How can we run smart-ups 3000 rackmount on a 20a circuit?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How can we run smart-ups 3000 rackmount on a 20a circuit?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:32 AM

0 Likes
3
3327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:32 AM

How can we run smart-ups 3000 rackmount on a 20a circuit?

How can we run smart-ups 3000 rackmount on a 20a circuit?
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:32 AM

0 Likes
0
3327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:32 AM

We have purchased exact same model and have exact same issue except our load is 1300 Watts. We purchased 2 units one attached to storage and other attached to server. Went for 3000 Watts option to have additional power available down the road when we move to new facility in 6 months.

If I understood correctly unit does not always draw 3000 Watts/30 Amps If we have 1300 watts max load will be 1300 Watts/15 Amps. Can you please confirm or share relationship between load and power consumption? Thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:32 AM

0 Likes
0
3327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:32 AM

Hi Eugene,

While you can find conversion for a locking ("twist-lock") plug on-line, there are adapters you can buy "locally" that will allow you to convert from a regular (straight blade) 30 amp plug to 15 amp plug.

BUT before I go further, I ask you to consider what the result will be, and what can be considered "safe".

A 20 amp circuit is "rated" to provide only 2/3 the current of a 30 amp circuit-- or approximately 2000VA from the UPS, considering efficiency. Theoretically, exceeding 20 amps (or 2000VA load on the UPS) SHOULD cause the circuit breaker to trip, resulting in the 3000VA UPS switching over to battery operation until first the load is reduced AND then someone resets the circuit breaker. Assuming you chose the 3000VA model so that you could approach that load, this is not a practical solution. If you chose the 3000VA model while considering the (community) perspective of running close to 1/2 or 2/3 the max rating of the UPS, you MAY get away with this arrangement.

Regarding safety, circuit breakers and fuses open quickly under an extreme overload or short circuit, but they WILL tolerate a "modest" overload for a while (could be many minutes) which could lead to heating of the wires and connectors, something that really should NOT be considered "safe". A 3000VA UPS is designed to draw 30 amps indefinitely if that is what the load needs, so there is the potential to create such an overload condition.

The "punch line"-- this is NOT a recommended solution, but you can search on-line for NEMA L5-30R to L5-20P (or 5-20P if your existing receptacle is "straight-blade, again, not recommended) adapters for converting the factory installed locking connector, or you can buy adapters to go from a 30 amp to 15 amp straight blade plug at most stores that sell RV supplies and accessories.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:32 AM

0 Likes
0
3327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:32 AM

I would also like to note that using an adapter or modifying the input plug will void the UL listing of the UPS as well as the Equipment Protection Policy of the UPS. In short, it will work, but it is not supported and is potentially unsafe. APC strongly recommends having the proper circuit installed or using a smaller UPS. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:32 AM

0 Likes
0
3328
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:32 AM

We have purchased exact same model and have exact same issue except our load is 1300 Watts. We purchased 2 units one attached to storage and other attached to server. Went for 3000 Watts option to have additional power available down the road when we move to new facility in 6 months.

If I understood correctly unit does not always draw 3000 Watts/30 Amps If we have 1300 watts max load will be 1300 Watts/15 Amps. Can you please confirm or share relationship between load and power consumption? Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of