Ask our Experts
Didn't find what you are looking for? Ask our experts!
Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-23 06:23 PM
Is there any way to get the power consumption of each port in the PDU?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-24 06:34 AM
Short answer - No
Long answer - If power / energy (monitoring) and management is required it’s easier and more efficient by installing a dedicated unit that use CT’s.
The (CT) Current Transformer simply clips over a branch circuit in the service panel or using an approved cUL split cord plug.
A true energy monitor will allow you to adjust (dial in) the input line voltage. Any hardware that doesn’t reference or allow you to adjust the input line voltage is a waste of time and gathered data.
Once in place these units can provide critical insight about low, high, average, peak, inrush values. That cover voltage, power, current, PF, KWH.
Having the ability to see live real-time power draw and consumption can’t be overstated! Never mind being able to recall days, weeks, months, years of historical data.
Once known the facility can design or manage their infrastructure better and reduce energy consumption and waste.
During a grid down event having this empirical data allows you to know how long backup systems will operate for given an ever changing power draw.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-24 06:34 AM
Short answer - No
Long answer - If power / energy (monitoring) and management is required it’s easier and more efficient by installing a dedicated unit that use CT’s.
The (CT) Current Transformer simply clips over a branch circuit in the service panel or using an approved cUL split cord plug.
A true energy monitor will allow you to adjust (dial in) the input line voltage. Any hardware that doesn’t reference or allow you to adjust the input line voltage is a waste of time and gathered data.
Once in place these units can provide critical insight about low, high, average, peak, inrush values. That cover voltage, power, current, PF, KWH.
Having the ability to see live real-time power draw and consumption can’t be overstated! Never mind being able to recall days, weeks, months, years of historical data.
Once known the facility can design or manage their infrastructure better and reduce energy consumption and waste.
During a grid down event having this empirical data allows you to know how long backup systems will operate for given an ever changing power draw.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.