hello, i has using the PowerChute Business Edition, but i can't shutdown the machines, exemple:
i'm try using the following script
@START "" "C:\Program Files (x86)\APC\PowerChute Business Edition\agent\cmdfiles\myShut.bat"
Inside the file myshut.bat have this script: shutdown /s /m
myPC /d 1:1 /f /t 60
i did try without the tag @START only shutdown /s /m
myPC /d 1:1 /f /t 60, but with the application PowerChute B. doesn't execute the .bat .
I have 3 server on this no-break and i didn't turn off him.
Someone can help?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 12:34 AM . Last Modified: 2024-03-06 03:01 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 12:34 AM . Last Modified: 2024-03-06 03:01 AM
An APC UPS which supports the use of an APC Network Management Card (NMC). This currently includes any Smart-UPS UPS with a card slot or an embedded NMC, any Smart-UPS DP UPS, any Matrix-UPS UPS with a firmware revision of Y or later, any Symmetra UPS, and any Silcon Series UPS.
An APC Network Management Card (APC part number AP9617, AP9618 or AP9619) with a firmware revision of 1.1.0 or later OR an APC Web/SNMP Card (APC part number AP9606). If you are also using an APC Environmental Monitoring Card (APC part number AP9612TH), your Network Management Card must have firmware revision 1.1.5 or greater.
You can update your APC NMC firmware from the APC Web site.
PowerChute Network Shutdown cannot be used with APC PowerNet SNMP Adapters (cards). If your card has an APC part number of AP9605, AP9205, or AP9603, contact APC support or your APC dealer to upgrade the card.
If you are using multiple Smart-UPS devices, multiple Symmetra devices, or have a Parallel Silcon UPS system, you use one NMC in each UPS in the system. If your NMC has firmware revision 1.2.0 or later, be sure that the Synchronization option is disabled.
Note: AP9606 is only supported with single Smart-UPS, Matrix, Symmetra, or Silcon and Parallel Silcon configurations. It is not supported with either a multiple Smart-UPS or multiple Symmetra configuration.
A supported operating system as listed on the APC Web site.
The IP address for each APC Network Management Card.
A Java Virtual Machine (JVM), version 1.4.2 or later, on your server for all operating systems except NetWare (see two paragraphs down).
You can download a Java Virtual Machine from http://java.sun.com. PCNS installs JVM 1.4.2 if the most recent version found on your system is less than this (the rpm installer for VMWare is an exception to this, see Bare Metal Installation and Configuration with VMware ESX Server). If a JVM version greater than 1.4.2 is found on your system, PCNS will use the later version.
On Novell NetWare, both JVM 1.4.1 and 1.4.2 are supported. (NetWare 6 has JVM 1.3.1). Novell JVM 1.4.1 and 1.4.2 are available on Novell's Web site.
If you are installing PowerChute Network Shutdown on more than 50 computers powered by the same UPS, read the document "PowerChute Network Shutdown with more than 50 computers on one UPS" before continuing the installation. To obtain the document, go to the Software Downloads page on the APC Web site and select PowerChute Network Shutdown.
If you have a Parallel Silcon UPS, read the document "PowerChute Network Shutdown with a Parallel Silcon UPS System" before continuing the installation. To obtain the document, go to the Software Downloads page on the APC Web site and, select PowerChute Network Shutdown for Windows - Parallel Silcon Configuration Guide.
If you are installing on a multiple Smart-UPS or multiple Symmetra configuration, see Running a Multiple Configuration (Smart-UPS and Symmetra).
A monitor with a minimum resolution of 800 x 600; however, 1024 x 768 or greater is recommended.
If you are using a firewall, the http port used by the Network Management Card (default:80/TCP), and port 3052 (TCP and UDP) must be open for communication with the NMC.
You must have Administrator privileges on the network.
Overseas consultants in India
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 12:34 AM . Last Modified: 2024-03-06 03:01 AM
i'd start here -> http://nam-en.apc.com/app/answers/detail/a_id/7712
my main question would be does your script work correctly if you run it outside of PCBE? assuming so, just double check that kbase i posted.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 12:34 AM . Last Modified: 2024-03-06 03:01 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 12:34 AM . Last Modified: 2024-03-06 03:01 AM
An APC UPS which supports the use of an APC Network Management Card (NMC). This currently includes any Smart-UPS UPS with a card slot or an embedded NMC, any Smart-UPS DP UPS, any Matrix-UPS UPS with a firmware revision of Y or later, any Symmetra UPS, and any Silcon Series UPS.
An APC Network Management Card (APC part number AP9617, AP9618 or AP9619) with a firmware revision of 1.1.0 or later OR an APC Web/SNMP Card (APC part number AP9606). If you are also using an APC Environmental Monitoring Card (APC part number AP9612TH), your Network Management Card must have firmware revision 1.1.5 or greater.
You can update your APC NMC firmware from the APC Web site.
PowerChute Network Shutdown cannot be used with APC PowerNet SNMP Adapters (cards). If your card has an APC part number of AP9605, AP9205, or AP9603, contact APC support or your APC dealer to upgrade the card.
If you are using multiple Smart-UPS devices, multiple Symmetra devices, or have a Parallel Silcon UPS system, you use one NMC in each UPS in the system. If your NMC has firmware revision 1.2.0 or later, be sure that the Synchronization option is disabled.
Note: AP9606 is only supported with single Smart-UPS, Matrix, Symmetra, or Silcon and Parallel Silcon configurations. It is not supported with either a multiple Smart-UPS or multiple Symmetra configuration.
A supported operating system as listed on the APC Web site.
The IP address for each APC Network Management Card.
A Java Virtual Machine (JVM), version 1.4.2 or later, on your server for all operating systems except NetWare (see two paragraphs down).
You can download a Java Virtual Machine from http://java.sun.com. PCNS installs JVM 1.4.2 if the most recent version found on your system is less than this (the rpm installer for VMWare is an exception to this, see Bare Metal Installation and Configuration with VMware ESX Server). If a JVM version greater than 1.4.2 is found on your system, PCNS will use the later version.
On Novell NetWare, both JVM 1.4.1 and 1.4.2 are supported. (NetWare 6 has JVM 1.3.1). Novell JVM 1.4.1 and 1.4.2 are available on Novell's Web site.
If you are installing PowerChute Network Shutdown on more than 50 computers powered by the same UPS, read the document "PowerChute Network Shutdown with more than 50 computers on one UPS" before continuing the installation. To obtain the document, go to the Software Downloads page on the APC Web site and select PowerChute Network Shutdown.
If you have a Parallel Silcon UPS, read the document "PowerChute Network Shutdown with a Parallel Silcon UPS System" before continuing the installation. To obtain the document, go to the Software Downloads page on the APC Web site and, select PowerChute Network Shutdown for Windows - Parallel Silcon Configuration Guide.
If you are installing on a multiple Smart-UPS or multiple Symmetra configuration, see Running a Multiple Configuration (Smart-UPS and Symmetra).
A monitor with a minimum resolution of 800 x 600; however, 1024 x 768 or greater is recommended.
If you are using a firewall, the http port used by the Network Management Card (default:80/TCP), and port 3052 (TCP and UDP) must be open for communication with the NMC.
You must have Administrator privileges on the network.
Overseas consultants in India
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 12:34 AM . Last Modified: 2024-03-06 03:01 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 12:34 AM . Last Modified: 2024-03-06 03:01 AM
An APC UPS which supports the use of an APC Network Management Card (NMC). This currently includes any Smart-UPS UPS with a card slot or an embedded NMC, any Smart-UPS DP UPS, any Matrix-UPS UPS with a firmware revision of Y or later, any Symmetra UPS, and any Silcon Series UPS.
An APC Network Management Card (APC part number AP9617, AP9618 or AP9619) with a firmware revision of 1.1.0 or later OR an APC Web/SNMP Card (APC part number AP9606). If you are also using an APC Environmental Monitoring Card (APC part number AP9612TH), your Network Management Card must have firmware revision 1.1.5 or greater.
You can update your APC NMC firmware from the APC Web site.
PowerChute Network Shutdown cannot be used with APC PowerNet SNMP Adapters (cards). If your card has an APC part number of AP9605, AP9205, or AP9603, contact APC support or your APC dealer to upgrade the card.
If you are using multiple Smart-UPS devices, multiple Symmetra devices, or have a Parallel Silcon UPS system, you use one NMC in each UPS in the system. If your NMC has firmware revision 1.2.0 or later, be sure that the Synchronization option is disabled.
Note: AP9606 is only supported with single Smart-UPS, Matrix, Symmetra, or Silcon and Parallel Silcon configurations. It is not supported with either a multiple Smart-UPS or multiple Symmetra configuration.
A supported operating system as listed on the APC Web site.
The IP address for each APC Network Management Card.
A Java Virtual Machine (JVM), version 1.4.2 or later, on your server for all operating systems except NetWare (see two paragraphs down).
You can download a Java Virtual Machine from http://java.sun.com. PCNS installs JVM 1.4.2 if the most recent version found on your system is less than this (the rpm installer for VMWare is an exception to this, see Bare Metal Installation and Configuration with VMware ESX Server). If a JVM version greater than 1.4.2 is found on your system, PCNS will use the later version.
On Novell NetWare, both JVM 1.4.1 and 1.4.2 are supported. (NetWare 6 has JVM 1.3.1). Novell JVM 1.4.1 and 1.4.2 are available on Novell's Web site.
If you are installing PowerChute Network Shutdown on more than 50 computers powered by the same UPS, read the document "PowerChute Network Shutdown with more than 50 computers on one UPS" before continuing the installation. To obtain the document, go to the Software Downloads page on the APC Web site and select PowerChute Network Shutdown.
If you have a Parallel Silcon UPS, read the document "PowerChute Network Shutdown with a Parallel Silcon UPS System" before continuing the installation. To obtain the document, go to the Software Downloads page on the APC Web site and, select PowerChute Network Shutdown for Windows - Parallel Silcon Configuration Guide.
If you are installing on a multiple Smart-UPS or multiple Symmetra configuration, see Running a Multiple Configuration (Smart-UPS and Symmetra).
A monitor with a minimum resolution of 800 x 600; however, 1024 x 768 or greater is recommended.
If you are using a firewall, the http port used by the Network Management Card (default:80/TCP), and port 3052 (TCP and UDP) must be open for communication with the NMC.
You must have Administrator privileges on the network.