Discharge issue on SC450

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Discharge issue on SC450
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:10 AM . Last Modified: ‎2024-03-13 11:25 PM

0 Likes
2
650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:10 AM . Last Modified: ‎2024-03-13 11:25 PM

Discharge issue on SC450

We had a battery alarm on one of our small 450 units (rack mounted) I went down and replaced the battery..

Now we cannot clear the Discharged Battery Alarm, and the following message appears even though the Battery capacity is showing as 100%..

====================================================

Input Voltage: 241.9 VAC
Output Voltage: 239.0 VAC

Runtime Remaining: 0 minutes
Last Battery Transfer: Due to software command or UPS's test control


=======================

Discharged Battery
The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.

========================

We also we did the runtime calibration.. (didnt make any difference) The unit has Passed a self test

Any ideas anyone ???

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:10 AM . Last Modified: ‎2024-03-13 11:25 PM

0 Likes
0
650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:10 AM . Last Modified: ‎2024-03-13 11:25 PM

a couple questions come to mind..

1.) how did you initiate a runtime calibration? how was it performed? how long did the calibration force the UPS on battery for?

2.) where did this "new" battery come from? purchased new from APC? has been it been sitting for a while?

3.) how long has the battery been charging now? do you have a voltmeter to test the voltage on the actual battery?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:10 AM . Last Modified: ‎2024-03-13 11:25 PM

0 Likes
0
651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:10 AM . Last Modified: ‎2024-03-13 11:25 PM

a couple questions come to mind..

1.) how did you initiate a runtime calibration? how was it performed? how long did the calibration force the UPS on battery for?

2.) where did this "new" battery come from? purchased new from APC? has been it been sitting for a while?

3.) how long has the battery been charging now? do you have a voltmeter to test the voltage on the actual battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

home
home
Cadet

Posted: ‎2024-08-31 11:46 AM

0 Likes
0
331
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-31 11:46 AM

So I have the same problem.

 

0 Minutes runtime available, But if I pull the power cable the UPS runtime is 10 mins plus.

 

Both the calibration tests passed and I updated the battery replacement date also.

 

Also once the power is restored the runtime remaining doesn't update, battery charge will drop though to 60% for example. But later once charged shows 100% again.

 

I removed all the cables that the UPS feeds, Switched off and restarted the UPS again, No change.

 

 System Status

On Line, Battery Discharged
77.3
%
0
Minutes
 

- Battery Status

100.0
%
13.8
VDC
 
Any ideas please ?
 
Thanks in advance.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of