SMX1500RM2UNC Firmware

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMX1500RM2UNC Firmware
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
rinconmike_apc
Lieutenant JG rinconmike_apc
Lieutenant JG

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:44 PM

0 Likes
9
2085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:44 PM

SMX1500RM2UNC Firmware

I have SMX1500RM2UNC

Firmware Revision: UPS 03.8 / COM 03.8 / UBL 05.0 / CBL 02.1 (ID11)

The network card is Model Number: AP9631

It is hooked to a dedicated 20A circuit.  Load on it is around 50%.  Sensitivity set to reduced.

I get alerts that it is on battery power due to distorted input. Looking at event log I have recevied them on 4/20, 4/19, 3/23, 2/10, 2/9, 2/4, 1/20, and more before. 

Also, unit seems to reboot and I get event message of Restored the local network management interface-to-UPS communication.  Looking at the logs this happened on 4/8, 3/28, 11/25, 11/15, 10/22.

Is any of htis normal?

I see on the support site that there is a new firmware file of "PowerNet MIB v4.1.4" dated 1/29/2015.

thanks,

Mike

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:43 PM

0 Likes
0
2082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:43 PM

Hi Mike - yes, with all of the settings that we allow (transfer ranges, sensitivity, etc) even all at LOW, we would never put the attached equipment at risk. Furthermore, no matter what your settings are set to, we offer an equipment protection policy guarantee on Back-UPS, Smart-UPS, and Surge products if you felt that the unit was at fault for letting a surge or some other transient through to your equipment. Long story short, we stand behind the product and I would not worry that setting the settings to low would cause a problem for your equipment connected to your UPSs. cool 

Let me know if you have any other questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:44 PM

0 Likes
0
2082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:44 PM

Hello,

Can you provide the full event.txt, data.txt, and config.ini files? (Or, provide the .tar file) What I am talking about is explained here for retrieving log files depending on firmware version -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131 

The UPS firmware (UPS 03.8) is the latest. The PowerNet MIB you are referencing is an SNMP MIB used with the AP9631 for users that utilize SNMP and is not applicable to what we're discussing. 

We'll need to see the full logs to see if there is anything obvious going on here and to see what is rebooting. If you see Restored the local network management interface-to-UPS communication along with other events, the management interface on the AP9631 may have rebooted but I can't tell for certain based on what you've provided so far.

Once we have the logs, we can share more detail.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:44 PM

0 Likes
0
2082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:44 PM

I am getting almost the exact same situation:

Firmware Revision:UPS 09.1 (ID20)

Model: SMX1500RM2UNC

MFG date: 8/29/2014

I would be happy to provide logs.  If you can help where should I submit them?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:44 PM

0 Likes
0
2082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:44 PM

Hi Jason,

I can take a look at the files and see what I can tell. The other poster's UPS had a lot older firmware than yours so the cause may be something different for a similar symptom.

You can email the files here to a Box folder I made: upload.APC_For.obfq3m3rb5@u.box.com 

I prefer the full .tar file if you can provide that and your Network Management Card firmware is newer. Instructions were in that link you may have already seen above as to how to grab the files.

Reply

Link copied. Please paste this link to share this article on your social media post.

rinconmike_apc
Lieutenant JG rinconmike_apc
Lieutenant JG

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:43 PM

0 Likes
0
2082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:43 PM

I still get the issue.  Should I update the firmware?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:43 PM

0 Likes
0
2082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:43 PM

Hi Mike,

To give you an answer I'd be confident in, I'll still need to see your logs if you can send the .tar file I mentioned. You can send them to the same email address as I posted earlier.

Reply

Link copied. Please paste this link to share this article on your social media post.

rinconmike_apc
Lieutenant JG rinconmike_apc
Lieutenant JG

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:43 PM

0 Likes
0
2082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:43 PM

I thought I uploaded the logs a while back.

Another issue that may be related.  I have both and SMX1500RM2UNC and a SMT1500.

I have a whole house generator (Generac 22KW).  I have the SMT1500 on reduced power setting and it is fine the the generator power.  However, for the the SMX, when on reduced, it is constantly switching onto battery due to distorted input ot something like that (every 30 seconds it switches back and forth).  If I put the SMX on low, then it does not jump back and forth and has no issue with the generator power (acts like the SMT that is on reduced).

So right now I have the SMX on low and the SMT on reduced.  The SMX is backing up a network switch, router, phone system and a few other devices.  The SMT is a workstation and some othe devices.

Any reason why the SMX needs to be on low and the SMT is ok on reduced with the same power?  Both have dedicated outlets to the main panel.

The generator has an ATS and does the entire house.

I lost power yesterday for around 12 hours so had plenty of time to see this happen.

For both the SMT (on reduced) and SMX (on low) if any of the AC kicked it, it would switch to battery for a few seconds, but this is expected due to the startup load of the AC.

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:43 PM

0 Likes
0
2082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:43 PM

Hi,

I do not see the logs in the Box folder I made which is access with that email address I previously posted earlier.

My first and gut thought is that SMT and SMX are different UPS designs so they may have different thresholds and sensitivity settings within their respective firmware/hardware architectures. To see what the difference is though, we would need to see the event and data log but even that may not be granular enough without seeing the input power through an oscilloscope and then having someone see how the different SMT and SMX product lines are interpreting things differently. So unfortunately, I don't have a straight answer but they are different units on both the inside and outside so I imagine that is what the reason is.

Reply

Link copied. Please paste this link to share this article on your social media post.

rinconmike_apc
Lieutenant JG rinconmike_apc
Lieutenant JG

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:43 PM

0 Likes
0
2082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:43 PM

ok.   I will try and send the logs later this week.

I guess the real question is, do I still get good enough protection with the SMX in low?  The devices are sonicwall NSA router, Netger 748 swtich, ADT pulse router, Vera Home Automation Router, Panasonic TDA phone system.  All seemed to be fine during the recent power outage on generator backup.  

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:43 PM

0 Likes
0
2083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:25 PM . Last Modified: ‎2024-03-04 10:43 PM

Hi Mike - yes, with all of the settings that we allow (transfer ranges, sensitivity, etc) even all at LOW, we would never put the attached equipment at risk. Furthermore, no matter what your settings are set to, we offer an equipment protection policy guarantee on Back-UPS, Smart-UPS, and Surge products if you felt that the unit was at fault for letting a surge or some other transient through to your equipment. Long story short, we stand behind the product and I would not worry that setting the settings to low would cause a problem for your equipment connected to your UPSs. cool 

Let me know if you have any other questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of