Figure out UPS size

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Figure out UPS size
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:16 AM . Last Modified: ‎2024-03-12 03:11 AM

0 Likes
3
1048
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:16 AM . Last Modified: ‎2024-03-12 03:11 AM

Figure out UPS size

I currently have 5 Cisco 3750 48 port switches and will be looking to add a 3750 24 port POE and a Barracuda Web Filter 410. How can i determine or size the appropriate APC unit? Using APC's product selector tool it looks like he unit i would need cost over $5,000, is that possible? I currently have single power supplies in each switch.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:16 AM . Last Modified: ‎2024-03-12 03:11 AM

0 Likes
0
1048
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:16 AM . Last Modified: ‎2024-03-12 03:11 AM

Hello,

While sizing UPS "manually" we should always follow a pessimistic approach to avoid any overloads in near future. In your case I'd suggest you to follow the below method to come to any suitable conclusion.

[{(Critical Load in VA x 0.67) + (Future Load in VA x 0.67)} x 1.05] = A
(Ax 0.32) = B
Now A+B = Load in Watts

P.S : Get the VA ratings from equipment's nameplate. We are multiplying by 0.67 for a minimum power factor adjustment, 1.05 for peak values & 0.32 for UPS inefficiencies & battery charging

e.g if you have 2000VA of critical load and 500VA of future load, the UPS Watt rating you should be looking for would be

(((2500x0.67) x 1.05)
((1675 x 1.05) x 0.32)

A= 1758.75

B= 1758.75 x 0.32 = 562.8

Hence Watts = 2321


Once you have load in watts, check for the relevant technical specifications you are looking for from APC fleet of UPSs
i.e BACK UPS, SMART UPS, Symmetra UPS.....etc and choose your warrior. It is pertinent to note that a maximum of 80% load is suggested for enhancing UPS life time.

Best of luck

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:16 AM . Last Modified: ‎2024-03-12 03:11 AM

0 Likes
0
1047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:16 AM . Last Modified: ‎2024-03-12 03:11 AM

Hello,

What UPS did it suggest to you?

I do technical support primarily but when I go through sales questions, here is what I keep in mind to narrow the choices of appropriate UPS.

  • Is rack or tower mounting required?
  • How many watts do these pieces of equipment draw, and consider any requirements for inrush?
  • How much on battery runtime is required?
  • Do these pieces of equipment require anything special as far as you know, i.e. 0ms transfer time to/from battery (typically seen with really sensitive equipment)
  • Should we account for room for expansion, keeping in mind any required battery runtime with that expansion (like should the UPS potentially support extended run batteries)?
  • Do you just want a basic UPS or do you want something with bypass, modularity, etc?
  • What is the input voltage required at the site - 120V, 208V, or 240V or doesn't matter? Along with that, do you need to meet a certain input plug type at the site?
  • What about the plug types on your equipment? Obviously, we'd want to make sure they'd plug into the UPS that is chosen.

The UPS selector if it had your model of equipment would at least maybe list the wattage draw? That could help us to make a manual selection too.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:16 AM . Last Modified: ‎2024-03-12 03:11 AM

0 Likes
0
1049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:16 AM . Last Modified: ‎2024-03-12 03:11 AM

Hello,

While sizing UPS "manually" we should always follow a pessimistic approach to avoid any overloads in near future. In your case I'd suggest you to follow the below method to come to any suitable conclusion.

[{(Critical Load in VA x 0.67) + (Future Load in VA x 0.67)} x 1.05] = A
(Ax 0.32) = B
Now A+B = Load in Watts

P.S : Get the VA ratings from equipment's nameplate. We are multiplying by 0.67 for a minimum power factor adjustment, 1.05 for peak values & 0.32 for UPS inefficiencies & battery charging

e.g if you have 2000VA of critical load and 500VA of future load, the UPS Watt rating you should be looking for would be

(((2500x0.67) x 1.05)
((1675 x 1.05) x 0.32)

A= 1758.75

B= 1758.75 x 0.32 = 562.8

Hence Watts = 2321


Once you have load in watts, check for the relevant technical specifications you are looking for from APC fleet of UPSs
i.e BACK UPS, SMART UPS, Symmetra UPS.....etc and choose your warrior. It is pertinent to note that a maximum of 80% load is suggested for enhancing UPS life time.

Best of luck

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:16 AM . Last Modified: ‎2024-03-12 03:10 AM

0 Likes
0
1047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:16 AM . Last Modified: ‎2024-03-12 03:10 AM

Thank you both very much for your help!!!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore