Do I need to replace the battery?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Do I need to replace the battery?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:31 AM . Last Modified: ‎2024-03-07 03:03 AM

0 Likes
3
2296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:31 AM . Last Modified: ‎2024-03-07 03:03 AM

Do I need to replace the battery?

Hi guys,

We've 3 server running - mac, windows2003 small server, windows 2003 server.
who ever installed the UPS system they just configure to handle windows 2003 server during power outages. one time there was a power outages and mac user lost lot of work and corrupted files. I've managed to create a batch file and shutdown the mac server
when there is a power outage.(Delay 1 min)

the battery and UPS is 4.2 years old and the model is SUA3000MRI2U. I need someone's advice or suggestion to whether I should replace the battery. we don't have enough budget.

Once we replace the batter I will add another batch file to shutdown small business server.

Please look at the attachment. I don't understand what is delay and duration.
Current run time is 19 mins. So for the command shutdown I used 1min delay and 1 min duration
shuting down attached device - delay 5mins duration 1.30 mins

The risk is Medium - errors are UPS age, Battery age and Application shutdown - see the log risk summary.

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-30 08:31 AM . Last Modified: ‎2024-03-07 03:02 AM

0 Likes
0
2296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:31 AM . Last Modified: ‎2024-03-07 03:02 AM

I notice in one of your screen shots that the load power consumption was 28 % and the UPS runtime was 19 mins. The UPS runtime appears to be very low according to the SUA3000RMI2U run time chart. Please look at the attached screen shot to view the detailed runtime chart of this unit.

The firmware inside a Smart-UPS is designed to last for years, yet the batteries are consumable items. As the batteries age, they lose their ability to hold a charge and therefore available runtime will decrease over time. I believe that its time to replace the batteries in your unit.

See Answer In Context

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:31 AM . Last Modified: ‎2024-03-07 03:02 AM

0 Likes
0
2296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:31 AM . Last Modified: ‎2024-03-07 03:02 AM

Thanks. more screen shots.

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-30 08:31 AM . Last Modified: ‎2024-03-07 03:02 AM

0 Likes
0
2296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:31 AM . Last Modified: ‎2024-03-07 03:02 AM

What are your settings under "Power failure" on the PCBE console?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-30 08:31 AM . Last Modified: ‎2024-03-07 03:02 AM

0 Likes
0
2297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:31 AM . Last Modified: ‎2024-03-07 03:02 AM

I notice in one of your screen shots that the load power consumption was 28 % and the UPS runtime was 19 mins. The UPS runtime appears to be very low according to the SUA3000RMI2U run time chart. Please look at the attached screen shot to view the detailed runtime chart of this unit.

The firmware inside a Smart-UPS is designed to last for years, yet the batteries are consumable items. As the batteries age, they lose their ability to hold a charge and therefore available runtime will decrease over time. I believe that its time to replace the batteries in your unit.

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of