Posted: 2021-06-30 05:20 AM . Last Modified: 2024-03-08 02:40 AM
Hi everyone,
Just need your help after a failed f/w update on my smart UPS SMT3000I with an APC9630 Card. I tried to update with the apc_hw05_aos688_sumx688_bootmon109.exe file. After the bootmon update, the software reboot the card to continue the update process... it's at this point that everything failed after.
I have looked for on forums some people with the same problem... some solved the problem with a "format" command and then a "reboot" one -> failed for me. Others applying update again -> failed for me, Updating via ftp... well, i can log in on the FTP, but i can't d/l or u/l a file -> failed again. Well, i'am feeling a little bit confused.
American Power Conversion Network Management Card AOS v6.1.1
(c) Copyright 2014 All Rights Reserved
-------------------------------------------------------------------------------
Name : apc863A8D Date : 06/11/2014
Contact : Unknown Time : 03:31:59
Location : Unknown User : Super User
Up Time : 0 Days 0 Hours 55 Minutes Stat : P+ N4+ N6+ A-
Type ? for command listing
Use tcpip command for IP address(-i), subnet(-s), and gateway(-g)
apc>system
E000: Success
Host Name Sync: Enabled
Name: apc863A8D
Contact: Unknown
Location: Unknown
Message:
DateTime: 06/11/2014:03:32:06
User: apc
Up Time: 0 Days 0 Hours 55 Minutes
Stat: P+ N4+ N6+ A-
Bootmon: bootmon:v1.0.9
AOS: aos:v6.1.1
App: bootmon:v1.0.9
If someone have an idea or could help me it would be really great.
Thank everyone
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:20 AM . Last Modified: 2024-03-08 02:40 AM
Hi RAMOINO,
So basically what is happening is that update is divided into three parts, the boot loader, operating system and the application, If your update is failing after the boot loader has been transferred then this is what you'll need to do to get back on track:
Extract the update and go into the folder "apc_hw05_aos688_sumx688_bootmon109", next go into the "Bins" folder
Now you will need to connect to the NMC using FTP, I recommend the WinSCP client.
Then you'll need to place apc_hw05_aos_688.bin in the root directory of the NMC
***This will cause the NMC to reboot
Next you'll need to copy apc_hw05_sumx_688.bin to the root directory,
****This will again cause the NMC to reboot
The device should now work as expected
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:20 AM . Last Modified: 2024-03-08 02:40 AM
Hi RAMOINO,
So basically what is happening is that update is divided into three parts, the boot loader, operating system and the application, If your update is failing after the boot loader has been transferred then this is what you'll need to do to get back on track:
Extract the update and go into the folder "apc_hw05_aos688_sumx688_bootmon109", next go into the "Bins" folder
Now you will need to connect to the NMC using FTP, I recommend the WinSCP client.
Then you'll need to place apc_hw05_aos_688.bin in the root directory of the NMC
***This will cause the NMC to reboot
Next you'll need to copy apc_hw05_sumx_688.bin to the root directory,
****This will again cause the NMC to reboot
The device should now work as expected
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:21 AM . Last Modified: 2024-03-08 02:40 AM
Hi Gavan,
Just amazing. I had understood that the update process were in three parts, and i already try to u/l the aos file via ftp and it didn't work. I tried with filezilla and i always got some errors.
I used so WinSCP in FTP mode (SFTP didn't work) and all files were uploaded without any error et the card reboot two times. All is working right now !
Thank you,
Have a nice day,
Regards