High BATTV voltage?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • High BATTV voltage?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

0 Likes
20
4013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

High BATTV voltage?

Today I've installed new batteries in my SMT2200I

It looks that it's stopping at 27%.

MODEL    : Smart-UPS 2200 

STATUS   : ONLINE 

BCHARGE  : 27.0 Percent

TIMELEFT : 27.0 Minutes

MBATTCHG : 5 Percent

MINTIMEL : 3 Minutes

But what is strange is the BATTV looks high.

BATTV    : 49.9 Volts

Isn't that too high?

When I look in the manual op page 38 it says: "[...] this should be near 24 Volts plus or minus 5 Volts. "

Did I missed something or is this 'normal' for the SMT2200I?

[update]

8 hours later... charge dropped to 4%

MODEL    : Smart-UPS 2200 

STATUS   : ONLINE 

BCHARGE  : 4.0 Percent

TIMELEFT : 4.0 Minutes

I've disconnected batteries for now until I know what happening here.

Regards,

Peter

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:40 PM . Last Modified: ‎2024-02-29 11:49 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:40 PM . Last Modified: ‎2024-02-29 11:49 PM

Service is great isn't it 🙂

I thought you were out of warranty or I would have told you to use them earlier 😄

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 20
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

0 Likes
0
4010
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

It should float at 54 volts as it is 2 24v packs.

Your charger is not working, try to braindead the unit by shutting down and removing the mains with no batteries for a minute and see if it works after. Also check the breakers on the back are not out.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

0 Likes
0
4010
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

The replacement batteries RBC55 (for the SMT2200i) are 12V - 17 Ah each and not 24V.

Is the BATTV then not a bit too high?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

As the owner of 2 2200i's I can confirm the RBC55's are 2 packs of 24v batteries consisting of 2 12v cells each (12x4=48 plus maintenance charge from the UPS taking it to an average of 54.4 on a healthy UPS)

When installed you either read the voltage shown by the software/hardware or if using a meter on the front battery pack it will only read the voltage of the pack you are testing so you will need to times it by 2 to get the voltage.

DzKmxYgax97%2BPAvbh4YCXA%3D%3D.pngDzKmxYgax97%2BPAvbh4YCXA%3D%3D.png

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

Hi Gareth,

Thanks!

That explains it clearly! (and why I was confused about the 12/24V and the load of 50V on BATTV)

I will look later on today when I'm back home on the fuses.


Regards,

Peter

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

Gareth,

Any more suggestions?

Fuse is OKE.

UPS is now running for 3 hours without any load and still not charging.

MODEL    : Smart-UPS 2200 

STATUS   : ONLINE 

BCHARGE  : 0.0 Percent

TIMELEFT : 0.0 Minutes

MBATTCHG : 5 Percent

MINTIMEL : 3 Minutes

MAXTIME  : 0 Seconds

ALARMDEL : 30 Seconds

BATTV    : 48.0 Volts

What can I do more?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

Assuming you did a braindead on it (pull batteries and mains power then hit the on button a few times to discharge everything) you have a faulty unit if it is under warranty call support, if you at your own risk you can remove the case and check the big internal fuse, it's connected to the charging cables but like I say it is inside and APC would advise against taking the case off due to the risk of shock.

Of course what you do is up to you 🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

Yes, I made it braindead for around 30 minutes. and then connected the batteries again and power source.

Well... I'll like shocking experiences... 😉

The strange point is that I'm not receiving any warnings or errors.

I'll start today with dismantling my 2200 and see what I an find.

When I look now... 

BATTV    : 45.1 Volts

Doesn't promise much good...

I'll let you know when I've found something.

Thanks,

Peter

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

I'm out of ideas...

The internal fuse is also OK. (what a massive fuse is that... 32V 100A. resistance was 0.3 Ohm)

UPS was approx 1 hour without batteries installed. So should be enough for brain-dead. 🙂 

BATTV is now 44.5 frown

Seems to going further down...

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:38 PM . Last Modified: ‎2024-02-29 11:50 PM

Gareth,

I want to upgrade my firmware, but it's still running on 6.2

To upgrade to the latest version I need to be on an minimal version of 6.4 before I can get tot the latest version.

The problem is that I can't find the 6.4. (I've already 9.4 (SMT18UPS_09-4) downloaded)

Do you have 6.4 available (or any other version what I can use to upgrade from 6.2) or know where I can find it?

Regards, Peter

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:50 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:50 PM

If you download the firmware upgrade wizard from:
http://www.apc.com/us/en/faqs/FA164737/

It should have contain latest version of firmware for each UPS. Note the numerical IDs on the file... ie SMT18UPS_9-4 is the file for version 9.4 on ID 18 hardware. Different hardware IDs have different firmware, each with their own version. Only firmware for the same hardware ID as your UPS will work.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:50 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:50 PM

Sounds like you have your wires crossed (no pun intended)

6.2 and 6.4 are NMC firmwares (current is 6.5) not UPS firmwares, you will probably find the UPS is running 9.3 and the latest is 9.4

Download the update for the network management card and get that up to date, then you can move onto the UPS, 

ftp://restrict:Kop$74!@ftp.apc.com/restricted/hardware/nmcard/firmware/sy/650/apc_hw05_aos650_sy650_...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:50 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:50 PM

My mistake... innocent You're completely right! Mine runs on 8.8 but will upgrade it to 9.4.

[update]

Just upgraded the NMC and is running now on 6.5.

1 small 'but'... He doesn't recognise the UPS self anymore.

KVhy%2B3OJCfS8ARxnjz0j8g%3D%3D.pngKVhy%2B3OJCfS8ARxnjz0j8g%3D%3D.png

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:50 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:50 PM

Did you upgrade with the SUMX app? You can see which app is running under About->NMC

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:50 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:50 PM

Yup... That's also on 6.5.0

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:50 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:50 PM

post screenshots of the about page for the UPS and NMC please.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:49 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:49 PM

Tried to upgrade UPS from virtual machine with W7Pro on my macbook, but without success.

I will try tomorrow with W7 laptop.

tDE%2Fi8TLFSyaMYG%2B9ufNug%3D%3D.pngtDE%2Fi8TLFSyaMYG%2B9ufNug%3D%3D.png

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:49 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:49 PM

Argh, sorry I posted a link to the wrong NMC firmware, just reflash with this and it will show the UPS again, sorry!

At least these cards are one for all so you can flash any firmware and flash back again.

It's this one

 ftp://restrict:Kop$74!@ftp.apc.com/restricted/hardware/nmcard/firmware/sumx/650/apc_hw05_aos650_sumx...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:49 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:49 PM

Gareth,

Tnx! This one works! 🙂

Will do this afternoon the upgrade of the UPS self from 8.8 to 9.4

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:49 PM

0 Likes
0
4011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:39 PM . Last Modified: ‎2024-02-29 11:49 PM

Tuesday contacted APC.

They've made a case.

Yesterday I've send reaction with the detailed information and today received my new UPS!

Wow... that's a service!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 11:40 PM . Last Modified: ‎2024-02-29 11:49 PM

0 Likes
0
4012
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:40 PM . Last Modified: ‎2024-02-29 11:49 PM

Service is great isn't it 🙂

I thought you were out of warranty or I would have told you to use them earlier 😄

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore