Posted: 2021-06-29 06:19 AM . Last Modified: 2024-03-12 11:44 PM
I have a SmartUPS sending me email alerts every 10 minutes
"UPS: Refused a self-test; UPS is overloaded."
This is an NMC2 (AP9631) runningAOS 6.4.0 in a Smart-UPS RT 8000 RM XL.
Where in "Configuration => Notification => Event Actions => By Event" can I find the entry for this specific alert to reduce the frequency of messages?
Thanks
Stefan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:19 AM . Last Modified: 2024-03-12 11:44 PM
Hi Squirrel,
Under which event group did you find event action "Refused a self-test; UPS is Overloaded"?
Power Events, Environment Events or System Events?
I cannot find it.
Thanks
Stefan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:19 AM . Last Modified: 2024-03-12 11:44 PM
Hi Stefan,
For the Critical Email Alert notifications on the AP9631, you would proceed to >Configuration=>Notification=>Event Action=>UPS:Refused a self-test; UPS is Overloaded<. Once selected, you will have the option to adjust E-mail / Trap Delay/Repeat/Interval and Dureation.
Secret Squirrel
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:19 AM . Last Modified: 2024-03-12 11:44 PM
Hi Squirrel,
Under which event group did you find event action "Refused a self-test; UPS is Overloaded"?
Power Events, Environment Events or System Events?
I cannot find it.
Thanks
Stefan