Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Detected an unauthorized user attempting to access the SNMP

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Detected an unauthorized user attempting to access the SNMP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
7
2358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

Detected an unauthorized user attempting to access the SNMP

I have a Smart-UPS 2200 RM XL at a remote location sending me SNMPv1 errors.  " Informational - Detected an unauthorized user attempting to access the SNMP interface from 192.168.".  The IP is listed in the access control with Type Read, SNMPv1 is enabled, SNMPv3 is disabled. Network card firmware has been updated to v6.5.0.  I have tried to remove the IP in question and re-add it with no such luck.  I have tried removing the batteries and powering down the unit.  Most recient attempt was to update the firmware of the newtork card. Network card firmware has been updated to v6.5.0.  Any ideas team?

Attached are screen shots I thought might be helpful.  IP addresses, Mac addresses, Serial information, and Community Names have been removed.

1IqWrv1ULtfCvWiNKayqCQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png1IqWrv1ULtfCvWiNKayqCQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pnga9KDw6SovFM%2B5aLfTinAbg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pnga9KDw6SovFM%2B5aLfTinAbg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

sx6ifxOHaxkOuJT1VfuW%2BQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngsx6ifxOHaxkOuJT1VfuW%2BQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

UUI1S3r7%2BrOsLv8gg17qew%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngUUI1S3r7%2BrOsLv8gg17qew%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

8L2DSpbzxvHaaqS2oHRb4g%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png8L2DSpbzxvHaaqS2oHRb4g%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
B-DoubleE_apc
Commander B-DoubleE_apc
Commander

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
0
2355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

I dont think the NMC model would really matter much here, but for safety sake could you send from the 1500 with the AP9631, and one from the 2200 with the AP9630? I'd rather have too much data than not enough 😄

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 7
B-DoubleE_apc
Commander B-DoubleE_apc
Commander

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
0
2355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

Hi Adam,

Could you have multiple NMS on the same IP that are polling via SNMP? If you've customized the community names to match that of the IP that's listed in the event log, that would be my guess. Could you temporarily change the public2/private2 community names to the default of public/private to see if you still get these attempts?

If it's still happening (or there are no other NMS's running on that machine), then a packet capture between that IP and the NMC might be needed to see what kind of SNMP traffic is being sent to the card.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
0
2355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

Matt, thank you for your response.  I apologize for getting back to you so late.  I disabled the SNMP in question and ran WireShark looking for traffic to the UPS.  No traffic, yet I still get an attempt every 4 hours.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
B-DoubleE_apc
Commander B-DoubleE_apc
Commander

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
0
2355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

Hi Adam,

No worries. If I send you my contact information, would you be able to send me the log/configuration files from the NMC so I can take a look and help further?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
0
2355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:30 PM . Last Modified: ‎2024-03-12 12:48 AM

Matt, i received your information and will be sending you those files soon.  However as a general "what the" moment.  The SNMP in question is Spiceworks and its associated IP.  Every four hours I would get an error from the UPS stating something on that IP was an unauthorized user.  As a test, at 1PM yesterday I shut down Spirceworks, and at 4:14PM when the errors should have happened, it didn't.  8:14PM, 12:14AM, 4:14AM, and now at 8:14AM still no errors.

So here is my confusion, obviously the SNMP attempt is from Spircworks, which is supposed to be allowed.  We have 10+ APC 2200 units spread out around the city, configured the same way as far as SNMP goes, with no issues.  Only this one UPS gives us problems.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
B-DoubleE_apc
Commander B-DoubleE_apc
Commander

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
0
2357
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

Hi Adam,

Thanks for the extra info, that helps. Would you be able to send me the same debug file from one of the other UPS's you have that is not showing the issue? I'm assuming all of the units are the same model, and running the same revision of NMC firmware?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
0
2357
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

This is the oldest unit.  And it has a AP9631 my others 2200 have AP9630's 😞  I do have a 1500 with AP9631 would you like that? Or would you rather have the 2200 from the AP9630's?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
B-DoubleE_apc
Commander B-DoubleE_apc
Commander

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
0
2356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

I dont think the NMC model would really matter much here, but for safety sake could you send from the 1500 with the AP9631, and one from the 2200 with the AP9630? I'd rather have too much data than not enough 😄

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of