AP9619 - Upgraded Firmware from v2.6.1 to v3.7.2 card no longer communicating

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9619 - Upgraded Firmware from v2.6.1 to v3.7.2 card no longer communicating
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
monaglekm_apc
monaglekm_apc
Cadet

Posted: ‎2021-07-08 12:36 AM . Last Modified: ‎2024-02-29 11:09 PM

0 Likes
3
2662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:36 AM . Last Modified: ‎2024-02-29 11:09 PM

AP9619 - Upgraded Firmware from v2.6.1 to v3.7.2 card no longer communicating

I have an APC Smart-UPS RT 5000 XL that we have been monitoring on line.  We attempted to upgrade the firmware from v2.6.1 to v3.7.2, but encountered 1 failure (feedback from results.txt below). I was still able to telnet to the device, but could not get the web interface working. I tried to Reboot the Management Interface from the telnet session, but it did not help.  I then reseated the card but still no difference.  I finally reset to defaults through telnet and allowed the device to use DHCH.  From the network port I can see that it is being assigned an IP address, but I can not get a reply by ping and can no longer telnet to the device.  Is there any way to roll back the firmware to the prior version? I no longer the APC smart-signaling cable (940-0024 or 940-1524) that came with the device.  Will a 940-0625A work with my AP9619?  Please guide me on how best to proceed to be able to monitor my UPS again.

Thank you,

Kit

results.txt

Using AOS file        : AOS = apc_hw02_aos_373.bin
Using Application file: APP = apc_hw02_sumx_372.bin

 

Checking network connection ...  Checking version information ...
 *************** Next **************

Before Upgrading the NMC the AOS is: apc_hw02_aos_264.bin
Attempting to log in to 172.19.36.254 ... Log in sucessful
Loading OS, please wait ...                      OK
Please wait (2 minutes ) for system restart   OK
Attempting connection to verify restart  Failed to ping at 172.19.36.254System reboot failed. Aborting this Upgrade.

 

Not all Network Management Cards were upgraded successfully:
 172.19.36.254: The Management Card at this address is not responsive.

Encountered 1 failures during upgrade.

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • 940-0625a
  • ap9619
  • firmware
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:36 AM . Last Modified: ‎2024-02-29 11:09 PM

0 Likes
0
2662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:36 AM . Last Modified: ‎2024-02-29 11:09 PM

Glad to help Kit!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:36 AM . Last Modified: ‎2024-02-29 11:09 PM

0 Likes
0
2662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:36 AM . Last Modified: ‎2024-02-29 11:09 PM

Hello Kit,

Can you confirm the exact model of the Smart-UPS RT 5000 - is it SURTD5000XLT or SURT5000XLT? Depending on that answer, it will confirm to me what cable you can use. Essentially, if it is an SURTD5000XLT, you should be using the 940-0625 as it has an RJ-45 connection on the UPS and if it is SURT5000XLT it has a DB-9 style serial port and would need 940-0024/1524.

But, if you don't have the correct cable, we have these options to configure the device. Perhaps the Device IP Configuration Wizard may work to search a DHCP pool range? Here are the options to configure TCP/IP settings and refer to NMC1 instructions -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156064 we need to sort that out so then we can fix the firmware and connect to it via an IP address.

Once you get TCP/IP settings sorted out, we'll likely just want to FTP the application file over and you'll be fine. I think what happened is the wizard tried to connect back into the card after the operating system firmware file was loaded and the AP9619 wasn't ready yet so the wizard aborted. This is easily addressed once we get an IP address on it.

What I'll want you to do is FTP to the AP9619, log in with your administrator username and password, and then do the ls command and see what files are there. I anticipate apc_hw02_aos_373.bin and then you'll just FTP the file you should've extracted when you downloaded the firmware to your computer, apc_hw02_sumx_372.bin. If you do not see that file, let me know. If you do, follow the steps to "put" this file on the AP9619 and that should be it since your operating system is already updated. http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA15604 Also refer to NMC1 manual FTP instructions here.

Let me know if you have questions before you get started.

Reply

Link copied. Please paste this link to share this article on your social media post.

monaglekm_apc
monaglekm_apc
Cadet

Posted: ‎2021-07-08 12:36 AM . Last Modified: ‎2024-02-29 11:09 PM

0 Likes
0
2662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:36 AM . Last Modified: ‎2024-02-29 11:09 PM

Angela,

Thank you! Your reply was spot on.  I did locate a 940-0024 cable, so I was able to console to the device and sort out the TCP/IP issue.

I had attempted to use an FTP server to update the sumx file, but it kept timing out.  Once I changed to the Widows ftp client as documneted in the second link that you sent it worked perfectly.

Thank you again for your very prompt reply.

Kit

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:36 AM . Last Modified: ‎2024-02-29 11:09 PM

0 Likes
0
2663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:36 AM . Last Modified: ‎2024-02-29 11:09 PM

Glad to help Kit!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore