FW update failed Smart UPS SMT3000i / APC9630

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • FW update failed Smart UPS SMT3000i / APC9630
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:40 AM

0 Likes
2
1085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:40 AM

FW update failed Smart UPS SMT3000i / APC9630

Hi everyone,

 

   Just need your help after a failed f/w update on my smart UPS SMT3000I with an APC9630 Card. I tried to update with the apc_hw05_aos688_sumx688_bootmon109.exe file. After the bootmon update, the software reboot the card to continue the update process... it's at this point that everything failed after.

   I have looked for on forums some people with the same problem... some solved the problem with a "format" command and then a "reboot" one -> failed for me. Others applying update again -> failed for me, Updating via ftp... well, i can log in on the FTP, but i can't d/l or u/l a file -> failed again. Well, i'am feeling a little bit confused.

American Power Conversion               Network Management Card AOS      v6.1.1

(c) Copyright 2014 All Rights Reserved  

-------------------------------------------------------------------------------

Name      : apc863A8D                                 Date : 06/11/2014

Contact   : Unknown                                   Time : 03:31:59

Location  : Unknown                                   User : Super User

Up Time   : 0 Days 0 Hours 55 Minutes                 Stat : P+ N4+ N6+ A-

 

 

Type ? for command listing

Use tcpip command for IP address(-i), subnet(-s), and gateway(-g)

 

apc>system

E000: Success

Host Name Sync: Enabled

Name: apc863A8D

Contact: Unknown

Location: Unknown

Message: 

DateTime: 06/11/2014:03:32:06

User: apc

Up Time: 0 Days 0 Hours 55 Minutes

Stat: P+ N4+ N6+ A-

Bootmon: bootmon:v1.0.9

AOS: aos:v6.1.1

App: bootmon:v1.0.9

If someone have an idea or could help me it would be really great.

Thank everyone 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:40 AM

0 Likes
0
1084
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:40 AM

Hi RAMOINO,

So basically what is happening is that update is divided into three parts, the boot loader, operating system and the application, If your update is failing after the boot loader has been transferred then this is what you'll need to do to get back on track:

Extract the update and go into the folder "apc_hw05_aos688_sumx688_bootmon109", next go into the "Bins" folder

Now you will need to connect to the NMC using FTP, I recommend the WinSCP client.

Then you'll need to place apc_hw05_aos_688.bin in the root directory of the NMC

***This will cause the NMC to reboot

Next you'll need to copy apc_hw05_sumx_688.bin to the root directory,

****This will again cause the NMC to reboot

The device should now work as expected

-Gavan

Like

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:40 AM

0 Likes
0
1085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:40 AM

Hi RAMOINO,

So basically what is happening is that update is divided into three parts, the boot loader, operating system and the application, If your update is failing after the boot loader has been transferred then this is what you'll need to do to get back on track:

Extract the update and go into the folder "apc_hw05_aos688_sumx688_bootmon109", next go into the "Bins" folder

Now you will need to connect to the NMC using FTP, I recommend the WinSCP client.

Then you'll need to place apc_hw05_aos_688.bin in the root directory of the NMC

***This will cause the NMC to reboot

Next you'll need to copy apc_hw05_sumx_688.bin to the root directory,

****This will again cause the NMC to reboot

The device should now work as expected

-Gavan

Like
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:21 AM . Last Modified: ‎2024-03-08 02:40 AM

0 Likes
0
1084
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:21 AM . Last Modified: ‎2024-03-08 02:40 AM

Hi Gavan,

   Just amazing. I had understood that the update process were in three parts, and i already try to u/l the aos file via ftp and it didn't work. I tried with filezilla and i always got some errors.

I used so WinSCP in FTP mode (SFTP didn't work) and all files were uploaded without any error et the card reboot two times. All is working right now ! 

Thank you,

Have a nice day,

Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of