Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Do I need to replace the battery?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Do I need to replace the battery?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
netmastan_apc
Crewman netmastan_apc
Crewman

Posted: ‎2021-06-30 08:31 AM

0 Likes
3
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:31 AM

Do I need to replace the battery?

This was originally posted on APC forums on 5/28/2009


Hi guys,

We've 3 server running - mac, windows2003 small server, windows 2003 server.
who ever installed the UPS system they just configure to handle windows 2003 server during power outages. one time there was a power outages and mac user lost lot of work and corrupted files. I've managed to create a batch file and shutdown the mac server
when there is a power outage.(Delay 1 min)

the battery and UPS is 4.2 years old and the model is SUA3000MRI2U. I need someone's advice or suggestion to whether I should replace the battery. we don't have enough budget.

Once we replace the batter I will add another batch file to shutdown small business server.

Please look at the attachment. I don't understand what is delay and duration.
Current run time is 19 mins. So for the command shutdown I used 1min delay and 1 min duration
shuting down attached device - delay 5mins duration 1.30 mins

The risk is Medium - errors are UPS age, Battery age and Application shutdown - see the log risk summary.

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Admiral Techie_apc
Admiral

Posted: ‎2021-06-30 08:31 AM

0 Likes
0
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:31 AM

This was originally posted on APC forums on 7/17/2009


I notice in one of your screen shots that the load power consumption was 28 % and the UPS runtime was 19 mins. The UPS runtime appears to be very low according to the SUA3000RMI2U run time chart. Please look at the attached screen shot to view the detailed runtime chart of this unit.

The firmware inside a Smart-UPS is designed to last for years, yet the batteries are consumable items. As the batteries age, they lose their ability to hold a charge and therefore available runtime will decrease over time. I believe that its time to replace the batteries in your unit.

See Answer In Context

Attachments
Reply
Replies 3
netmastan_apc
Crewman netmastan_apc
Crewman

Posted: ‎2021-06-30 08:31 AM

0 Likes
0
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:31 AM

This was originally posted on APC forums on 5/28/2009


Thanks. more screen shots.

Attachments
Reply
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-30 08:31 AM

0 Likes
0
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:31 AM

This was originally posted on APC forums on 6/1/2009


What are your settings under "Power failure" on the PCBE console?

Reply
Techie_apc
Admiral Techie_apc
Admiral

Posted: ‎2021-06-30 08:31 AM

0 Likes
0
933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:31 AM

This was originally posted on APC forums on 7/17/2009


I notice in one of your screen shots that the load power consumption was 28 % and the UPS runtime was 19 mins. The UPS runtime appears to be very low according to the SUA3000RMI2U run time chart. Please look at the attached screen shot to view the detailed runtime chart of this unit.

The firmware inside a Smart-UPS is designed to last for years, yet the batteries are consumable items. As the batteries age, they lose their ability to hold a charge and therefore available runtime will decrease over time. I believe that its time to replace the batteries in your unit.

Attachments
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc