Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Esxi Standalone Network Shutdown PCNS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Esxi Standalone Network Shutdown PCNS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:51 AM . Last Modified: ‎2024-03-13 01:18 AM

0 Likes
2
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:51 AM . Last Modified: ‎2024-03-13 01:18 AM

Esxi Standalone Network Shutdown PCNS

Hi All,

Hope you can help clear up a few questions I have around the vmware appliance and shutdown of a standalone ESXI host.

As an example:

We have a single host configured with a 4.1 APC vmware appliance installed it has 30 minutes of battery remaining at 100%.

We have set the NMC installed to trigger low battery condition with 18 minutes to go (this includes the 2 minutes statutory shutdown on the nmc delay).

We have configured the appliance to shutdown the os after 120 seconds after a low batt condition above leaving 16 minutes of actual power to shutdown everything.

I have also set the vm to shutdown with a 30 second delay between and also set it to guest shutdown as per the guides.

The question I have is how does this work once the trigger happens does it shutdown all vm's at once with 20 seconds between them delay in the order specified under virtual machine startup/shutdown, and what happens after they are all down does the host shutdown or does it literally wait the 120 seconds start the shutdown and then the vms have just 2 minutes to shutdown before the os goes into maintenance and then shutdown at the host level?

thanks

Lee

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:51 AM . Last Modified: ‎2024-03-13 01:18 AM

0 Likes
0
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:51 AM . Last Modified: ‎2024-03-13 01:18 AM

Hi Bill,

Thanks for your post.

Just want to send over some screenshots just to be 100% sure we have our setup right we are basically running on a battery with 38 mins runtime remaining we want at 20 minutes left on battery to start shutting things down as we think thats the time needed to shutdown.

So NMC we have the following set

nmc

SO Low batt is set to 20 minutes (from talking with an APC rep who confirm this was correct) this is the time the NMC will wait before issuing a low battery condition to the PCNS clients.

Shutdown delay is the default 2 minute waiting time built into the NMC.

Then we have this set on the ESXI PCNS

So from your message we need to increase this value as I believe you have stated that once the low batt is sent after 20 minutes the host is set to turn off the guest VM's but will force power them off after 120 seconds with this set above and then shutdown the host.

It  then works top to bottom on this list below shutting down vm's however again I need to incrase the shutdown delay as that is the amount of time I am giving Esxi to shutdown the VMs probably about 1-2 minutes on each should suffice so set to 120 seconds per vm?

Hope this helps understand our setup and what we are trying to achieve and I appreciate the help.

thanks

Lee

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:51 AM . Last Modified: ‎2024-03-13 01:18 AM

0 Likes
0
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:51 AM . Last Modified: ‎2024-03-13 01:18 AM

Lee,

When PowerChute receive the low battery signal from the NMC it start the shutdown process immediately. Any delays are ignored so once the NMC reports the battery has less than 18 minutes of battery life remaining PowerChute will start the shutdown sequence. 

On 8/18/2016 11:26 AM, Lee said:

The question I have is how does this work once the trigger happens does it shutdown all vm's at once with 20 seconds between them delay in the order specified under virtual machine startup/shutdown, and what happens after they are all down does the host shutdown or does it literally wait the 120 seconds start the shutdown and then the vms have just 2 minutes to shutdown before the os goes into maintenance and then shutdown at the host level?

This is described in VMware Knowledge Base document 1004421 copied below. 

Shutdown delay is the maximum time the ESX host will wait for a shutdown command to complete. If the Virtual Machine does not shutdown within the delay time  specified a power off is issued to the Virtual Machine.
When an ESX host is shut down, the host follows this process:
  1. Autostart Manager initiates the automatic shutdown of the first Virtual Machine. The shut down is one of the power operations (Power Off, Guest Shutdown or Suspend) depending on the configuration.
  2. Autostart Manager waits the amount of time specified in the Shutdown Delay parameter for the Virtual Machine to complete the power operation.
    1. If the power operation is completed in less time than specified in the Shutdown Delay, the ESX host begins to shut down its next Virtual Machine.
    2. If the power operation is not completed within the time specified in the Shutdown Delay, the ESX host sends a power off command then then begins to shut down its next Virtual Machine.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:51 AM . Last Modified: ‎2024-03-13 01:18 AM

0 Likes
0
1415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:51 AM . Last Modified: ‎2024-03-13 01:18 AM

Hi Bill,

Thanks for your post.

Just want to send over some screenshots just to be 100% sure we have our setup right we are basically running on a battery with 38 mins runtime remaining we want at 20 minutes left on battery to start shutting things down as we think thats the time needed to shutdown.

So NMC we have the following set

nmc

SO Low batt is set to 20 minutes (from talking with an APC rep who confirm this was correct) this is the time the NMC will wait before issuing a low battery condition to the PCNS clients.

Shutdown delay is the default 2 minute waiting time built into the NMC.

Then we have this set on the ESXI PCNS

So from your message we need to increase this value as I believe you have stated that once the low batt is sent after 20 minutes the host is set to turn off the guest VM's but will force power them off after 120 seconds with this set above and then shutdown the host.

It  then works top to bottom on this list below shutting down vm's however again I need to incrase the shutdown delay as that is the amount of time I am giving Esxi to shutdown the VMs probably about 1-2 minutes on each should suffice so set to 120 seconds per vm?

Hope this helps understand our setup and what we are trying to achieve and I appreciate the help.

thanks

Lee

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore