Guidance Help

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Guidance Help
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:36 AM . Last Modified: ‎2024-02-29 11:09 PM

0 Likes
8
1459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:36 AM . Last Modified: ‎2024-02-29 11:09 PM

Guidance Help

I was wondering if anyone could help me out with my setup. My company wants me to install PowerChute Network Shutdown on our Virtual environment and I am lost. Ive been reading up on this for sometime now and keep finding myself having issues. Ive found what i thought to be useful guides that get me pretty far but then fail. Any help would be apperciated. 

My setup is this 

1 data center, 1 cluster, 3 ESXi Hosts 5.5.0, with 31 VMs attached to the hosts. 

From my reading I am finding its best to install a virtual appliance to the host to control all the VMs but I am not familar with Linux. So what I have done is installed PCNS on all 31 of my VM's. I am fairly certain if a power outage occurs it will result in th VMs being powered down which is my number one goal at the moment. But what worries me is when the power is restored my three hosts will not power back on because the software isnt installed on them. So this means my Vms will stay down until I manually power back on the hosts. Does this sound correct so far?

How should I properly get this installed, does anyone have a good guide for newb Linux users that will walk me through the entire process? Thanks for your time.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:37 AM . Last Modified: ‎2024-02-29 11:08 PM

0 Likes
0
1458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:37 AM . Last Modified: ‎2024-02-29 11:08 PM

Hey Bill I went ahead and installed PCNS on a standalone Windows Machine, I skipped the laptop and used an older workstation I had in office.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:36 AM . Last Modified: ‎2024-02-29 11:09 PM

0 Likes
0
1458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:36 AM . Last Modified: ‎2024-02-29 11:09 PM

Michael,

You do not need to install the PowerChute Appliance. PowerChute can be installed on a Windows system that will power down the ESXi hosts if you have vCenter server managing the hosts and VMs? Also, have you received any VMware training?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:37 AM . Last Modified: ‎2024-02-29 11:09 PM

0 Likes
0
1458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:37 AM . Last Modified: ‎2024-02-29 11:09 PM

Hello Bill,

Thanks for the reply. Out of the 31 VMs we have running one of them is setup as the VMserver. The VMserver has PCNS installed on it. I do not know if the VMserver is managing the hosts though. I do see a service called VMare VirtualCenter Server running on the VM.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:37 AM . Last Modified: ‎2024-02-29 11:09 PM

0 Likes
0
1456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:37 AM . Last Modified: ‎2024-02-29 11:09 PM

Michael,


vCenter Server is designed to managed the VMware hosts, clusters, and VMs. PowerChute integrates with vCenter to gracefully shutdown the VMs and the host/s in the event of a power outage. PowerChute should not be installed on the VM that has vCenter installed on it. It sould be on its own VM or a standalone Windows system.
Application Note 180 and the users guide should help you understand the possibile configurations. I recommended the configuration on page 3 of application note 180 "vCenter Server running on a VM; PowerChute is installed on a physical machine" since you are not familiar with Linux. You should also get training in VMware since this is a complex enterprise configuration.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:37 AM . Last Modified: ‎2024-02-29 11:09 PM

0 Likes
0
1458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:37 AM . Last Modified: ‎2024-02-29 11:09 PM

Hello Again Bill,

Thanks for the reply. I guess the main reason I am confused on all this is, ive seen 4-5 different documents and forums talking about setting up and installing powerchute. How exactly does PcnS communicate with vCenter? Is there a plugin or something for it? Right now since I have PCNS installed on all my VMs and they are pointed to the UPS and able to communicate with in your opinion what is the major downside?

I guess I dont understand how having PCNS installed on one VM or one machine will communicate the shutdowns to the hosts and other VMs. I am probably missing a installation of something i imagine.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:37 AM . Last Modified: ‎2024-02-29 11:09 PM

0 Likes
0
1458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:37 AM . Last Modified: ‎2024-02-29 11:09 PM

Hey Bill,

I made some headway here and I wanted to see if you thought this was correct. I went around uninstalled PCNS on all of my VMs. I downloaded and installed PCNS on a new VM i created, I configured it for VMsupport followed the prompts pointed towards the vCenter Server IP when asked, then pointed towards UPS ip and applied username and password.

Previously I didnt have the Virtualiation Setting as a tab in PCNS but I do now. Is this all that really needed to be done? Will a power failure now communicate the shutdown terms with my VMs/hosts and power them back on when power is restored?

Thanks for all your help so far!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:37 AM . Last Modified: ‎2024-02-29 11:09 PM

0 Likes
0
1458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:37 AM . Last Modified: ‎2024-02-29 11:09 PM

Michael,

What VM did you install PowerChute on? If you did not install the PowerChute Appliance or VMware vMA they your setup is not supported. I assume that you did not since you wrote earlier that you did not understand Linux and both of those options are Linux.

You can install PowerChute on a standalone Windows system and have it communicate with vCenter server. The Windows system cannot be a virtual machine. The reason for this is when the shutdown starts the VMs are the first to be powered down and since PowerChute is running on a VM it will get shutdown stopping the process. If PowerChute is running on the appliance or on the vMA those OS have special services running so they do not get shutdown until the last moment allow the process to complete.

Also, have you followed the steps in application note 180 concerning active directory and setting up local account? A local account needs to be created on each ESXi server/host since vCenter is running on a VM. The local account will be used to shut the servers/host down once vCenter is shut down.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:37 AM . Last Modified: ‎2024-02-29 11:09 PM

0 Likes
0
1458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:37 AM . Last Modified: ‎2024-02-29 11:09 PM

Good Morning Bill,

I went with what was on page 4 B) Both vCenter Server and PowerChute are running on Virtual Machines.

I am going to find a laptop in office that I can use as the standalone machine and setup powerchute on that. Would that work still? I can probably fit it on the server rack somewhere.

As for AD user setting I didnt know that was actually needed in the setup. Since reading on the setup for B it didnt mention using an AD account for login permissions for the shutdown. I will attempt to go over this a bit more. Just let me know if a laptop will work for the standalone Windows Machine.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:37 AM . Last Modified: ‎2024-02-29 11:08 PM

0 Likes
0
1459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:37 AM . Last Modified: ‎2024-02-29 11:08 PM

Hey Bill I went ahead and installed PCNS on a standalone Windows Machine, I skipped the laptop and used an older workstation I had in office.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore