Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Power Failed when UPS self-test
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2904:51 AM. Last Modified: 2024-03-1301:18 AM
Power Failed when UPS self-test
Hi All
I have a Smart UPS 2200 RM with Expander Card (serial port)
when the ups start self-test process, It will send alert email to me about Power Failed for a Server who connected with Expander Card
how self test procedure work ? and why it alert me same as electric problem
and why ups don't send me a Power Failed message for all server was connect this UPS.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2904:51 AM. Last Modified: 2024-03-1301:18 AM
the purpose of the interface expander is to provide simple signalling to additional powerchute clients for graceful shutdown. because it is simple signaling, i am assuming it saw the UPS went to battery and it is unable to tell the difference between a self test and power failure.
before i say that though, can you confirm the cable part numbers in use on the interface expander and on the UPS serial port for the client connected there? have you reviewed the email settings to see if maybe the other client is not enabled for email to see if that is why you got an email from one client but not on the other?
the self test procedure puts the UPS on battery for about 20-30 seconds to ensure the battery is able to support the load.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2904:51 AM. Last Modified: 2024-03-1301:18 AM
the purpose of the interface expander is to provide simple signalling to additional powerchute clients for graceful shutdown. because it is simple signaling, i am assuming it saw the UPS went to battery and it is unable to tell the difference between a self test and power failure.
before i say that though, can you confirm the cable part numbers in use on the interface expander and on the UPS serial port for the client connected there? have you reviewed the email settings to see if maybe the other client is not enabled for email to see if that is why you got an email from one client but not on the other?
the self test procedure puts the UPS on battery for about 20-30 seconds to ensure the battery is able to support the load.