Execute virtualization shutdown sequence

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Execute virtualization shutdown sequence
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-13 04:16 AM

0 Likes
4
993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-13 04:16 AM

Execute virtualization shutdown sequence

"This triggers a shutdown sequence using the actions configured on the  Virtualization Settings  page. This option should be enabled for all UPS Setups that are powering physical equipment."

I'm sure I'm missing something obvious here. I never noticed Execute virtualization shutdown sequence under shutdown settings in PCNS 4.0 so not sure if this check box is new in 4.1. By default this setting is disabled. I have UPS on battery and temp probe 1 out of range enabled to shutdown my environment. Do I also need to enable Execute virtualization shutdown sequence?

Also, shut down PowerChute Server is grayed out with no check. Should I be able to enable it?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-13 04:16 AM

0 Likes
0
992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-13 04:16 AM

Hi,

Below is the description of Execute Virtualization Shutdown Sequence and Shut down PowerChute Server from the help file

Execute Virtualization Shutdown Sequence

Use this option to trigger the actions enabled on the Virtualization Settings page for ESXi hosts that are linked to UPSs/UPS Setups: VM migration/VM Shutdown/vApp shutdown followed by ESXi host shutdown.

This option is available only in a configuration in which a UPS setup is powering something other than a virtual host (e.g. a storage array) - it is enabled by default.

Shut down PowerChute Server

This is enabled by default and is used to gracefully shut down the physical machine running PowerChute.

This option should be disabled if the PowerChute machine is not being powered by the UPS’s in a particular setup, and if it is being used to remotely shut down other servers/ equipment.

This option is not available if PowerChute is installed on vMA or deployed as a virtual appliance.

These options are available when you select Advanced Redundant UPS when configuring PCNS in a virtualized environment. What is your environment / configurations? Do you require Advanced Redundant UPS setup? 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-13 04:16 AM

0 Likes
0
993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-13 04:16 AM

Hi,

Below is the description of Execute Virtualization Shutdown Sequence and Shut down PowerChute Server from the help file

Execute Virtualization Shutdown Sequence

Use this option to trigger the actions enabled on the Virtualization Settings page for ESXi hosts that are linked to UPSs/UPS Setups: VM migration/VM Shutdown/vApp shutdown followed by ESXi host shutdown.

This option is available only in a configuration in which a UPS setup is powering something other than a virtual host (e.g. a storage array) - it is enabled by default.

Shut down PowerChute Server

This is enabled by default and is used to gracefully shut down the physical machine running PowerChute.

This option should be disabled if the PowerChute machine is not being powered by the UPS’s in a particular setup, and if it is being used to remotely shut down other servers/ equipment.

This option is not available if PowerChute is installed on vMA or deployed as a virtual appliance.

These options are available when you select Advanced Redundant UPS when configuring PCNS in a virtualized environment. What is your environment / configurations? Do you require Advanced Redundant UPS setup? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:29 AM . Last Modified: ‎2024-03-13 04:15 AM

0 Likes
0
992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:29 AM . Last Modified: ‎2024-03-13 04:15 AM

Bill, thanks for the reply.

Using Advanced setup because I will eventually tie PCNS into my SAN. PCNS is on a physical server.

Do I enable Execute Virtualization Shutdown Sequence for my events to trigger a shutdown? If so, why would someone not enable this?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:29 AM . Last Modified: ‎2024-03-13 04:15 AM

0 Likes
0
992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:29 AM . Last Modified: ‎2024-03-13 04:15 AM

Hi,

On 4/4/2016 4:36 PM, Brian said:

Do I enable Execute Virtualization Shutdown Sequence for my events to trigger a shutdown? If so, why would someone not enable this?

Yes assuming the UPS is providing power to a host, the system PCNS is running on, or the SAN. You may not what to enable if the UPS is powering say a telephone system. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:29 AM . Last Modified: ‎2024-03-13 04:15 AM

0 Likes
0
992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:29 AM . Last Modified: ‎2024-03-13 04:15 AM

Gotcha. Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore