking at my procurement system here at work, I have these two models that are the right size for my wiring closets:
APC Smart-UPS 1000VA LCD 120V
APC Smart-UPS 2200VA LCD 120V

The docs don't seem to indicate these have bypass either - so if these newer models have a failed battery that goes undetected by my team, will they still eventually power down like the scenario I'm having right now? I assume neither of these has online inverters either?

What's the lowest end APC that supports auto bypass when a failed battery has been sitting for a long period of time? Just curious, I don't think it makes sense in my situation as my infrastructure is so spread out.

Thanks for your help!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

0 Likes
0
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:27 AM . Last Modified: ‎2024-03-13 05:33 AM

Doesn't the self-test put a load on the battery? I was theorizing failing (at least) two self-tests in a row was causing the issue. If a battery is completely dead (0v) and a self-test runs, won't the UPS shut down when it transfers over during the test?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore