How do I have two servers shutdown at different times.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How do I have two servers shutdown at different times.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:24 AM . Last Modified: ‎2024-03-05 02:19 AM

0 Likes
2
692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:24 AM . Last Modified: ‎2024-03-05 02:19 AM

How do I have two servers shutdown at different times.

We just bought a couple of Smart-UPS's, 750's. We also bought the AP9630 network cards.

I have it up and running after some struggles, (its easy when you know how I didn't). Anyway one  working and emailing on a test machine computer.

However I can't see how to configure it so that I have one server shutdown first then another. I wanted to put the PDC and the Exchange server on one UPS.

I want the Exchange server to shutdown first and give it 15 Minutes or so to shutdown then the PDC. I cant see any way to make them different. IT seems that the shutdown settings on the card are going to shut everything down. How can I separate the shutdowns.

Am I missing something ?

thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:25 AM . Last Modified: ‎2024-03-05 02:19 AM

0 Likes
0
693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:25 AM . Last Modified: ‎2024-03-05 02:19 AM

Well Im testing this actually right now on a xp machine. I downloaded the windows2003 / XP 32 bit PowerChute Network Shutdown software for the onto the computer and installed it. It is important to note that this is NOT the software that comes with the UPS but with the card, and actually I downloaded it from there site.

So your saying that I should enter the software from the computer. And on that computer I can configure the proper shutdown procedure?

Is that in the configure events?

Thanks.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:24 AM . Last Modified: ‎2024-03-05 02:19 AM

0 Likes
0
693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:24 AM . Last Modified: ‎2024-03-05 02:19 AM

Hi,

Depending on the OS of each system you can install PowerChute Network Shutdown and configure the software to power down the OS's at different times. You can find documentation and the OS compatibility chart for PowerChute at PowerChute Network Shutdown – Network Power Management Software | APC

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:25 AM . Last Modified: ‎2024-03-05 02:19 AM

0 Likes
0
694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:25 AM . Last Modified: ‎2024-03-05 02:19 AM

Well Im testing this actually right now on a xp machine. I downloaded the windows2003 / XP 32 bit PowerChute Network Shutdown software for the onto the computer and installed it. It is important to note that this is NOT the software that comes with the UPS but with the card, and actually I downloaded it from there site.

So your saying that I should enter the software from the computer. And on that computer I can configure the proper shutdown procedure?

Is that in the configure events?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.