ESXi & vCSA 6.5

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ESXi & vCSA 6.5
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:53 PM . Last Modified: ‎2024-03-12 01:04 AM

0 Likes
4
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:53 PM . Last Modified: ‎2024-03-12 01:04 AM

ESXi & vCSA 6.5

Hi,

I am having some problems getting the ESXi 6.5 hosts to shutdown correctly.

Our infrastructure consists of three ESXi hosts running various VM's, one of which is the vCSA.

I have PCNS running on a physical Windows server, which also provides DNS for our network.

I do NOT have Active Directory in use.

PCNS is successfully communicating with both the NMC in the UPS, and the vCSA, two of the ESXi hosts will go into maintenance mode, but the ESXi host running the vCSA will not go into maintenance mode. I then get an error saying that the ESXi hosts have failed to shutdown.

After consulting the PCNS error logs, I can see that there is a permission errors:

ERROR Thread-27 com.apcc.m11.components.WebServer.util.virtualization.VMWareConnection - Unable to log directly into host (NoPermission or InvalidLogin): esxi-1.psdn.lan

and

ERROR Thread-52 com.apcc.m11.components.Shutdowner.Hosts.ESXManagedHost - checkForVCSAVMAndHostInCriticalHosts - cannot obtain HostSystem using findByIP and findByDnsName for critical host esxi-1.psdn.lan

And after consulting the APC VMware User Guide, I see that I need to create a Shared User account with the same credentials on both the ESXi hosts and the vCSA.

I have a little brain fog and its unclear to me on exactly how to achieve this!

On the ESXi hosts, I can log in with a simple user account such as root.

However, on the vCSA, I am unable to use such simple user accounts, I have to use administrator@vsphere.local for example.

I have created an account on each ESXi host, apcupsmgmt. I then created the same user account on the vCSA. However, when I create this apcupsmgmt account on the vCSA, I cannot login to vCSA with just apcupsmgmt, it has to have the @vsphere.local apended to it to allow login.

How do I create the required shared account on both the ESXi host and the vCSA?

Thanks for your help.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:53 PM . Last Modified: ‎2024-03-12 12:58 AM

0 Likes
0
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:53 PM . Last Modified: ‎2024-03-12 12:58 AM

Hi,

Runtime Exceeded is explained in the User's Guide page 101, by clicking on help in PCNS or by reviewing Schneider Electric FAQ FA241713

If you have not done so you need to increase the low battery threshold of the network card to include the time needed for the VMs/vApps, VCSA, PCNS to power down and up. As an example: if VMs needed 120 seconds to power down, 120 seconds to power up, and VCSA needs 240 seconds to power down the low battery threshold on the network card needs to be 12 minutes. 120 +120 + 240 = 480 plus 120 for PCNS and 120 buffer = 12 minutes. 

I also recommend you review "Sample shutdown scenarios" starting on page 83 of the User's Guide. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:53 PM . Last Modified: ‎2024-03-12 01:04 AM

0 Likes
0
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:53 PM . Last Modified: ‎2024-03-12 01:04 AM

Hi,

Is VCSA running on Windows of Linux? If on Linux you need to create the apcupsmgmt account on the system and then follow the instructions in Schneider Electric FAQ FA241010 If VCSA is running on Windows you can follow the instruction from the FAQ to add the user. 

An example for Linux run the adduser and passwd commands to add the user. 

adduser apcupsmgmt

passwd APCpassword

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:53 PM . Last Modified: ‎2024-03-12 01:04 AM

0 Likes
0
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:53 PM . Last Modified: ‎2024-03-12 01:04 AM

Hi Bill,

Thanks for your reply.

I think I haven't explained myself very well.

The vCentre Server is running as an appliance on one of the ESXi hosts, so I would imagine that it is a Linux based system. It was installed via the ISO downloaded from VMware.

I can login to the vCSA via the CLI as root. However, the adduser commend does not work.

I am missing something simple here I am sure!

Thanks,

Dorian

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:53 PM . Last Modified: ‎2024-03-12 12:58 AM

0 Likes
0
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:53 PM . Last Modified: ‎2024-03-12 12:58 AM

I think I have managed to sort this out!

I logged in to the vCSA via ssh as root, used the useradd command to create the new user apcupsmgmt and the passwd command to create the password for the new account.

I then tried to login to the vCSA web client with the new account, but of course this did not work! Reason for that is that there were no permissions set in the vCSA web client for the new user! This is easily done from the permissions tab in the vCSA web client.

I can now login to the vCSA web client with the new apcupsmgmt account, and the PowerChute web GUI has accepted the username using the localos/apcupsmgmt format.

Error logs are no longer showing permission errors!! Yay!

I am not onsite to fully test a shutdown procedure, but I feel it will work now!

But one door opens, and another closes in my case, the logs are now saying "Available runtime has been exceeded." Which is odd as the UPS reports a 30.5% load and 45 minute run time! More reading is in order!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:53 PM . Last Modified: ‎2024-03-12 12:58 AM

0 Likes
0
892
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:53 PM . Last Modified: ‎2024-03-12 12:58 AM

Hi,

Runtime Exceeded is explained in the User's Guide page 101, by clicking on help in PCNS or by reviewing Schneider Electric FAQ FA241713

If you have not done so you need to increase the low battery threshold of the network card to include the time needed for the VMs/vApps, VCSA, PCNS to power down and up. As an example: if VMs needed 120 seconds to power down, 120 seconds to power up, and VCSA needs 240 seconds to power down the low battery threshold on the network card needs to be 12 minutes. 120 +120 + 240 = 480 plus 120 for PCNS and 120 buffer = 12 minutes. 

I also recommend you review "Sample shutdown scenarios" starting on page 83 of the User's Guide. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore