Generator Sizing for total 15kVA

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Generator Sizing for total 15kVA
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 02:43 AM . Last Modified: ‎2024-03-19 01:54 AM

0 Likes
4
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:43 AM . Last Modified: ‎2024-03-19 01:54 AM

Generator Sizing for total 15kVA

Hello to everyone, nice to meet you.

I would like your opinion to the following matter.

I Already own 2APC Smart UPS. The first one is the SRT5KXLI (Single Phase) and the second one is a SRT10KRMXLI (Three Phase). In our business we are running a small Data Centre and I would like to match the above products with a Stand-By Diesel Generator.

More specifically, the one that I have in mind is a Caterpillar 22KVA DE22.

The UPSs are running now at about the 45-60% of the load (each) and I also have a small Air Condition 18kBTU in the server room.

What do you think for the above mention Generator, is it going to work seamlessly with the configuration (the 2 UPSs & AC)?

Thank you very much

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-26 02:44 AM . Last Modified: ‎2024-03-19 01:54 AM

0 Likes
0
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:44 AM . Last Modified: ‎2024-03-19 01:54 AM

Thank you once again for your advice! I will come back to this thread to let you know about the progress of the project.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-26 02:43 AM . Last Modified: ‎2024-03-19 01:54 AM

0 Likes
0
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:43 AM . Last Modified: ‎2024-03-19 01:54 AM

Honestly, backup power design and generator specification is a bit more complex than "Do you think this one will work?".

Both your UPS are power factor corrected, so no major issue there, and the 10KVa should balance across all three phases. The only real unknown is your AC. Singe or 3 phase supply? Any power factor correction? What is the start current on the compressor? Is it in inverter drive?

How do you intend to balance the load across the phases? Do you have a plan in place for maintaining the generator and sufficient constant load to prevent wet-stacking? How does the generator respond to a significant unbalanced load? Do you plan to run your lighting also (makes it awkward to see what you are doing when your battery emergency lights go flat and you have no lights).

Lots of variables to start with.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 02:44 AM . Last Modified: ‎2024-03-19 01:54 AM

0 Likes
0
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:44 AM . Last Modified: ‎2024-03-19 01:54 AM

Hello and thank you for your reply.

The AC has a three phase Power Supply with an Inverter Module, its a Carrier, but I don't know the Starting current at the moment.

As far as the lighting, yes, our back up lighting will be connected directly to the one phase of the Generator (later on).

The Generator will be activated for a few hours per month for maintaining purposes. In case that our loads (at the time speaking) are not sufficient and lets say they are 35-40% of the capability of the generator, do you have in mind an example of a dummy load we can connect to the Generator (for example some more 3-Phase AC or extra lighting) in order to prevent the problems you mentioned?

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-26 02:44 AM . Last Modified: ‎2024-03-19 01:54 AM

0 Likes
0
1093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:44 AM . Last Modified: ‎2024-03-19 01:54 AM

G'day George,

My experience with generator load banks is simply resistive heaters (some of them have been pretty huge). What you need to do is talk to the generator manufacturer to get recommendations on minimum load levels, minimum run times and maintenance recommendations.

With the AC being a 3 phase inverter, you'll find it's start current is actually pretty tame (unlike the old 3 phase DOL compressors), so you're probably pretty good there. You would do well to find out what its running power factor is as a bit of a heads up. Generator tests are a good time to crank up your redundant AC and verify it is performing also.

So really, your only issue is do you have enough load to reliably prevent the cylinder walls glazing while you run the unit. Diesel standbys are one of the rare exceptions to the "bigger is better" rule if you want them to live a long and useful life.

You then start getting into things like fuel rotation for shelf life and general diesel maintenance. 22KVA is not a big diesel in the scheme of things, but they're not cheap to purchase or maintain so you want to maximise your investment.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 02:44 AM . Last Modified: ‎2024-03-19 01:54 AM

0 Likes
0
1094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:44 AM . Last Modified: ‎2024-03-19 01:54 AM

Thank you once again for your advice! I will come back to this thread to let you know about the progress of the project.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore