generally the fan comes on for that model when anyone of the following conditions are true:
• internal temp is above 104º
• UPS is on battery
• UPS is charging its battery
• load is above 75% of UPS's rated capacity
have you verified that any one of these is not true when the fan is on? do you have any logs from software or a network management card to look at? how old is the UPS?