Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

How using PowerChute Business Edition to shut any pc's

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How using PowerChute Business Edition to shut any pc's
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 12:34 AM

0 Likes
3
383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 12:34 AM

How using PowerChute Business Edition to shut any pc's

This question was originally posted by Guilherme on APC forums on 8/18/2011


hello, i has using the PowerChute Business Edition, but i can't shutdown the machines, exemple:
i'm try using the following script
@START "" "C:\Program Files (x86)\APC\PowerChute Business Edition\agent\cmdfiles\myShut.bat"

Inside the file myshut.bat have this script: shutdown /s /m
myPC /d 1:1 /f /t 60
i did try without the tag @START only shutdown /s /m
myPC /d 1:1 /f /t 60, but with the application PowerChute B. doesn't execute the .bat .
I have 3 server on this no-break and i didn't turn off him.
Someone can help?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
britney12_apc
Crewman britney12_apc
Crewman

Posted: ‎2021-07-01 12:34 AM

0 Likes
0
383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 12:34 AM

This was originally posted on APC forums on 8/22/2011


An APC UPS which supports the use of an APC Network Management Card (NMC). This currently includes any Smart-UPS UPS with a card slot or an embedded NMC, any Smart-UPS DP UPS, any Matrix-UPS UPS with a firmware revision of Y or later, any Symmetra UPS, and any Silcon Series UPS.

An APC Network Management Card (APC part number AP9617, AP9618 or AP9619) with a firmware revision of 1.1.0 or later OR an APC Web/SNMP Card (APC part number AP9606). If you are also using an APC Environmental Monitoring Card (APC part number AP9612TH), your Network Management Card must have firmware revision 1.1.5 or greater.

You can update your APC NMC firmware from the APC Web site.

PowerChute Network Shutdown cannot be used with APC PowerNet SNMP Adapters (cards). If your card has an APC part number of AP9605, AP9205, or AP9603, contact APC support or your APC dealer to upgrade the card.

If you are using multiple Smart-UPS devices, multiple Symmetra devices, or have a Parallel Silcon UPS system, you use one NMC in each UPS in the system. If your NMC has firmware revision 1.2.0 or later, be sure that the Synchronization option is disabled.
Note: AP9606 is only supported with single Smart-UPS, Matrix, Symmetra, or Silcon and Parallel Silcon configurations. It is not supported with either a multiple Smart-UPS or multiple Symmetra configuration.

A supported operating system as listed on the APC Web site.

The IP address for each APC Network Management Card.

A Java Virtual Machine (JVM), version 1.4.2 or later, on your server for all operating systems except NetWare (see two paragraphs down).

You can download a Java Virtual Machine from http://java.sun.com. PCNS installs JVM 1.4.2 if the most recent version found on your system is less than this (the rpm installer for VMWare is an exception to this, see Bare Metal Installation and Configuration with VMware ESX Server). If a JVM version greater than 1.4.2 is found on your system, PCNS will use the later version.

On Novell NetWare, both JVM 1.4.1 and 1.4.2 are supported. (NetWare 6 has JVM 1.3.1). Novell JVM 1.4.1 and 1.4.2 are available on Novell's Web site.

If you are installing PowerChute Network Shutdown on more than 50 computers powered by the same UPS, read the document "PowerChute Network Shutdown with more than 50 computers on one UPS" before continuing the installation. To obtain the document, go to the Software Downloads page on the APC Web site and select PowerChute Network Shutdown.

If you have a Parallel Silcon UPS, read the document "PowerChute Network Shutdown with a Parallel Silcon UPS System" before continuing the installation. To obtain the document, go to the Software Downloads page on the APC Web site and, select PowerChute Network Shutdown for Windows - Parallel Silcon Configuration Guide.

If you are installing on a multiple Smart-UPS or multiple Symmetra configuration, see Running a Multiple Configuration (Smart-UPS and Symmetra).

A monitor with a minimum resolution of 800 x 600; however, 1024 x 768 or greater is recommended.

If you are using a firewall, the http port used by the Network Management Card (default:80/TCP), and port 3052 (TCP and UDP) must be open for communication with the NMC.

You must have Administrator privileges on the network.


Overseas consultants in India

See Answer In Context

Reply
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 12:34 AM

0 Likes
0
383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 12:34 AM

This reply was originally posted by Angela on APC forums on 8/18/2011


i'd start here -> http://nam-en.apc.com/app/answers/detail/a_id/7712

my main question would be does your script work correctly if you run it outside of PCBE? assuming so, just double check that kbase i posted.

Reply
britney12_apc
Crewman britney12_apc
Crewman

Posted: ‎2021-07-01 12:34 AM

0 Likes
0
383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 12:34 AM

This was originally posted on APC forums on 8/22/2011


An APC UPS which supports the use of an APC Network Management Card (NMC). This currently includes any Smart-UPS UPS with a card slot or an embedded NMC, any Smart-UPS DP UPS, any Matrix-UPS UPS with a firmware revision of Y or later, any Symmetra UPS, and any Silcon Series UPS.

An APC Network Management Card (APC part number AP9617, AP9618 or AP9619) with a firmware revision of 1.1.0 or later OR an APC Web/SNMP Card (APC part number AP9606). If you are also using an APC Environmental Monitoring Card (APC part number AP9612TH), your Network Management Card must have firmware revision 1.1.5 or greater.

You can update your APC NMC firmware from the APC Web site.

PowerChute Network Shutdown cannot be used with APC PowerNet SNMP Adapters (cards). If your card has an APC part number of AP9605, AP9205, or AP9603, contact APC support or your APC dealer to upgrade the card.

If you are using multiple Smart-UPS devices, multiple Symmetra devices, or have a Parallel Silcon UPS system, you use one NMC in each UPS in the system. If your NMC has firmware revision 1.2.0 or later, be sure that the Synchronization option is disabled.
Note: AP9606 is only supported with single Smart-UPS, Matrix, Symmetra, or Silcon and Parallel Silcon configurations. It is not supported with either a multiple Smart-UPS or multiple Symmetra configuration.

A supported operating system as listed on the APC Web site.

The IP address for each APC Network Management Card.

A Java Virtual Machine (JVM), version 1.4.2 or later, on your server for all operating systems except NetWare (see two paragraphs down).

You can download a Java Virtual Machine from http://java.sun.com. PCNS installs JVM 1.4.2 if the most recent version found on your system is less than this (the rpm installer for VMWare is an exception to this, see Bare Metal Installation and Configuration with VMware ESX Server). If a JVM version greater than 1.4.2 is found on your system, PCNS will use the later version.

On Novell NetWare, both JVM 1.4.1 and 1.4.2 are supported. (NetWare 6 has JVM 1.3.1). Novell JVM 1.4.1 and 1.4.2 are available on Novell's Web site.

If you are installing PowerChute Network Shutdown on more than 50 computers powered by the same UPS, read the document "PowerChute Network Shutdown with more than 50 computers on one UPS" before continuing the installation. To obtain the document, go to the Software Downloads page on the APC Web site and select PowerChute Network Shutdown.

If you have a Parallel Silcon UPS, read the document "PowerChute Network Shutdown with a Parallel Silcon UPS System" before continuing the installation. To obtain the document, go to the Software Downloads page on the APC Web site and, select PowerChute Network Shutdown for Windows - Parallel Silcon Configuration Guide.

If you are installing on a multiple Smart-UPS or multiple Symmetra configuration, see Running a Multiple Configuration (Smart-UPS and Symmetra).

A monitor with a minimum resolution of 800 x 600; however, 1024 x 768 or greater is recommended.

If you are using a firewall, the http port used by the Network Management Card (default:80/TCP), and port 3052 (TCP and UDP) must be open for communication with the NMC.

You must have Administrator privileges on the network.


Overseas consultants in India

Reply
britney12_apc
Crewman britney12_apc
Crewman

Posted: ‎2021-07-01 12:34 AM

0 Likes
0
384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 12:34 AM

This was originally posted on APC forums on 8/22/2011


An APC UPS which supports the use of an APC Network Management Card (NMC). This currently includes any Smart-UPS UPS with a card slot or an embedded NMC, any Smart-UPS DP UPS, any Matrix-UPS UPS with a firmware revision of Y or later, any Symmetra UPS, and any Silcon Series UPS.

An APC Network Management Card (APC part number AP9617, AP9618 or AP9619) with a firmware revision of 1.1.0 or later OR an APC Web/SNMP Card (APC part number AP9606). If you are also using an APC Environmental Monitoring Card (APC part number AP9612TH), your Network Management Card must have firmware revision 1.1.5 or greater.

You can update your APC NMC firmware from the APC Web site.

PowerChute Network Shutdown cannot be used with APC PowerNet SNMP Adapters (cards). If your card has an APC part number of AP9605, AP9205, or AP9603, contact APC support or your APC dealer to upgrade the card.

If you are using multiple Smart-UPS devices, multiple Symmetra devices, or have a Parallel Silcon UPS system, you use one NMC in each UPS in the system. If your NMC has firmware revision 1.2.0 or later, be sure that the Synchronization option is disabled.
Note: AP9606 is only supported with single Smart-UPS, Matrix, Symmetra, or Silcon and Parallel Silcon configurations. It is not supported with either a multiple Smart-UPS or multiple Symmetra configuration.

A supported operating system as listed on the APC Web site.

The IP address for each APC Network Management Card.

A Java Virtual Machine (JVM), version 1.4.2 or later, on your server for all operating systems except NetWare (see two paragraphs down).

You can download a Java Virtual Machine from http://java.sun.com. PCNS installs JVM 1.4.2 if the most recent version found on your system is less than this (the rpm installer for VMWare is an exception to this, see Bare Metal Installation and Configuration with VMware ESX Server). If a JVM version greater than 1.4.2 is found on your system, PCNS will use the later version.

On Novell NetWare, both JVM 1.4.1 and 1.4.2 are supported. (NetWare 6 has JVM 1.3.1). Novell JVM 1.4.1 and 1.4.2 are available on Novell's Web site.

If you are installing PowerChute Network Shutdown on more than 50 computers powered by the same UPS, read the document "PowerChute Network Shutdown with more than 50 computers on one UPS" before continuing the installation. To obtain the document, go to the Software Downloads page on the APC Web site and select PowerChute Network Shutdown.

If you have a Parallel Silcon UPS, read the document "PowerChute Network Shutdown with a Parallel Silcon UPS System" before continuing the installation. To obtain the document, go to the Software Downloads page on the APC Web site and, select PowerChute Network Shutdown for Windows - Parallel Silcon Configuration Guide.

If you are installing on a multiple Smart-UPS or multiple Symmetra configuration, see Running a Multiple Configuration (Smart-UPS and Symmetra).

A monitor with a minimum resolution of 800 x 600; however, 1024 x 768 or greater is recommended.

If you are using a firewall, the http port used by the Network Management Card (default:80/TCP), and port 3052 (TCP and UDP) must be open for communication with the NMC.

You must have Administrator privileges on the network.


Overseas consultants in India

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc