We moved our 3-phase APC SYMSTRF3I UPS to another building, which only has a single phase supply currenlty. Is it possible to power this UPS with just a single phase (UPS will only be supporting 2 servers). If possible could you please let me know how I could connect and power up the UPS. Thanks
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:04 AM . Last Modified: 2024-03-19 01:11 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:04 AM . Last Modified: 2024-03-19 01:11 AM
Hi Matt- thanks for this info. As you said:SYMSTRF3I can be used in either 3:1 or 1:1 mode.How can I input a single phase supply(used in 1:1 )?Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:04 AM . Last Modified: 2024-03-19 01:11 AM
SYMSTRF3I can be used in either 3:1 or 1:1 mode. The SYPM power module is universal and the 3:1 chassis allows for full current to pass through the AC_IN1 bus.
In 1:1 mode, acceptable nominal input (Hot-Neutral-Ground) would be 220/230/240 as you would expect.
And the full *3:1* user manual can be found here:
http://www.apcmedia.com/salestools/ASTE-6Z8LBY_R0_EN.pdf
The full *1:1* user manual can be found here:
http://www.apcmedia.com/salestools/ASTE-6Z8L9K_R0_EN.pdf
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:04 AM . Last Modified: 2024-03-19 01:11 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:04 AM . Last Modified: 2024-03-19 01:11 AM
Hi Matt- thanks for this info. As you said:SYMSTRF3I can be used in either 3:1 or 1:1 mode.How can I input a single phase supply(used in 1:1 )?Thanks!