Generator no longer running scheduled test
  • Generator no longer running scheduled test
Posted: ‎2021-06-26 02:50 AM . Last Modified: ‎2024-03-19 01:49 AM
739
We have a APC InfraStuxure ATS swith on a Cummins generator (125DSHAE-6409) that quit running the weekly test that are scheduled. The event only shows last test from a couple of weeks ago and no alarms. Have tried changed scheduled test today about 3 times and count down to time of start, but doesn't do anything. Again no alarms or events.
125DSHAE-6409
  • Data Center & Facility 3 Phase UPS
Yes it manually starts fine, but wasn't sure about power outage so I threw the main breaker and it worked fine.
Replies 5
Janeway
Just a shot in the dark but check to see if the web interface is keeping time correctly and also try a reset to defaults.
The clock is keeping correct time. What would I set to defaults? Whole system?
Janeway
Save the config.ini file first -- it contains all configuration parameters.
Also, restart the network management card if you haven't already done so. The network management card runs the scheduled generator tests.
Can you manually run a generator test?
I did just kill the power to make sure the generator kicks in and it did. Thanks