Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Batteries discharged on SmartUPS SU2200XLINET

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Batteries discharged on SmartUPS SU2200XLINET
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:53 PM . Last Modified: ‎2024-03-11 04:25 AM

0 Likes
6
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:53 PM . Last Modified: ‎2024-03-11 04:25 AM

Batteries discharged on SmartUPS SU2200XLINET

Hi All,

We have an older SmartUPS 2200XLINET that I replaced the batteries on last month. After running a self test battery replacement LED finally went out, but the UPS still reports that the batteries are discharged:

Discharged Battery

The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.

I've read various forum posts and blogs that suggest either asking APC for a calibration key (we're well out of warranty though), using APCFix (unsupported) or resetting the battery constant using a serial connection. I'm not sure what the "correct" procedure is though, so could someone suggest the best solution?

Thanks,

Phil.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • calibration
  • constant
  • discharged
  • su2200xlinet
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:53 PM . Last Modified: ‎2024-03-11 04:24 AM

0 Likes
1
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:53 PM . Last Modified: ‎2024-03-11 04:24 AM

Ok - normally, we'd suggest a manual calibration which means putting a 30% (most likely non critical load) on the UPS that does not fluctuate more than 5% and running the UPS on battery until it turns off. You'd most likely want to remove the management card and make arrangements for any devices that have powerchute software running on them.

The other option is to adjust the UPS battery constants via serial cable (which also requires the management card to be removed). I can't really post the instructions here but I'll direct message them to you if that is the route you want to go. I've never used APCfix myself

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:53 PM . Last Modified: ‎2024-03-11 04:24 AM

0 Likes
0
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:53 PM . Last Modified: ‎2024-03-11 04:24 AM

The first thing we should verify is what the low battery signaling time is set to? it sounds like this message is coming from a Network Management Card - is that correct? if so, this setting should be listed under the UPS configuration options for shutdown. On newer firmware, check under UPS->Configuration->Shutdown within your management card web interface and let me know what it is set to.

I also need to know the total runtime reported by the UPS.

Thanks.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:53 PM . Last Modified: ‎2024-03-11 04:24 AM

0 Likes
0
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:53 PM . Last Modified: ‎2024-03-11 04:24 AM

Hi All,

We have an older SmartUPS 2200XLINET that I replaced the batteries on last month. After running a self test battery replacement LED finally went out, but the UPS still reports that the batteries are discharged:

Discharged Battery

The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.

I've read various forum posts and blogs that suggest either asking APC for a calibration key (we're well out of warranty though), using APCFix (unsupported) or resetting the battery constant using a serial connection. I'm not sure what the "correct" procedure is though, so could someone suggest the best solution?

Thanks,

Phil.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:53 PM . Last Modified: ‎2024-03-11 04:24 AM

0 Likes
0
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:53 PM . Last Modified: ‎2024-03-11 04:24 AM

Hi Angela,

Thanks so much for taking the time to help.

- Yes, the message I'm seeing is reported in the web server of the management card.

- The low battery duration setting is set to 02 minutes.

- The runtime remaining is reported as 2 minutes whilst the reported battery capacity is 100% and the load is reported as 23.9%.

Thanks, and hope this helps.

Phil.


Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:53 PM . Last Modified: ‎2024-03-11 04:24 AM

0 Likes
0
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:53 PM . Last Modified: ‎2024-03-11 04:24 AM

Hi Angela,

Can I try the serial cable route? Its a little tricky to arrange for the load from this UPS to be disconnected and the runtime calibration to be done because it's a remote site with limited access out of hours.

Thanks,

Phil.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:53 PM . Last Modified: ‎2024-03-11 04:24 AM

0 Likes
1
1653
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:53 PM . Last Modified: ‎2024-03-11 04:24 AM

Ok - normally, we'd suggest a manual calibration which means putting a 30% (most likely non critical load) on the UPS that does not fluctuate more than 5% and running the UPS on battery until it turns off. You'd most likely want to remove the management card and make arrangements for any devices that have powerchute software running on them.

The other option is to adjust the UPS battery constants via serial cable (which also requires the management card to be removed). I can't really post the instructions here but I'll direct message them to you if that is the route you want to go. I've never used APCfix myself

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

radium
Crewman radium
Crewman

Posted: ‎2024-08-31 06:17 PM

In response to BillP
0 Likes
0
643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-31 06:17 PM

Hi,  I have the same problem after I repalced the dischaged batteries on my Smart-UPS 1000 XL.

Would you send me a copy of instruction to  adjust the UPS battery constants via serial cable?

BTW , Can I remove the management cart without shutting down the UPS? 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now