Recently i have purchased on SUA 2200 Online UPS for my Server (750 Watt). But from the very first day, the Load Graph of the Face Plat is not showing any activities. can any one give me some advice, how to solve this problem ...... please ??????
null
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:00 AM . Last Modified: 2024-03-13 01:56 AM
how much load do you think you have on the UPS? have you checked to see if via powerchute software or a network management card what the percentage is reported as? the lower the load, the less accurate the reading is for load. so you might not see a very small load reported, depending on what is attached to the UPS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:00 AM . Last Modified: 2024-03-13 01:56 AM
how much load do you think you have on the UPS? have you checked to see if via powerchute software or a network management card what the percentage is reported as? the lower the load, the less accurate the reading is for load. so you might not see a very small load reported, depending on what is attached to the UPS.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.