Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Grace shutdown for 3 servers with 1 smart UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Grace shutdown for 3 servers with 1 smart UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
denywinarto_apc
Ensign denywinarto_apc
Ensign

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-11 04:21 AM

0 Likes
9
2023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-11 04:21 AM

Grace shutdown for 3 servers with 1 smart UPS

Hi, I'm using a SUA2200 ups for a server running win 2012 R2.

And i have 2 other server running same OS with dumb UPS'.

All 3 are connected to a switch, which is also connected to the dumb UPS.

Now i need the sua2200 to gracefully shutdown all 3 servers in the event of blackout.

What is the most reliable way to do this?

If possible I'd like to keep the dumb UPS and have the smart UPS broadcast shutdown signal.

I tried some methods namely here 

http://forums.apc.com/spaces/5/smart-ups-symmetra-lx-rm/forums/general/5391/how-to-have-single-ups-s...

But my issue is that i tweaked around with the 2 other servers and i installed domain controllers on both of them, while the server with smart UPS does not have domain controllers feature installed.

thus it complicates things even more, on the part where i need users that have admin rights of all 3 servers.

Any other ideas? 

thanks

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
denywinarto_apc
Ensign denywinarto_apc
Ensign

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

0 Likes
0
2023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

Strange, if i add arp-s from machine that is connected using serial cable, i'm getting arp addition failed, access denied,

From other machine that is within the same network, it didn't throw out any error.

But pinging gives me RTO

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-11 04:21 AM

0 Likes
0
2023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-11 04:21 AM

Hi,

I recommend installing a network management card in the SUA and then installing PowerChute Network Shutdown on each server. The PowerChute client will listen to the NMC and react as you have configured it to. See the PCNS Installation Guide and PCNS User's Guide. The UPS will accept the older AP9617, AP9618, or AP9619 and the newer AP9630 or AP9631 network cards. You should be able to find a AP9617 on line. 

Another option is to install APCUPSD on each server and set one up as NIS server and the others as NIS clients. The APCUPSD users manual discusses NIS configuration. 

Reply

Link copied. Please paste this link to share this article on your social media post.

denywinarto_apc
Ensign denywinarto_apc
Ensign

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-11 04:21 AM

0 Likes
0
2023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-11 04:21 AM

Thanks but are you sure the PNC can detect a machine that's not connected to APC UPS?

I was told by a local seller here that it only detects APC UPS...

regarding apcusbd, i was having some issues about network error i think

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-11 04:20 AM

0 Likes
0
2023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-11 04:20 AM

Hi,

You wrote "Now i need the sua2200 to gracefully shutdown all 3 servers in the event of blackout." so my recommendation of using PCNS will work. You will install PCCNS on all 3 servers and they will listen the the NMC in the SUA2200. The servers cannot listen to the dumb UPS because it is not on line.

You can do the same with APCUPSD with one system communicating with the SUA2200 and that server will then send information to the others using NIS.  

Reply

Link copied. Please paste this link to share this article on your social media post.

denywinarto_apc
Ensign denywinarto_apc
Ensign

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

0 Likes
0
2023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

Thanks Bill! Gonna grab AP9617 and i will update the result

Reply

Link copied. Please paste this link to share this article on your social media post.

denywinarto_apc
Ensign denywinarto_apc
Ensign

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

0 Likes
0
2023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

Ok just got AP9617 and installed it, but there's one issue, It doesnt come with any manuals.

And i saw on video we have to know the mac address in order to set it up.

ANy other way to do this then?

Reply

Link copied. Please paste this link to share this article on your social media post.

denywinarto_apc
Ensign denywinarto_apc
Ensign

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

0 Likes
0
2023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

Anyone ? i tried Device IP configuration but it wont detect it..

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

0 Likes
0
2023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

Hi,

I have attached the install guide. You should be able to connect to the NMC via serial cable. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

denywinarto_apc
Ensign denywinarto_apc
Ensign

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

0 Likes
0
2023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

Local access to the control console You can use a local computer, a computer that connects to the Management Card through the serial port at the Management Card’s UPS or expansion chassis, to access the Control Console.

1. Select a serial port at the local computer and disable any service that uses that port.

2. Unless an APC smart-signaling cable (940-0024 or 940- 1524) is already connected to the selected port, connect the smart-signaling cable that came with the Management Card to the selected port and to the serial port at the Management Card’s UPS or chassis.

3. Run a terminal program (such as HyperTerminal) and configure the selected port for 2400 bps, 8 data bits, no parity, 1 stop bit, and no flow control, and save the changes.

4. Press ENTER to display the User Name prompt.

5. Use apc for the User Name and Password. 6. See “Control console” on page 16 to finish the configuration

Edit : Found the mac address on the card,

The NMC is installed on UPS, and the UPS is connected to the PC, which is connected using APC 940-0024 cable

I followed a youtube video that sets the arp by assigning ip with same subnet

But i cant ping the assigned ip.. getting rto with Ping [IP] l-113

Reply

Link copied. Please paste this link to share this article on your social media post.

denywinarto_apc
Ensign denywinarto_apc
Ensign

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

0 Likes
0
2024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-11 04:20 AM

Strange, if i add arp-s from machine that is connected using serial cable, i'm getting arp addition failed, access denied,

From other machine that is within the same network, it didn't throw out any error.

But pinging gives me RTO

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore