Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
How to configure server shutdown when power to UPS is cut off?
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2904:00 AM. Last Modified: 2024-03-1301:56 AM
you will have the network management card configured and the software you need to install on your clients you want to gracefully shutdown is powerchute network shutdown. powerchute business edition is only for use with the serial cables or USB options and should not be used at the same time or as the graceful shutdown software when already using a network management card.
by default, when you install the software and provide the IP of the NMC in the UPS, then they communicate over the network for status updates (on battery, low battery, etc) and then the UPS will signal the client to shutdown when the UPS has a low battery, which by default is when 2 minutes of runtime remain. if this won't work for you, you can raise the low battery setting in the network management card and/or change shutdown settings or shutdown trigger events in the powerchute network shutdown interface on your individual clients.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2904:00 AM. Last Modified: 2024-03-1301:56 AM
you will have the network management card configured and the software you need to install on your clients you want to gracefully shutdown is powerchute network shutdown. powerchute business edition is only for use with the serial cables or USB options and should not be used at the same time or as the graceful shutdown software when already using a network management card.
by default, when you install the software and provide the IP of the NMC in the UPS, then they communicate over the network for status updates (on battery, low battery, etc) and then the UPS will signal the client to shutdown when the UPS has a low battery, which by default is when 2 minutes of runtime remain. if this won't work for you, you can raise the low battery setting in the network management card and/or change shutdown settings or shutdown trigger events in the powerchute network shutdown interface on your individual clients.