Extended Overvoltage notifications a few times a day, getting annoying :(

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Extended Overvoltage notifications a few times a day, getting annoying :(
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-12 07:40 AM

0 Likes
3
1611
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-12 07:40 AM

Extended Overvoltage notifications a few times a day, getting annoying :(

I have a Smart-UPS 750 RM that frequently goes into AVR Trim mode and sends a notification to my cell phone:

PowerChute Business Edition has detected the following event: Extended Overvoltage on Agent Gateway-i7

 

I checked the High-Transfer Voltage settings but they were set to 127v so I'm not sure why it goes into AVR trim at 124.5v??

 

The notifications every day are starting to get pretty annoying, it is just a matter of increasing the high transfer voltage to say 130v?

 

Any information you can provide would be great.

 

-Jamie M.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:44 PM

0 Likes
0
1611
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:44 PM

When I had this problem it turned out the incoming was going above the specified range, the UPS doesn't do a constant log so it can appear the voltage is within range. We ended up getting a monitor fitted to our consumer unit that logged every 5 seconds. This was enough for the electricity board to see it was going above range, it was higher again at the substation when they moved the monitor there. We ended up having the substation dialed down 10 volts and it has been fine since.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:44 PM

0 Likes
0
1611
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:44 PM

Hey Jamie,

I am having the exact same issue a few times a day ... did you get any response or resolution to this?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:44 PM

0 Likes
0
1611
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:44 PM

On 1/30/2017 8:34 PM, David said:

Hey Jamie,

I am having the exact same issue a few times a day ... did you get any response or resolution to this?

Nope, still happens all the time 😞 I shut off the e-mail notifications so it doesn't annoy me as much.

-Jamie M.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:44 PM

0 Likes
0
1612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:44 PM

When I had this problem it turned out the incoming was going above the specified range, the UPS doesn't do a constant log so it can appear the voltage is within range. We ended up getting a monitor fitted to our consumer unit that logged every 5 seconds. This was enough for the electricity board to see it was going above range, it was higher again at the substation when they moved the monitor there. We ended up having the substation dialed down 10 volts and it has been fine since.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of