Smart UPS 3000 XL not switching to battery

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 3000 XL not switching to battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:44 AM

0 Likes
2
1875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:44 AM

Smart UPS 3000 XL not switching to battery

I inherited a site using a Smart UPS 3000 XL that doesn't appear to be switching to battery power. According to what I can get from the site contact all lights appear to show a functioning system. Battery shows fully charged, running on line power, only a single load light lit and no replace battery lit. This site has power fluctuations and the two servers connected to the UPS restart if there is a blip and when I had the contact do a self-test, the UPS shut down.

I do not know when the batteries were replaced, if ever, and I can replace the battery pack. Just wanted to see if anything else might be wrong or something else I can have them check before ordering a battery pack and making the trip to the site. I'm thinking that even though the system shows fully charged, that doesn't necessarily mean the batteries can handle the load when line power drops so the batteries could still be bad. Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:44 AM

0 Likes
0
1875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:44 AM

Thanks! I will have to get to the site in the next couple of days to get more info. I just started and they just recently acquired this location so I know nothing of the history. I do know that when they lose power, even for a split second, anything connected to the UPS restarts, as if it was directly connected to a power strip and you turned it off momentarily They have power issues and from what I can gather, it was working fine up to a month or so ago. Meaning, when they had a short power outage, the servers stayed up. When I had a person do the self-test ( I think he did it right), everything immediately restarted as if it wasn't transferring to battery. There are two servers connected and a router and as far as I can tell, it all resets. I don't think there is a management card or if there is it's not hooked up. I will have them check that for me. I also might shut the servers down and have them move the plugs to different outlets just to rule that out although I can't imagine 2-3 outlets being bad.

I'll just have to get out there and do some more troubleshooting. Based on information from them, the system has been in place for 4-5 years and as far as anyone knows, there has never been any changes to it. Thanks again for the tips and I will check that stuff as soon as I can get to it, it's far enough away that it's basically an all day trip for me.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:44 AM

0 Likes
0
1875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:44 AM

i would definitely recommend doing a pull plug test or tripping the upstream breaker on the UPS and seeing what happens. a pull plug test would be to pull the plug from the wall with an attached load to see what happens. you might want to take the critical load off and put something else on the UPS incase it does turn off. also, is ALL of the attached load rebooting or some of it. do you have a network management card log available for the UPS or powerchute business edition log? these could be very helpful. lastly, when the servers turn off, does the UPS turn off too? this issue does not scream "new battery" to me so we might want to see what else we can find out before you buy a battery. it especially does not seem like a "new battery" issue if the servers reboot versus turn off so you might want to double check to make sure it is a restart versus turn off. has this set up ever worked properly?

i forgot to mention that it would be worth while to have someone check serial numbers on the UPS and battery if available. the age could really help too along with the other questions i asked.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:44 AM

0 Likes
0
1876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:17 AM . Last Modified: ‎2024-03-11 02:44 AM

Thanks! I will have to get to the site in the next couple of days to get more info. I just started and they just recently acquired this location so I know nothing of the history. I do know that when they lose power, even for a split second, anything connected to the UPS restarts, as if it was directly connected to a power strip and you turned it off momentarily They have power issues and from what I can gather, it was working fine up to a month or so ago. Meaning, when they had a short power outage, the servers stayed up. When I had a person do the self-test ( I think he did it right), everything immediately restarted as if it wasn't transferring to battery. There are two servers connected and a router and as far as I can tell, it all resets. I don't think there is a management card or if there is it's not hooked up. I will have them check that for me. I also might shut the servers down and have them move the plugs to different outlets just to rule that out although I can't imagine 2-3 outlets being bad.

I'll just have to get out there and do some more troubleshooting. Based on information from them, the system has been in place for 4-5 years and as far as anyone knows, there has never been any changes to it. Thanks again for the tips and I will check that stuff as soon as I can get to it, it's far enough away that it's basically an all day trip for me.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore