Network Shutdown with multiple vmware hosts connected to multiple UPSs

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Network Shutdown with multiple vmware hosts connected to multiple UPSs
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:41 AM

0 Likes
4
716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:41 AM

Network Shutdown with multiple vmware hosts connected to multiple UPSs

We are trying to set up Network Shutdown functionality at a site that has 5 vmhosts connected to 6 UPSs (along with switches and other equipment). We had gotten it set up at one point, then it decided at some point that it had to shut everything down in the middle of the day for no reason and we uninstalled the NS server. We're not certain what happened. We were able to verify that it was the shutdown agent sending the signal, but we don't entirely understand why. Closest we could ascertain is that it determined that there was not enough runtime left to shut everything down before power failure, but we don't know why it thought it was on battery, or that there was an issue.

The hosts are connected to the UPSs in redundant fashion (with each PSU connected to a different UPS), but the connections are done at random (NOTE: we did not set any of this equipment up, we just inherited the mess from an idiot). We are not in a position where we can shut everything down and rearrange, so we are stuck working with this unless it becomes clear we have no choice. I have taken the time to trace the power cords on everything so we know where everything is plugged in.

As far as we've been able to tell in the NS client, there is no way to assign specific UPSs to specific hosts. Is this correct? Is there any work around?

The UPSs are just a group of 6 Smart-UPS RT 3000 XL with NMC1 (AP9619) cards and they seem a bit flaky. Is there a better configuration? I've discovered that these NMCs are either old or bottom end, can we upgrade these without taking the UPS offline?

Any suggestions would be greatly appreciated. If anything is not clear, I can try to elaborate. Thank you for your input!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:41 AM

0 Likes
0
716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:41 AM

Hi,

On 7/24/2020 6:21 PM, Ben said:

We are trying to set up Network Shutdown functionality at a site that has 5 vmhosts connected to 6 UPSs (along with switches and other equipment). We had gotten it set up at one point, then it decided at some point that it had to shut everything down in the middle of the day for no reason and we uninstalled the NS server. We're not certain what happened. We were able to verify that it was the shutdown agent sending the signal, but we don't entirely understand why. Closest we could ascertain is that it determined that there was not enough runtime left to shut everything down before power failure, but we don't know why it thought it was on battery, or that there was an issue.

Did you configure PCNS to start a shutdown when available runtime has been exceeded? if so, that would explain the shutdown. See Schneider Electric FAQs 

FA405707 What is the Low Battery Duration setting used for?

FA241713 PowerChute Network Shutdown reports "Available runtime has been exceeded".

On 7/24/2020 6:21 PM, Ben said:

As far as we've been able to tell in the NS client, there is no way to assign specific UPSs to specific hosts. Is this correct? Is there any work around?

Are you running VMware vCenter Server or are the hosts standalone? If the hosts are managed by vCenter Server see Application Note 180 starting on page 6 for Advanced Redundant UPS configuration and Application Note 186. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:41 AM

0 Likes
0
717
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:41 AM

Hi,

On 7/24/2020 6:21 PM, Ben said:

We are trying to set up Network Shutdown functionality at a site that has 5 vmhosts connected to 6 UPSs (along with switches and other equipment). We had gotten it set up at one point, then it decided at some point that it had to shut everything down in the middle of the day for no reason and we uninstalled the NS server. We're not certain what happened. We were able to verify that it was the shutdown agent sending the signal, but we don't entirely understand why. Closest we could ascertain is that it determined that there was not enough runtime left to shut everything down before power failure, but we don't know why it thought it was on battery, or that there was an issue.

Did you configure PCNS to start a shutdown when available runtime has been exceeded? if so, that would explain the shutdown. See Schneider Electric FAQs 

FA405707 What is the Low Battery Duration setting used for?

FA241713 PowerChute Network Shutdown reports "Available runtime has been exceeded".

On 7/24/2020 6:21 PM, Ben said:

As far as we've been able to tell in the NS client, there is no way to assign specific UPSs to specific hosts. Is this correct? Is there any work around?

Are you running VMware vCenter Server or are the hosts standalone? If the hosts are managed by vCenter Server see Application Note 180 starting on page 6 for Advanced Redundant UPS configuration and Application Note 186. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:40 AM

0 Likes
0
716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:40 AM

On 7/28/2020 11:08 AM, Bill said:

Did you configure PCNS to start a shutdown when available runtime has been exceeded? if so, that would explain the shutdown.

Except that nothing was running on battery, so why would it shutdown? It was also on for 3 days before it decided to kill everything.

But yes, runtime exceeded was configured and the NMCs had the default 2 minute low battery duration.

On 7/28/2020 11:08 AM, Bill said:

Are you running VMware vCenter Server or are the hosts standalone?

Server

We actually figured all this out yesterday as we continued researching on our own, but thank you for the reply. However, this brings up a new question. NS is on a VM, which it warns about not being supported if you choose advanced configuration but it doesn't stop you from using it. Is that just due to the possibility of NS getting shutdown before everything else is done?

Oh, and can this shutdown the MSA's that hold the datastores?

I realize these questions are probably rather rudimentary, but information seems a bit scattered so we're asking questions along side our own research efforts. The input is much appreciated!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:40 AM

0 Likes
0
716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:40 AM

Hi,

On 7/28/2020 2:10 PM, Ben said:

Is that just due to the possibility of NS getting shutdown before everything else is done?

Yes. We cannot guaranty safe shutdown when PCNS is running on a VM in an advanced redundant UPS configuration.  

 

On 7/28/2020 2:10 PM, Ben said:

Oh, and can this shutdown the MSA's that hold the datastores?

I am not familiar with MSA datastores but if they allow for remote control via SSH you can write a script PCNS will run to command the datastores down. You will find information starting on page 79 fo the PowerChute VMware User's Guide. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:40 AM

0 Likes
0
716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:20 AM . Last Modified: ‎2024-03-08 02:40 AM

Ok, thank you for your input. It has been very helpful.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of