How to resolve error code 0x0109?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to resolve error code 0x0109?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:35 AM

0 Likes
11
5645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:35 AM

How to resolve error code 0x0109?

Two days ago, I accidentally switch to bypass manually. The Smart RT 6000 turned off. I quickly knew what I had done so I switch it back to Normal and turned on the UPS. Now I finally had a chance to configure the Network Management Card. Upon logging into the browser, the home page displayed 1 warning event - Power Failure. I setup the email notification and every 2 minutes, I get a warning alert. Warning - UPS: On battery power in response to an input power problem. Where do I start to troubleshoot this issue to eliminate the warning? Thank you in advance.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:34 AM

0 Likes
0
5641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:34 AM

sorry. the firmware version i meant/was looking for is the APP and AOS. APP name is sumx and there should be something like 3.5.8 and AOS something similar to 3.6.1.

i believe this is an issue with the management card only.

lets log into the web interface on the management card and go to the Administration menu->General->Reset/Reboot->Reboot Management Interface.

this will reboot the management interface of the network management card and will not affect the UPS output.

let me know how that happens and if the message clears. thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:35 AM

0 Likes
0
5641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:35 AM

can you post the entire event log?

was the current status of the UPS a power failure? or was that happening when you went to bypass? i am confused on whats actually happening. if there really is a power outage or voltage is out of range and you go to bypass, the UPS will turn off since bypass means the UPS is passing utility power straight through with no battery back up.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:35 AM

0 Likes
0
5641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:35 AM

Here is the entire log. Please mind the date. The 02/16/2000 is actually 06/15/2009. I placed it accidentally on bypass on that date.
I have also attached a print screen of the UPS overview settings. Hope they help. Thank you for helping.

02/16/2000 01:48:38 UPS: Passed a self-test.
02/16/2000 01:48:23 UPS: The output power is now turned on.
02/16/2000 01:47:57 UPS: The output power is turned off.
02/16/2000 01:47:57 UPS: No longer in bypass.
02/16/2000 01:47:54 UPS: In bypass in response to the bypass switch at the UPS, typically for maintenance.
02/08/2000 17:47:25 UPS: Passed a self-test.
02/08/2000 17:47:10 UPS: Started a self-test.
02/08/2000 17:45:22 UPS: Passed a self-test.
02/08/2000 17:45:08 UPS: The output power is now turned on.
02/08/2000 17:45:08 UPS: On battery power in response to an input power problem.
02/08/2000 17:44:52 UPS: The output power is turned off.
02/05/2000 04:06:20 UPS: No longer on battery power.
02/05/2000 04:06:19 UPS: On battery power in response to an input power problem.
02/04/2000 01:40:00 UPS: No longer on battery power.
02/04/2000 01:39:59 UPS: On battery power in response to an input power problem.
01/29/2000 00:02:37 UPS: Passed a self-test.
01/29/2000 00:02:21 UPS: Started a self-test.
01/15/2000 00:02:33 UPS: Passed a self-test.
01/15/2000 00:02:18 UPS: Started a self-test.
01/01/2000 00:02:42 UPS: Passed a self-test.
01/01/2000 00:02:26 UPS: The output power is now turned on.
01/01/2000 00:01:33 UPS: The output power is turned off.
01/01/2000 00:01:33 UPS: Restored the local network management interface-to-UPS communication.
01/01/2000 00:01:07 System: Coldstart.
01/01/2000 03:54:40 UPS: The output power is turned off.
01/01/2000 00:04:27 UPS: Restored the local network management interface-to-UPS communication.
01/01/2000 00:01:07 System: Coldstart.
01/01/2000 00:02:08 UPS: The output power is turned off.
01/01/2000 00:02:03 System: Console user 'apc' logged out from serial port.
01/01/2000 00:01:57 System: Event Log cleared.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:35 AM

0 Likes
0
5641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:35 AM

Sorry, I forgot to answer your other question. The power failure was caused by switching it to bypass mode. Upon returning it to normal mode. I powered on the UPS. Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:34 AM

0 Likes
0
5641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:34 AM

ok this is interesting. its saying its on battery but the battery percentage is 100%. the event log looks a little screwy too as far as reporting the output power turning on and off.

a couple questions:

1.) has the output actually been turning on and off as far as you know pertaining to those events showing in the log? (besides when you went to bypass - the load dropped right?)
2.) can you tell me the firmware versions on the network card under Administration->General->About?
3.) can you see what indicators are illuminated on the front of the UPS? i have attached a picture of the front display and LEDs.
4.) can you get the data log too just incase?
5.) i wanted to go to bypass at some point and reseat the network management card and then come back out of bypass depending on what your answers are to the above questions but it could drop the load if you said going to bypass did earlier.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:34 AM

0 Likes
0
5642
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:34 AM

Here is the Data Log: I went did a custom search from 01/01/2000 to now and this is what it return.
Date Time Vmin Vmax Vout Iout %Wout Freq %Cap Vbat TupsC %VAout TIambC %HumI
06/17/2009 14:34:43 228.9 236.1 208.2 10.16 46.0 60.00 100.0 217.0 29.6 35.0
06/17/2009 14:24:43 231.8 236.1 208.2 10.08 46.0 60.01 100.0 217.0 29.6 35.0
06/17/2009 14:14:43 233.2 236.1 208.2 10.08 46.0 59.98 100.0 217.0 29.1 35.0
06/17/2009 14:04:43 231.8 236.1 208.2 10.08 47.0 60.00 100.0 217.0 29.1 35.0
06/17/2009 13:54:43 231.8 234.7 208.2 10.16 45.0 60.01 100.0 217.0 29.1 35.0
06/17/2009 13:44:43 230.4 234.7 208.2 10.08 46.0 59.98 100.0 217.0 29.1 35.0
06/17/2009 13:34:43 228.9 233.2 208.2 10.08 45.0 59.98 100.0 217.0 29.1 33.0
06/17/2009 13:24:43 228.9 236.1 209.4 10.08 46.0 59.98 100.0 217.0 28.5 35.0
06/17/2009 13:14:43 231.8 234.7 208.2 10.08 46.0 60.00 100.0 217.0 28.5 35.0
06/17/2009 13:04:43 231.8 234.7 208.2 10.08 46.0 59.97 100.0 217.0 29.1 35.0
06/17/2009 12:54:43 233.2 236.1 208.2 10.08 45.0 59.96 100.0 217.0 28.5 35.0
06/17/2009 12:44:43 234.7 236.1 208.2 10.16 45.0 60.00 100.0 217.0 28.0 35.0
06/17/2009 12:34:43 230.4 236.1 208.2 10.16 46.0 60.03 100.0 217.0 28.0 35.0
06/17/2009 12:24:43 231.8 237.6 208.2 10.08 46.0 59.99 100.0 217.0 28.5 35.0
06/17/2009 12:14:43 236.1 237.6 208.2 10.08 46.0 59.99 100.0 217.0 28.0 35.0
06/17/2009 12:04:43 234.7 237.6 208.2 10.08 46.0 60.01 100.0 217.0 28.0 35.0
06/17/2009 11:54:43 231.8 236.1 208.2 10.16 46.0 60.01 100.0 217.0 28.0 35.0
06/17/2009 11:44:43 234.7 236.1 208.2 9.92 46.0 60.00 100.0 217.0 28.5 35.0

Answers:
1.) The UPS only has shutdown once as far as I know. It's on 02/16/2000 (actual date 06/15/2009). This is when I moved the switch from normal to bypass by accident. However on 02/08/2000 (actual date 06/08/2009), the APC receptacles in the back tripped shutting down all the servers. But the APC was still up and running with 100% battery but with zero load. I have attached receptacles.jpg. The farthest black cord on the right is a PDU with a server, tape loader, and switches. It was plugged into the first set of receptacles on the upper left. The left receptacle already had another PDU plugged in with 5 servers, and a switch. It overloaded that left receptacle so I had to press the white button to bring it back on line. I then switch one PDU to another receptable as pictured. So as far as I know the APC has only shutdown once.
2.) The firmware version of the network management card is A10 with a manufactured date of 11/09/08.
3.) See above
4.) See attach bezel.jpg. Battery is at 100% (5 LED). Load is 40% (2 LED). It is currently running on power source.

Thanks for your help.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:34 AM

0 Likes
0
5642
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:34 AM

See attach data log.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:34 AM

0 Likes
0
5642
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:34 AM

sorry. the firmware version i meant/was looking for is the APP and AOS. APP name is sumx and there should be something like 3.5.8 and AOS something similar to 3.6.1.

i believe this is an issue with the management card only.

lets log into the web interface on the management card and go to the Administration menu->General->Reset/Reboot->Reboot Management Interface.

this will reboot the management interface of the network management card and will not affect the UPS output.

let me know how that happens and if the message clears. thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:34 AM

0 Likes
0
5642
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:34 AM

Here is the correct firmware information. I will now reboot the management card per your instructions. I will let you know the outcome. Thanks.

Application Module

Name: sumx
Version: v3.5.5
Date: 05/24/2007
Time: 16:14:52


APC OS (AOS)

Name: aos
Version: v3.5.5
Date: 05/24/2007
Time: 15:44:22

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:34 AM

0 Likes
0
5642
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:34 AM

i picKed a winna...That did it! Thank you very much for all your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:34 AM

0 Likes
0
5641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:22 PM . Last Modified: β€Ž2024-03-14 04:34 AM

Sorry for my ignorance. But what menu options do I select to upgrade the firmware on the Network Management Card? Will this affect the UPS in terms of rebooting? Do you recommend upgrading it after office hours? Thank You.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:23 PM . Last Modified: β€Ž2024-03-14 04:34 AM

0 Likes
0
5641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:23 PM . Last Modified: β€Ž2024-03-14 04:34 AM

you dont need to do anything on the management card end.

to run the firmware upgrade, just download the file i attached which extracts some .bin files and includes a batch file that you execute that will prompt you for the IP address of the network management card to upgrade and the username/password, etc. it is a little wizard that will do everything for you.

the upgrade will NOT affect the UPS load or anything like that, it will only reboot the management interface just like you did to clear up the prior issue so you can do this during office hours if you'd like πŸ˜‰

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore