PowerChute Network Shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Network Shutdown
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Harg-IT
Crewman Harg-IT
Crewman

Posted: ‎2024-08-27 03:14 AM

0 Likes
4
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-27 03:14 AM

PowerChute Network Shutdown

Hi,

 

I have PowerChute Network Shutdown version 4.4.1 on Linux centos (8).

 

We need to upgrade as 5.1.0 is available what's the best way to upgrade the documentation advises to run dnf update from the Linux VM but APC advise rebuild the OVA from the newer version.

 

If i run dnf update i get a error that it cannot find the mirror server as the server looks deprecated after a centos update.

 

It seems pretty backward on having to reinstall and reconfigure the VM with the same settings on every update.

 

Cheers James

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Harg-IT
Crewman Harg-IT
Crewman

Posted: ‎2024-09-01 11:14 PM

In response to Harg-IT
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-01 11:14 PM

Resolved this my self by enabling SSH and then logging in via WINSCP locating the ini file backing it shutting down the VM and then spinning up the new VM enabling SSH and copying the INI once all configured but the new system wants a licence now so ended up keeping the old VM and will have a look at costs for the new licence which is very unacceptable & cheeky from APC Scheider. As I may have to use the old software just depends on the costing.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2024-08-27 05:48 AM

0 Likes
1
1130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-27 05:48 AM

@Harg-IT 

 

 If you would like to use the PowerChute 4.4.1 configuration with 5.1, you can save the pcnsconfig.ini file from the 4.4.1 VM and install the 5.1 VM. Once the 5.1 VM has been installed, you can edit the 5.1 pcnsconfig.ini file and copy in the required sections from the 4.4.1 file. Before editing the file, you should stop the PowerChute service, edit the file, and restart the service. 

 

Note: The PowerChute 5.1 VM is a AlmaLinux. CentOS 8 reached end of life 31 December 2021. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Harg-IT
Crewman Harg-IT
Crewman

Posted: ‎2024-08-27 05:53 AM

In response to BillP
0 Likes
0
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-27 05:53 AM

@BillP 

Is there any instructions for this i have looked through the web gui and cannot see anything that lets me download the config.

Reply

Link copied. Please paste this link to share this article on your social media post.

Harg-IT
Crewman Harg-IT
Crewman

Posted: ‎2024-08-27 11:24 PM

0 Likes
1
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-27 11:24 PM

@BillP 

All I have is the vmware Linux Box and the web gui.

In those i cannot see any way to export the file in question.

I presume it be rebuilding from scratch which as i said seems backward.

Reply

Link copied. Please paste this link to share this article on your social media post.

Harg-IT
Crewman Harg-IT
Crewman

Posted: ‎2024-09-01 11:14 PM

In response to Harg-IT
0 Likes
0
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-01 11:14 PM

Resolved this my self by enabling SSH and then logging in via WINSCP locating the ini file backing it shutting down the VM and then spinning up the new VM enabling SSH and copying the INI once all configured but the new system wants a licence now so ended up keeping the old VM and will have a look at costs for the new licence which is very unacceptable & cheeky from APC Scheider. As I may have to use the old software just depends on the costing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of