Error messages from our Symettra 80KVa UPS- Runtime error
Showing results forΒ
Did you mean:Β
  • Error messages from our Symettra 80KVa UPS- Runtime error
Posted: β€Ž2021-06-26 05:04 AM . Last Modified: β€Ž2024-03-19 01:11 AM
925
I get this log error often right after the self test- Firmware is most current version. Log info is at bottom.
Here is the device info on the unit:
Main Intelligence Module (MIM)
Module Status: On & OK
Serial Number: PD0635130190
Manufacture Date: 08/23/06
Firmware Revision: 19.00
Hardware Revision: B
Redundant Intelligence Module (RIM)
Serial Number: PD0635130801
Manufacture Date: 08/25/06
Internal Communication Status
Communication Status: OK
MIM Internal CAN Bus: OK
MIM External CAN Bus: OK
MIM <--> RIM CAN Bus: OK
RIM Internal CAN Bus: OK
RIM External CAN Bus: OK
**Here is the Log entries Below:**
11/17/2010 12:27:38 UPS: A runtime alarm threshold violation no longer exists.
11/17/2010 12:27:34 System: Web user 'apc' logged in from 10.128.26.138.
11/17/2010 12:26:56 UPS: Failed a self-test.
*11/17/2010 12:26:44 UPS: A runtime alarm threshold violation exists.*
11/17/2010 12:26:16 UPS: Started a self-test.
11/15/2010 12:09:48 System: FTP user 'apc' logged out from 10.200.228.11.
11/15/2010 12:09:35 System: FTP user 'apc' logged in from 10.200.228.11.
11/15/2010 12:09:19 System: FTP user 'apc' logged out from 10.200.228.11.
11/15/2010 12:09:19 System: FTP user 'apc' logged in from 10.200.228.11.
11/15/2010 12:09:14 System: FTP user 'apc' logged out from 10.200.228.11.
11/15/2010 12:08:58 System: FTP user 'apc' logged in from 10.200.228.11.
11/15/2010 12:08:58 System: FTP user 'apc' logged out from 10.200.228.11.
11/15/2010 12:08:21 UPS: Restored the local network management interface-to-UPS communication.
11/15/2010 12:07:17 System: Network service started. System IP is 10.200.228.39 from manually configured settings.
11/15/2010 12:07:17 System: Warmstart.
11/15/2010 12:04:07 System: FTP user 'apc' logged in from 10.200.228.11.
11/10/2010 12:26:31 UPS: A runtime alarm threshold violation no longer exists.
11/10/2010 12:25:32 UPS: A runtime alarm threshold violation exists.
11/10/2010 12:25:30 UPS: Failed a self-test.
11/10/2010 12:25:03 UPS: Started a self-test.
11/03/2010 12:25:21 UPS: A runtime alarm threshold violation no longer exists.
11/03/2010 12:24:26 UPS: Failed a self-test.
11/03/2010 12:24:20 UPS: A runtime alarm threshold violation exists.
11/03/2010 12:23:48 UPS: Started a self-test.
10/27/2010 12:24:13 UPS: A runtime alarm threshold violation no longer exists.
10/27/2010 12:23:15 UPS: Failed a self-test.
10/27/2010 12:23:07 UPS: A runtime alarm threshold violation exists.
10/27/2010 12:22:34 UPS: Started a self-test.
  • Data Center & Facility 3 Phase UPS
So, I am showing 21 minutes of available battery runtime based on current load, but the alert was set to 10 minutes...I changed it to "disable" and set the new alert based on load...I'll see if that helps...Thanks for your assistance!
Jon in Las Vegas
you're welcome πŸ™‚
Jon in Las Vegas
Β