Gracefull shutdown of vSAN cluster

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Gracefull shutdown of vSAN cluster
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

0 Likes
2
879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

Gracefull shutdown of vSAN cluster

Hello.

I'm planning a new ups solution for our 2 node hyperconverged vSAN 6.6 cluster on vSphere 6.5 (HA enabled).

Can PCNS gracefully shutdown vSAN cluster? The recommended sequence is disable HA, shut down VM's except vCenter, shutdown vCenter, place ESXi into into maintenance, shutdown ESXi. And do I need any special PCNS licence?


Thank for you reply.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

0 Likes
0
879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

Hi,

PowerChute Network Shutdown does support ESXi and vSAN Cluster. However, PowerChute does not support installation on a host that is part of a vSAN enabled cluster. In a configuration that includes a vSAN enabled cluster, PowerChute must be installed on a physical machine, or on a host that is not part of the vSAN enabled cluster. 

When PowerChute starts a maintenance mode task via vSphere API it does not pass any arguments for vSAN data migration option. Because of this the default option Ensure accessibility is used.

The shutdown sequence is different than you listed. How many UPS will be in use? There is a diagram of PowerChute in an Advanced setup with vSAN cluster listed on page 16 of Application Note 180. 

As for license, there is no special license required. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

0 Likes
0
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

Hi,

PowerChute Network Shutdown does support ESXi and vSAN Cluster. However, PowerChute does not support installation on a host that is part of a vSAN enabled cluster. In a configuration that includes a vSAN enabled cluster, PowerChute must be installed on a physical machine, or on a host that is not part of the vSAN enabled cluster. 

When PowerChute starts a maintenance mode task via vSphere API it does not pass any arguments for vSAN data migration option. Because of this the default option Ensure accessibility is used.

The shutdown sequence is different than you listed. How many UPS will be in use? There is a diagram of PowerChute in an Advanced setup with vSAN cluster listed on page 16 of Application Note 180. 

As for license, there is no special license required. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

0 Likes
0
877
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

Thanks for you reply.

Installation of PCNS on standalone host is not a problem.

We've got more third party UPS, but basic licence of bundled software doesn't shutdown vsan properly.

We also have one APC Smart-UPS RT 2000 so I'll give it a try.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of