How to enable AP9630's DHCP funcation

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to enable AP9630's DHCP funcation
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:49 PM . Last Modified: ‎2024-03-11 04:28 AM

0 Likes
3
2894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:49 PM . Last Modified: ‎2024-03-11 04:28 AM

How to enable AP9630's DHCP funcation

Hi,

Our company recently bought around 200 piece of AP9630 network Management card 2.  I do not know how to enable its DHCP function by command line.   I would like to let the card automatically obtain an ip address from dhcp server but without changing/configure the DHCP server (option 43). 

Thanks a lot for help!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • apc_ap9630
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:49 PM . Last Modified: ‎2024-03-11 04:28 AM

0 Likes
0
2894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:49 PM . Last Modified: ‎2024-03-11 04:28 AM

hello again.

tcpip only shows manual settings. netstat shows active settings. since DHCP is an automatic method of assigning IPs, tcpip is blank. (in v6.0.6 and higher, we will be making it so that tcpip shows both active and manual settings to avoid confusion. netstat will still work).

DHCP option 43 is not required. some users like it. it helps identify the device as an APC device after you set it to a certain value. most users don't use it.

i'd suggest maybe reviewing this guide: http://www.apcmedia.com/salestools/PMAR-8P9G2C/PMAR-8P9G2C_R2_EN.pdf

it goes over all of the CLI commands. the user command provides functionality for changing usernames and passwords. as you navigate the interface, you can type a ? after a command for help. so if you need help using the user command, type user ?

you don't need to do any further configuration for the card to get a DHCP address as that is what it will do by default.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:49 PM . Last Modified: ‎2024-03-11 04:28 AM

0 Likes
0
2894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:49 PM . Last Modified: ‎2024-03-11 04:28 AM

hello mybox65

DHCP option 43 cookie is disabled by default on AP9630/31/35 v5.1.X and higher firmware. DHCP only with no cookie required is the default boot mode. Do you know what firmware is on your card? You can find this easily when you log in via command line on the top right of the screen. In this newer firmware, you can turn it on if you'd like.

If your firmware is v5.0.X and several years old now, then you'd use the boot command if you want to disable the cookie since we used to ship the NMCs with the cookie enabled by default in v5.0.X. The default bootmode was DHCP/BOOTP with cookie enabled.

The boot command has many options and boot -c are the options. So, to disable the cookie, type boot -c disable and then most likely, you'll need to type reboot to apply the change. it should tell you to reboot if that's the case.

Hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:49 PM . Last Modified: ‎2024-03-11 04:28 AM

0 Likes
0
2894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:49 PM . Last Modified: ‎2024-03-11 04:28 AM

The firmware version is V5.1.7  .    Once I type command "tcpip", I see there are no any ip address.    However once I type command "netstat", I see the card already got an ip address from DHCP server. 

My question ,   Do I need do any extra configuration after I installing the card to UPS,  if I just want the card automatically get an ip address from DHCP Server ?    What is the DHCP option 43 for ?  How do I change the password by command line ?

Thank you very much for your kindly assistance

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:49 PM . Last Modified: ‎2024-03-11 04:28 AM

0 Likes
0
2895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:49 PM . Last Modified: ‎2024-03-11 04:28 AM

hello again.

tcpip only shows manual settings. netstat shows active settings. since DHCP is an automatic method of assigning IPs, tcpip is blank. (in v6.0.6 and higher, we will be making it so that tcpip shows both active and manual settings to avoid confusion. netstat will still work).

DHCP option 43 is not required. some users like it. it helps identify the device as an APC device after you set it to a certain value. most users don't use it.

i'd suggest maybe reviewing this guide: http://www.apcmedia.com/salestools/PMAR-8P9G2C/PMAR-8P9G2C_R2_EN.pdf

it goes over all of the CLI commands. the user command provides functionality for changing usernames and passwords. as you navigate the interface, you can type a ? after a command for help. so if you need help using the user command, type user ?

you don't need to do any further configuration for the card to get a DHCP address as that is what it will do by default.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore