I get this log error often right after the self test- Firmware is most current version. Log info is at bottom.
Here is the device info on the unit:
Main Intelligence Module (MIM) 
Module Status: On & OK 
Serial Number: PD0635130190 
Manufacture Date: 08/23/06 
Firmware Revision: 19.00 
Hardware Revision: B 
Redundant Intelligence Module (RIM) 
Module Status: On & OK 
Serial Number: PD0635130801 
Manufacture Date: 08/25/06 
Firmware Revision: 19.00 
Hardware Revision: B 
Internal Communication Status 
Communication Status: OK 
MIM Internal CAN Bus: OK 
MIM External CAN Bus: OK 
MIM <--> RIM CAN Bus: OK 
RIM Internal CAN Bus: OK 
RIM External CAN Bus: OK 
**Here is the Log entries Below:**
11/17/2010 12:27:38 UPS: A runtime alarm threshold violation no longer exists. 
11/17/2010 12:27:34 System: Web user 'apc' logged in from 10.128.26.138. 
11/17/2010 12:26:56 UPS: Failed a self-test. 
*11/17/2010 12:26:44 UPS: A runtime alarm threshold violation exists.* 
11/17/2010 12:26:16 UPS: Started a self-test. 
11/15/2010 12:09:48 System: FTP user 'apc' logged out from 10.200.228.11. 
11/15/2010 12:09:35 System: FTP user 'apc' logged in from 10.200.228.11. 
11/15/2010 12:09:19 System: FTP user 'apc' logged out from 10.200.228.11. 
11/15/2010 12:09:19 System: FTP user 'apc' logged in from 10.200.228.11. 
11/15/2010 12:09:14 System: FTP user 'apc' logged out from 10.200.228.11. 
11/15/2010 12:08:58 System: FTP user 'apc' logged in from 10.200.228.11. 
11/15/2010 12:08:58 System: FTP user 'apc' logged out from 10.200.228.11. 
11/15/2010 12:08:58 System: FTP user 'apc' logged in from 10.200.228.11. 
11/15/2010 12:08:21 UPS: Restored the local network management interface-to-UPS communication. 
11/15/2010 12:07:17 System: Network service started. System IP is 10.200.228.39 from manually configured settings. 
11/15/2010 12:07:17 System: Warmstart. 
11/15/2010 12:04:07 System: FTP user 'apc' logged in from 10.200.228.11. 
11/10/2010 12:26:31 UPS: A runtime alarm threshold violation no longer exists. 
11/10/2010 12:25:32 UPS: A runtime alarm threshold violation exists. 
11/10/2010 12:25:30 UPS: Failed a self-test. 
11/10/2010 12:25:03 UPS: Started a self-test. 
11/03/2010 12:25:21 UPS: A runtime alarm threshold violation no longer exists. 
11/03/2010 12:24:26 UPS: Failed a self-test. 
11/03/2010 12:24:20 UPS: A runtime alarm threshold violation exists. 
11/03/2010 12:23:48 UPS: Started a self-test. 
10/27/2010 12:24:13 UPS: A runtime alarm threshold violation no longer exists. 
10/27/2010 12:23:15 UPS: Failed a self-test. 
10/27/2010 12:23:07 UPS: A runtime alarm threshold violation exists. 
10/27/2010 12:22:34 UPS: Started a self-test. 
Link copied. Please paste this link to share this article on your social media post.
 
					
				
		
Posted: β2021-06-26 05:04 AM . Last Modified: β2024-03-19 01:11 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:04 AM . Last Modified: β2024-03-19 01:11 AM
So, I am showing 21 minutes of available battery runtime based on current load, but the alert was set to 10 minutes...I changed it to "disable" and set the new alert based on load...I'll see if that helps...Thanks for your assistance!
Jon in Las Vegas 
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:04 AM . Last Modified: β2024-03-19 01:11 AM
you're welcome π
Link copied. Please paste this link to share this article on your social media post.
 
					
				
		
Posted: β2021-06-26 05:04 AM . Last Modified: β2024-03-19 01:11 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:04 AM . Last Modified: β2024-03-19 01:11 AM
So, I am showing 21 minutes of available battery runtime based on current load, but the alert was set to 10 minutes...I changed it to "disable" and set the new alert based on load...I'll see if that helps...Thanks for your assistance!