Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-07-08 12:16 AM . Last Modified: 2024-02-29 11:22 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:16 AM . Last Modified: 2024-02-29 11:22 PM
Dear Support Team,
We have recenly Purchased couple of units with same type (SURTD3000XLI).
I just want to share the temperature sensor between two units.
If this is not possible then pls let me know is there any possibility to get Temperature details from another ups unit where Sensor is connected?
My Ultimate goal is to shutdown the servers when temperature increases to assigned value.
IP address of UPS 1 : 10.0.2.x
IP address of UPS 2 : 10.0.2.x
Thanks
Srinivas
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:16 AM . Last Modified: 2024-02-29 11:22 PM
Hi,
Each UPS would need to have its own temperature probe connected to its own Network Management Card.
Here is a knowledge base on this topic -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156076
Are you planning to have these units installed separately/standalone or do you have dual power corded equipment and plan to install PowerChute Network Shutdown in a redundant configuration where the PowerChute clients monitor both UPS units?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:16 AM . Last Modified: 2024-02-29 11:22 PM
Hi,
Each UPS would need to have its own temperature probe connected to its own Network Management Card.
Here is a knowledge base on this topic -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156076
Are you planning to have these units installed separately/standalone or do you have dual power corded equipment and plan to install PowerChute Network Shutdown in a redundant configuration where the PowerChute clients monitor both UPS units?
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.