Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

AP9619 - Upgraded Firmware from v2.6.1 to v3.7.2 card no longer communicating

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9619 - Upgraded Firmware from v2.6.1 to v3.7.2 card no longer communicating
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
monaglekm_apc
monaglekm_apc
Cadet

Posted: ‎2021-07-08 12:36 AM

0 Likes
3
613
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:36 AM

AP9619 - Upgraded Firmware from v2.6.1 to v3.7.2 card no longer communicating

This was originally posted on APC forums on 5/11/2015


I have an APC Smart-UPS RT 5000 XL that we have been monitoring on line.  We attempted to upgrade the firmware from v2.6.1 to v3.7.2, but encountered 1 failure (feedback from results.txt below). I was still able to telnet to the device, but could not get the web interface working. I tried to Reboot the Management Interface from the telnet session, but it did not help.  I then reseated the card but still no difference.  I finally reset to defaults through telnet and allowed the device to use DHCH.  From the network port I can see that it is being assigned an IP address, but I can not get a reply by ping and can no longer telnet to the device.  Is there any way to roll back the firmware to the prior version? I no longer the APC smart-signaling cable (940-0024 or 940-1524) that came with the device.  Will a 940-0625A work with my AP9619?  Please guide me on how best to proceed to be able to monitor my UPS again.

Thank you,

Kit

results.txt

Using AOS file        : AOS = apc_hw02_aos_373.bin
Using Application file: APP = apc_hw02_sumx_372.bin

 

Checking network connection ...  Checking version information ...
 *************** Next **************

Before Upgrading the NMC the AOS is: apc_hw02_aos_264.bin
Attempting to log in to 172.19.36.254 ... Log in sucessful
Loading OS, please wait ...                      OK
Please wait (2 minutes ) for system restart   OK
Attempting connection to verify restart  Failed to ping at 172.19.36.254System reboot failed. Aborting this Upgrade.

 

Not all Network Management Cards were upgraded successfully:
 172.19.36.254: The Management Card at this address is not responsive.

Encountered 1 failures during upgrade.

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • 940-0625a
  • ap9619
  • firmware
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:36 AM

0 Likes
0
613
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:36 AM

This reply was originally posted by Angela on APC forums on 5/12/2015


Glad to help Kit!

See Answer In Context

Reply
Share
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:36 AM

0 Likes
0
613
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:36 AM

This reply was originally posted by Angela on APC forums on 5/11/2015


Hello Kit,

Can you confirm the exact model of the Smart-UPS RT 5000 - is it SURTD5000XLT or SURT5000XLT? Depending on that answer, it will confirm to me what cable you can use. Essentially, if it is an SURTD5000XLT, you should be using the 940-0625 as it has an RJ-45 connection on the UPS and if it is SURT5000XLT it has a DB-9 style serial port and would need 940-0024/1524.

But, if you don't have the correct cable, we have these options to configure the device. Perhaps the Device IP Configuration Wizard may work to search a DHCP pool range? Here are the options to configure TCP/IP settings and refer to NMC1 instructions -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156064 we need to sort that out so then we can fix the firmware and connect to it via an IP address.

Once you get TCP/IP settings sorted out, we'll likely just want to FTP the application file over and you'll be fine. I think what happened is the wizard tried to connect back into the card after the operating system firmware file was loaded and the AP9619 wasn't ready yet so the wizard aborted. This is easily addressed once we get an IP address on it.

What I'll want you to do is FTP to the AP9619, log in with your administrator username and password, and then do the ls command and see what files are there. I anticipate apc_hw02_aos_373.bin and then you'll just FTP the file you should've extracted when you downloaded the firmware to your computer, apc_hw02_sumx_372.bin. If you do not see that file, let me know. If you do, follow the steps to "put" this file on the AP9619 and that should be it since your operating system is already updated. http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA15604 Also refer to NMC1 manual FTP instructions here.

Let me know if you have questions before you get started.

Reply
Share
monaglekm_apc
monaglekm_apc
Cadet

Posted: ‎2021-07-08 12:36 AM

0 Likes
0
613
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:36 AM

This was originally posted on APC forums on 5/12/2015


Angela,

Thank you! Your reply was spot on.  I did locate a 940-0024 cable, so I was able to console to the device and sort out the TCP/IP issue.

I had attempted to use an FTP server to update the sumx file, but it kept timing out.  Once I changed to the Widows ftp client as documneted in the second link that you sent it worked perfectly.

Thank you again for your very prompt reply.

Kit

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:36 AM

0 Likes
0
614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:36 AM

This reply was originally posted by Angela on APC forums on 5/12/2015


Glad to help Kit!

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc